Default Designing a General Purpose Heat Pump Controller

The Homemade Heat Pump concept has had some notable success.

However, one link in the chain that is missing is an open-source general-purpose heat pump controller.

If such a controller existed, it could increase the success of people who undertake a homemade heat pump project.

Such controllers have been built and put into service since the 'Manifesto' thread started, but the design considerations and full final specifications (diagrams, photographs, schematics, PWB files, software, etc) were not sufficiently made public such that 'just anybody' could use them.

We want a design that is sufficiently complete so that 'just anybody' can make it work for them.

The goal of this thread is to design, test and put into service such a controller... modifications and improvements can follow.

There is a hazard that this discussion could become so diluted to the point that nothing is ever produced.

In other words, this thread is totally oriented toward developing a working device. This is not a 'talking shop'.

* * *

jeff5may & I have had some preliminary discussion, and have decided that it is time to open up our conversation to anyone who can contribute.

Here we go...

-AC & jeff5may

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-29-14 at 02:20 PM..
AC_Hacker is offline   Reply With Quote
The Following 3 Users Say Thank You to AC_Hacker For This Useful Post:
b420ady (11-16-16), buffalobillpatrick (07-03-14), Mikesolar (07-06-14)
Old 07-02-14, 04:19 PM   #2
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Seems to me that we need to start with a conversation about "scope" and desired results, specific enough that we can tell when we are moving in the correct direction.

EDIT: Below is a working list of inputs & outputs for the GPC (general purpose controller), based on desired functionality. Additions are invited.
Quote:
  • Relay for compressor
  • Relay for crank case heater
  • Relay for fan
  • Relay for 4way valve
  • Relay for ground loop circulation pump
  • Relay for hydronic circulation pump
  • Input for flow switch so i am sure that water is circulating
  • Input for an S0 power meter to measure power usage.
  • Input for frost sensor (or water HX output temp sensor)
  • Two rs485 bus lines one for outside sensor print, and one to
    communicate with my other heating controller.
  • 2x16 lcd display
  • Some led's and push button to test

Best,

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-03-14 at 02:57 PM..
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
buffalobillpatrick (07-03-14)
Old 07-02-14, 04:34 PM   #3
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

I agree defining the scope is crucial to starting the project. Answering questions like what do you all need to be able to control (motors up to X amps, etc)? Or, what kind of sensors are you going to be dealing with? 220V or 110V?
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
The Following 2 Users Say Thank You to Daox For This Useful Post:
AC_Hacker (07-02-14), buffalobillpatrick (07-03-14)
Old 07-02-14, 07:59 PM   #4
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

There are at least four projects that are in various stages of development that I am aware of, it could be useful if the people who are working on their projects could describe what they would like a controller to do...

As for myself, I would like a GSHP controller that, as a very minimum requirement would:
  • Provide for a startup delay of the compressor
  • Monitor the output of the evaporator HX
  • If evaporator HX output temp was equal to or less than 37F the compressor would shut down for a selectable period off time (10 minutes for starters) while the water pumps keep running

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-02-14, 08:05 PM   #5
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default Hardware Requirements

Daox,
The actual brawny components residing in the machine will vary. They will differ depending on the specific application. However, the components on our controller should not. The controller module should be generic enough to fit the bill for a diverse range of end products. In addition to AC's requirements, I would like the controller to do these things:
  • Have the option for reverse cycle (heating and cooling modes)
  • Short cycle protection (compressor lockout)
  • Air or water source operation (selectable or configured)
  • Freeze protection (water source) or defrost (air source - compressor lockout or active reverse cycle)


I suggest we include a few "sugar cube" relays to directly control smaller devices, such as fans, pumps, or valves. It may sound hokey, but relays last a long time, are predictable, and can be wired a jillion different ways, to whatever power source the controlled device needs to operate. To control components that require more current than the relays can supply, a contactor or SSR can be added into the circuit. For that matter, the contactor or whatever can be wired to slave off a sugar cube relay.

Last edited by jeff5may; 07-02-14 at 09:21 PM..
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (07-03-14)
Old 07-02-14, 09:21 PM   #6
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by jeff5may View Post
The actual brawny components residing in the machine will vary. They will differ depending on the specific application. However, the components on our controller should not. I suggest we include a few "sugar cube" relays to directly control smaller devices, such as fans, pumps, or valves. To control components that require more current than the relays can supply, a contactor or SSR can be added into the circuit.
OK, this is good.

I do see all manner of SSRs, some smaller such as THIS_ONE, and THIS_ONE, and THIS_ONE.

I haven't designed much for any relays or SSRs except in my CO2 controller.

Is there a reason for electro-mechanical relays for the smaller devices and SSRs for the higher amp components?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-02-14, 09:32 PM   #7
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

I have a couple of local guys who would like to get involved in PCB design for this project.

But if we wanted to stay with "off the shelf" stuff, HERE_ARE some possibilities regarding smaller relays & SSRs.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-02-14, 10:08 PM   #8
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I like this one:
Amazon.com: SunFounder 4 Channel 5V Relay Shield Module for Arduino UNO 2560 1280 ARM PIC AVR STM32: Computers & Accessories

I was planning on using an Arduino Uno knock-off for my micro, so this board would attach like any other shield. This board will work with pretty much any microcontroller that spits out TTL for control. I believe they will need only 10 mA or less from the logic source per input.

Last edited by jeff5may; 07-03-14 at 05:12 AM..
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (07-03-14)
Old 07-02-14, 10:13 PM   #9
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

OK, I can see that... Pretty high current, indicator LEDs for prototyping, the little black chunks are opto-isolators (I hope). Price seems pretty good.

Can you trigger the relays directly from an Arduino output??

OK, so how do you plan to use something like this relay assembly?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-02-14, 10:46 PM   #10
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

An option to control VFDs (via RS232, PWM, or an analog voltage) would be nice.

__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (07-03-14)
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 08:11 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design