In Oz, I know this is true but not here. MAPP is still available, I buy a lot of it. There may be the same product you mention available here but I haven't seen it, but who knows, I've been wrong before.......
Update.....I'll bow to updated info. The stuff I used to buy is not what I thought it was. Maybe I should read the label.... haha Last edited by Mikesolar; 01-08-13 at 06:54 PM.. |
01-08-13, 06:53 PM | #32 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
|
Quote:
There should be a very large temperature difference there. Just after the TXV the line should be drastically colder than going in. -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
01-08-13, 07:59 PM | #33 | |
Helper EcoRenovator
Join Date: Jan 2013
Location: Northern Minnesota
Posts: 32
Thanks: 1
Thanked 0 Times in 0 Posts
|
Quote:
MikeSolar: The dryer / filter is in the liquid line between the output of the condenser and the input to the TXV. The inlet and outlet of the filter are the same temp, so I don't think this is the issue. Bill |
|
01-08-13, 08:04 PM | #34 | |
Helper EcoRenovator
Join Date: Jan 2013
Location: Northern Minnesota
Posts: 32
Thanks: 1
Thanked 0 Times in 0 Posts
|
Quote:
?? |
|
01-08-13, 08:07 PM | #35 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
F/D could still be an issue. Is the temp coming out of the condenser the same as that going into the TXV? Maybe you answered this before.......
|
01-08-13, 08:09 PM | #36 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Adjusting the water flow through the condenser and/or through the evap. Fine tuning can be done this way. If either of the HX are too big or too small for the current conditions, they may be adjusted by valving or increased pumping, to some extent.
|
01-08-13, 08:18 PM | #37 |
Helper EcoRenovator
Join Date: Jan 2013
Location: Northern Minnesota
Posts: 32
Thanks: 1
Thanked 0 Times in 0 Posts
|
Guys,
I also noticed that if I put ice on the TXV bulb, the temp dropped in the evaporator. When I did this, I also noticed significantly more output heat from the condenser into the load, although I didn't actually verify this with temp measurements because it was tough to keep ice on the bulb and measure anything at the same time! :-) It was pretty obvious to me just based on feeling the in and out lines that the load outlet water temp was heating up a lot more with ice on the TXV bulb. The TXV outlet line was also noticeable much colder. It seems like the existing TXV is opening up too much and just dumping the existing R22 into the evaporator. The only reason the compressor isn't getting flooded is that the charge is so low that the evaporator is boiling all the R22 it's getting. This is why I think changing out the existing fixed TXV with an adjustable TXV along with a full recharge will fix my issue. Again, I could be wrong, but I've been reading a LOT and thinking about this issue for quite a while... No other answer seems to make sense. Bill |
01-08-13, 08:20 PM | #38 |
Helper EcoRenovator
Join Date: Jan 2013
Location: Northern Minnesota
Posts: 32
Thanks: 1
Thanked 0 Times in 0 Posts
|
|
01-08-13, 08:54 PM | #39 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
|
Quote:
Yeah, I think the TXV is the culprit here. You said your unit is 50K right? as in 50,000 BTU? That would be about right for 48,000 (4 Ton). I saw a post where Steve Hull said, "A 24,000 BTU unit should be really pumping out the heat." Where did he get 24,000 BTU? Am I missing something? Have you mentioned what the specs are on your current compressor? Have you mentioned what the specs are on your current TXV? Also, there are specific mounting instructions for the TXV bulb, which line, how far from the compressor, on a horizontal run, firmly attached to the top of the line (or side), etc. Your comment on how putting ice on the TXV bulb increased the output... That seems like a pretty serious clue here. -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
01-08-13, 09:30 PM | #40 |
Helper EcoRenovator
Join Date: Jan 2013
Location: Northern Minnesota
Posts: 32
Thanks: 1
Thanked 0 Times in 0 Posts
|
Yes, it's a 4 ton unit.
I'm also not sure where Steve got the 24,000 BTUs from either. I attached the datasheet for the new compressor in a previous post. I don't have any information on the TXV and there isn't a model number or much info on it that I can see. I can just see "VX Charge" on it. The bulb was attached at the output of the evaporator between it and the suction input of compressor. |
|
|