#191 | |
Vapor Compression Goon
|
![]() Quote:
Last edited by marx290; 03-10-13 at 09:52 PM.. Reason: added quote |
|
![]() |
![]() |
![]() |
#192 |
Lurking Renovator
Join Date: Jun 2012
Location: Virginia
Posts: 28
Thanks: 0
Thanked 4 Times in 3 Posts
|
![]() Years ago I was putting a roof on a building and had several pieces of corrogated galvanized roofing left over. approximately 3 ft x 6 ft. I framed the metal with wood with a 1 in thick foam insulation back approximately 1 inch from the back of the metal and covered the front with clear plastic. The metal was painted black. I went inside to answer the telephone and a few minutes later came back to the project. the metal was so hot that it burnt my hand when I picked it up to reposition it. I leaned it against my house under a bed room window in such a way that opening the window let the heat in our out. It really kicked butt on sunny days...
|
![]() |
![]() |
![]() |
#193 |
Vapor Compression Goon
|
![]() I lived in SW Pennsylvania where we had pretty cold, sustained winters. There were a number of clear sunny days usually with a lot of wind. I always wanted to take advantage of that incoming radiation. We don't own our home nor did we then or I may have built a solar hot air collector. That's probably one of the simplest ways to take advantage of the insolation.
Maybe someday I'll play around with building an ASHP and rig it up on the sunny side of my home. I would think a small greenhouse bult around the Hx would at the very least keep the precipitation off and maybe reduce frosting over. |
![]() |
![]() |
The Following User Says Thank You to marx290 For This Useful Post: | AC_Hacker (05-16-13) |
![]() |
#194 |
Lurking Renovator
Join Date: Jun 2012
Location: Virginia
Posts: 28
Thanks: 0
Thanked 4 Times in 3 Posts
|
![]() HI; I took a Klimeaire 12K btu unit (a long story of how I got here) and charged it with R290 from my local hardware store. I used my IR scanning thermometer to scan the condensor coil to indicate the amount of charge in the system> I eventually got a Delta T of 22 degrees. I ran the system for a couple of days. This system was set up in my shop so I could play with it. Once I determined that it was working fine. I evacuated it and recharged it with R410a. re-installed it into the rental unit and it worked through the winter just fine...
|
![]() |
![]() |
![]() |
#195 |
Lurking Renovator
Join Date: Jun 2012
Location: Virginia
Posts: 28
Thanks: 0
Thanked 4 Times in 3 Posts
|
![]() I did not realize my previous post was still on line..
Last edited by Thepprof; 04-14-13 at 04:06 AM.. Reason: Repeat |
![]() |
![]() |
![]() |
#196 | |
Lurking Renovator
Join Date: Jun 2012
Location: Virginia
Posts: 28
Thanks: 0
Thanked 4 Times in 3 Posts
|
![]() Quote:
|
|
![]() |
![]() |
The Following User Says Thank You to Thepprof For This Useful Post: | Xringer (05-16-13) |
![]() |
#197 |
Lex Parsimoniae
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 115
Thanked 250 Times in 230 Posts
|
![]() Would you say that both refrigerants worked about the same? Or was one better?
__________________
My hobby is installing & trying to repair mini-splits EPA 608 Type 1 Technician Certification ~ 5 lbs or less.. |
![]() |
![]() |
![]() |
#198 |
Lurking Renovator
Join Date: Jun 2012
Location: Virginia
Posts: 28
Thanks: 0
Thanked 4 Times in 3 Posts
|
![]() I did not do a exhaustive study. did not monitor current usage. Since the minisplit does not lend the equipment to the usual line set measurements to get the proper gas in the system and I do not have scales, I used a IR thermometer and monitored the heat being released by the condensor coil to determine how much gas to add. As I added gas the area of the coil releasing heat elevated on the coil. When I started initially heat was coming from the bottom 5 inches or so as I added gas this area raised until I got close to the top. The Klimaire has a large reserve container (nearly as big as the compressor) and I felt safe at that point.
|
![]() |
![]() |
![]() |
#199 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
|
![]() Quote:
-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
![]() |
![]() |
![]() |
#200 |
Lurking Renovator
Join Date: Jun 2012
Location: Virginia
Posts: 28
Thanks: 0
Thanked 4 Times in 3 Posts
|
![]() I have a Klimaire 12K Minisplit. The limit switch on the compressor failed and the compressor locked up. Since I purchased the unit online I knew that warranty was a joke. I took a compressor out of a 10K window unit and installed it in the unit. Set the whole system up in the shop and serviced it with propane. I had no information with regard to how much propane to charge with so simply gave it a 30 second shot and monitored the temperature change in the coils. As I added more gas the heat radiating from the compressor coils rose in the coils. When I got to a point that heat seemed to be radiating uniformly from the unit I quit. Pressures dropped dramatically, while maintaining about a 25 degree difference at the air handler. Pumped the unit down, reinstalled it and so for it is working great...
|
![]() |
![]() |
The Following User Says Thank You to Thepprof For This Useful Post: | Xringer (07-01-14) |
![]() |
|
|