Default Designing an Advanced Heat Pump Controller

This thread is intended for discussions which could result in a fully featured, state of the art heat pump controller.

Advanced hardware, software, full features set.

-AC_Hacker

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-22-14 at 10:36 AM..
AC_Hacker is offline   Reply With Quote
Old 07-21-14, 09:33 PM   #2
mejunkhound
Apprentice EcoRenovator
 
Join Date: Apr 2011
Location: PNW
Posts: 197
Thanks: 0
Thanked 47 Times in 31 Posts
Default

"Simple" : start by revising your other thread:

VFD for 3 phase compressor

VFD for 3 phase condensor fan

NO reversing valve, HP only

VFD for 3 phase for ground loop circulation (or pump and dump pump, etc) pump

Flow meter

Turbine expansion with PM 6 phase micro generator

Some NTC resistors for indoor/outdoor/various line temperatures

Strain gauges on liquid and suction lines in a couple of places for pressure.

Laptop connections, serial USB

ACCURATE Mollier diagram/table of system components

Take all the inputs, Program laptop (e.g. Labview or similar)to compare to optimum operation point on Mollier diagram, readjust the VFDs for overall maximum COP every few minutes. Load the turbine expansion generator (by feeding 60 Hz back to line thru inverter) to control refrigerant flow consistent with optimum Molllier diagram COP point.

Program appropriate shutdown/safety points.

Similar algorithms for solar array peak power points can be used.
mejunkhound is offline   Reply With Quote
Old 07-22-14, 09:50 AM   #3
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by mejunkhound View Post
"Simple" : start by revising your other thread:

VFD for 3 phase compressor
VFD for 3 phase condensor fan
VFD for 3 phase for ground loop circulation (or pump and dump pump, etc) pump
How do you intend to provide the VFD function?

Quote:
Originally Posted by mejunkhound View Post
Turbine expansion with PM 6 phase micro generator
Can you elaborate in this? What is it and why do you want it?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-22-14, 10:07 AM   #4
mejunkhound
Apprentice EcoRenovator
 
Join Date: Apr 2011
Location: PNW
Posts: 197
Thanks: 0
Thanked 47 Times in 31 Posts
Default

VFD simply could be commercial drivers, literally hundreds of different models.
1st ebay hit as example:
High Quality 3HP 2 2KW 10A 220 250V Variable Frequency Drive Inverter VFD New A7 | eBay

Nearly all of these provide for RS422 or 1515 interface control.

Turbine expansion with PM 6 phase micro generator
To eliminate throttling losses from txv or expansion valve, the liquid to vapor transformation can be done by a turbine that recovers the lost energy of liquid to vapor transformation. Typically used in near absolute zero refrigeration setups.
Turboexpander - Wikipedia, the free encyclopedia
PM= permanent magnet, 6 phase to give smoother dc link for inverter and increase efficiency.
mejunkhound is offline   Reply With Quote
Old 07-22-14, 11:57 PM   #5
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

I have had great success using an ejector to recover the energy that went into raising the pressure. No moving parts apart from the refrigerant itself and it nicely gives you two stages of cooling for better dehumidification.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 07-23-14, 01:40 AM   #6
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by mejunkhound View Post
VFD simply could be commercial drivers, literally hundreds of different models.
I checked out your VFD link, pretty good prices.

In your previous post, you recommended using 3-phase for the compressor, fan, and circulating pumps.

I can see that the VFDs as you pointed out would be appropriate for precisely controlling a compressor, but what about the kind of VFDs would you use to drive a fan? The smallest VFD I've come across are about 1HP.

Then there's the issue of VFD for circ pumps. Do 3-phase circ pumps exist in the size that would be selected for a typical home? I would guess that the typical not-so-well-insulated home would require a heating system of something like 3.5 Tons, and the circ pumps could run in the 100 watt range, and sometimes, in a well designed radiant system, even less... like maybe 60 watts... I do think you are on to something, in fact, I think it's the way of the future. But do 3-phase VFDs and fans and pump motors in home sizes exist?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-23-14, 02:54 AM   #7
takyka
Helper EcoRenovator
 
Join Date: Jul 2014
Location: Hungary
Posts: 34
Thanks: 0
Thanked 16 Times in 10 Posts
Default

Hi,

The use of 3phase AC motors is a small step towards higher efficiency.
One problem, if you run a motor with VFD on 100% it is less efficient than the single phase counterpart. This is due the losses of the VFD.
Other issue is, BLDC motors are more effective. :-)
For circulation pump it's easy you can't beat (in price, simplicity and efficiency) the off the shelf units like Grundfos Alpha2
http://net.grundfos.com/Appl/WebCAPS...re-4352964.pdf
You can get 1/2-1/3 electric consumption from it than a single phase ac pump.
Biger problem to get BLDC (non circulation)pump, compressor and fan motor. I don't know if those are available as standard products...

VFDs are available from as small as 100W. I run my well pump from a 400W VFD on 23Hz, for passive cooling purposes.
http://ecorenovator.org/forum/attach...pfirsttest-jpg rightmost device in electrical box.

T.
takyka is offline   Reply With Quote
The Following 2 Users Say Thank You to takyka For This Useful Post:
AC_Hacker (07-23-14), ICanHas (08-13-14)
Old 07-23-14, 01:58 PM   #8
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by takyka View Post
Hi,

The use of 3phase AC motors is a small step towards higher efficiency.
One problem, if you run a motor with VFD on 100% it is less efficient than the single phase counterpart. This is due the losses of the VFD.
Other issue is, BLDC motors are more effective. :-)
For circulation pump it's easy you can't beat (in price, simplicity and efficiency) the off the shelf units like Grundfos Alpha2
http://net.grundfos.com/Appl/WebCAPS...re-4352964.pdf
You can get 1/2-1/3 electric consumption from it than a single phase ac pump.
Biger problem to get BLDC (non circulation)pump, compressor and fan motor. I don't know if those are available as standard products...

VFDs are available from as small as 100W. I run my well pump from a 400W VFD on 23Hz, for passive cooling purposes.
http://ecorenovator.org/forum/attach...pfirsttest-jpg rightmost device in electrical box.

T.
Thanks, great information!!

Where do you get the small VFD?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-23-14, 11:19 PM   #9
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Quote:
Originally Posted by takyka View Post
One problem, if you run a motor with VFD on 100% it is less efficient than the single phase counterpart. This is due the losses of the VFD.
Not the case if you use FOC (field oriented control). FOC essentially finds the most optimum V/Hz ratio to use at a given frequency. It's especially efficient on greatly varying loads like compressors.

__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 08:13 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design