Thinking of a way to Bench Test COP of my DIY W/W HP.

Also needed for charging refrigerant.

Using garden hoses, not pumps!!!

Set & measure water flow rates through Evaporator & Condenser. say 6gpm
Use 5gal bucket method.

Temperature rise (delta-T*F) of Condenser water in/out can be measured.

BTU = 500 x 6 (GPM) x delta-T*F

With Amp meter on Compressor, is this a good way to estimate Watts?
How about a Kill-a-Watt meter?

Calculate COP = Energy out / Energy In

Of course this isn't including the water pumps energy that will be in final product, I think manufactures conveniently don't include this either?

Even better, but more expensive, is to get 2 x 55gal drums & use pumps.

But as actual pump flow rates can't be determined very accurately, the tank temperatures would have to measured & averaged as temperature would vary with location within tank.

I have a nice expensive water flow gauge, but its restriction effects flow some.


Last edited by buffalobillpatrick; 11-18-14 at 01:56 PM..
buffalobillpatrick is offline   Reply With Quote
Old 11-19-14, 10:46 AM   #2
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,431
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

If you are bechmarking the unit, you could run all of the power drawing equipment through a kill o watt meter and log the hx temp Delta t of the indoor hx as a function of time. The flow rate is not so easy unless you have a good flow meter. Since you have one, I would definitely use it if I trusted it.

Measuring the bucket temp will introduce errors when or if you include them into your calculated heat values. You're better off using source water that is relatively constant in temperature. The closer to the output of your hx you can measure its discharge temperature, the better. This will exclude any heat loss in the plumbing.

Running off tap water, you can set the flow rate with ease. Testing the unit at different flow rates and calculating your heat transfer will help you zero in on the "sweet spot" of your setup. If the hx is oversized compared to the compressor capacity, there will exist a flow rate where you will stop gaining raw btu's. Above this flow rate, there will be a balance point where your pump power catches up with the increase in COP. Depending on your goals, your optimum flow rate will lie somewhere between these two points.


Last edited by jeff5may; 11-19-14 at 04:23 PM.. Reason: bLASTED "SMART" pHONE...
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (11-19-14)
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:28 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design