Old 02-03-13, 10:55 AM   #21
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Mikesolar and/or AC_Hacker,

Yes, the two main places I look are the hvac talk forum and refrigeration engineers forum. The pros in the know all design the PTAC and RAC setups for 30 degrees superheat at the inlet line to the cxr at design conditions (85 deg F/30 deg C ambient). Asked about SLHX, they said it's just another part that could make these things fail. In walk-in freezer systems, though, they are commonly used since they save money. Their main focus is on reliability, then cost, efficiency comes in a distant third. Unless it's a big system that costs a lot to run.

I read in an article I can't find now that a designer noticed the "foam burp" effect. What the pros know is that it is a well known condition and design for it not to happen. This one briefly discusses it in section 4.2

http://docs.lib.purdue.edu/cgi/viewc...8&context=icec

The main idea is that at "high" evap temps (>-10 deg c) and below about 15 k of superheat, the propane boils so rapidly in the evap that the oil doesn't fully separate. The obvious solution is to keep superheat above 15 k. You can do this by either raising the superheat setting on the TXV or by adding SOMETHING in between the evap and cxr. This something will be the SLHX in my unit. With it, I will be able to set the TXV to a lower superheat setting (than 15K).

For an insight into the theoretical arguments surrounding this subject, just google 'R290 suction superheat'. The pros will argue this to death because it depends so much on specific situations. When narrowed to R22a (refrigeration engineer grade propane), the topic quickly devolves into scare tactics and warnings that propane is explosive. They are all against drop-in replacement of r12/r134/r22.

All my experimental systems have been made from old R22-based units. They are plentiful and dirt cheap. Mineral oil, 10 SEER type units.


Last edited by jeff5may; 02-03-13 at 11:01 AM..
jeff5may is offline   Reply With Quote
Old 02-03-13, 03:27 PM   #22
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

AC,
I just read the paper you presented. Is this awesome or what? Exploiting supersonic evaporator flow for efficiency gain! The author admitted he shoulda used a larger accumulator because he slugged his compressor! Priceless...

I hope the next version will support sustained operation. It would be a tremendous innovation.

I don't know if my unit was producing supersonic flow, I highly doubt it, but it was doing the same thing as the author described in his paper. Right at the point where efficiency was greatest, the evap would burp foam. I wasn't slugging my cxr, I was foaming it. I believe it was at around 10 deg F of superheat at the bulb, 15 deg f at the cxr inlet. from this effect, I learned how hard I could push my evaporator.
jeff5may is offline   Reply With Quote
Old 02-03-13, 04:32 PM   #23
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by jeff5may View Post
Right at the point where efficiency was greatest, the evap would burp foam. I wasn't slugging my cxr, I was foaming it.
So, you had a sight glass, right?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 02-03-13, 08:59 PM   #24
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

It is interesting that, at the end of the first paragraph of section 2, they want to insult the compressor. Not sure how that will help
Mikesolar is offline   Reply With Quote
Old 02-03-13, 09:22 PM   #25
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default Doh!

Quote:
Originally Posted by AC_Hacker View Post
So, you had a sight glass, right?

-AC
Well,err,hmm,uh...no. That would have made my cheap reverse a/c unit not so cheap.

In all honesty, I have no way of knowing whether I was slugging my compressor or not. But I do know I was running my evap too hard.
jeff5may is offline   Reply With Quote
Old 02-03-13, 09:29 PM   #26
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

I wonder if the viscosity issues of R290 and mineral oil are the same with a scroll as they appear to be with the recip? Are you really getting the foaming or is there some other issue. BTW, a sight glass is not very expensive.
Mikesolar is offline   Reply With Quote
Old 02-04-13, 10:51 PM   #27
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

OK, OK, you win. In my next unit, I'll put a sight glass in the suction line right before the compressor. When and if I test the envelope, I'll know what actually got through the line. If I have more trouble with the existing unit, I'll stick one in it and revisit this issue. For now, the 30 degF superheat at the suction inlet will remain.

Mikesolar,
It seems to be an issue at high flow, high temp (>-10 degC), low superheat conditions. With r290 or r600, POE oil is the worst, then PAG, then mineral oil. The mfrs are recommending Shell clavus g68 or suniso 4gs oil in r290 systems due to their higher viscosity, where in r22 systems they recommend clavus g32 or suniso 3gs. Kind of like putting racing oil in your car if you like to rev the engine. If the oil thins out, it will start from a higher initial viscosity and won't get too thin or foam up.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (06-04-14)
Old 02-05-13, 05:29 AM   #28
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

I started with an R410 pot, drained the POE and put in MO. The fridgie boys say that 5% POE won't be a problem in running the system so i am not concerned about getting it all out BUT, I still haven't turned it on yet. There may be a host of issues most of which, I am guessing, will revolve around sizing Evaps and condensers properly.

I don't know if the oils noted by the authors are available here or are they European only.
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (06-04-14)
Old 02-05-13, 05:01 PM   #29
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by Mikesolar View Post
I started with an R410 pot, drained the POE and put in MO. The fridgie boys say that 5% POE won't be a problem in running the system so i am not concerned about getting it all out BUT, I still haven't turned it on yet. There may be a host of issues most of which, I am guessing, will revolve around sizing Evaps and condensers properly.

I don't know if the oils noted by the authors are available here or are they European only.
From what I know about compressors (not much), the R410 types are set up for a higher compression ratio and higher ultimate pressures (r22 or 290 high side runs in the 200's psi range, r410a runs in the 400's psi range). I have heard that you can run them at lower pressures, though.

The oils I posted are worldwide standards made by American companies. Suniso is made by Sunoco, same guys that supply gas to NASCAR. 3gs is 30 weight, 4gs is 40 weight. Shell Clavus is made by Shell oil, the number is the weight. Any Hvac supplier will know what they are and have something equivalent.
jeff5may is offline   Reply With Quote
Old 02-05-13, 07:58 PM   #30
BradC
Apprentice EcoRenovator
 
Join Date: Dec 2010
Location: Western Australia
Posts: 148
Thanks: 1
Thanked 48 Times in 34 Posts
Default

Quote:
Originally Posted by jeff5may View Post
From what I know about compressors (not much), the R410 types are set up for a higher compression ratio and higher ultimate pressures (r22 or 290 high side runs in the 200's psi range, r410a runs in the 400's psi range). I have heard that you can run them at lower pressures, though.
Mostly right. Compression ratios remain the same, it's just the low and high side pressures are higher in an absolute sense. The other thing about 410A vs 22 or 290 is it has quite a high latent heat capacity so you need less mass flow for the same refrigerating capacity.
This means 410 compressors have a smaller displacement than their R22 counterparts, so a 18KW compressor for 410A will provide a significantly reduced capacity with a lower pressure refrigerant.

I can dig up the figures and give you a calc if you are really interested (or you could run a quick simulation in coolpack with a fixed mass flow compressor and see the difference in Qc when you switch refrigerants)

BradC is offline   Reply With Quote
The Following 3 Users Say Thank You to BradC For This Useful Post:
buffalobillpatrick (06-04-14), jeff5may (02-05-13), Mikesolar (02-06-13)
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:38 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design