Default Jelly Jar surge protector

Several posts lately have mentioned using mov's for surge and lightning protection on mains voltage.
I thought I'd post my version that's been in use for a while.
The jelly jar is used because it's cheap, it has excellent insulation properties and mov's can have meltdowns when subjected to high amps and voltages.

I put the mov's on half of a 50 cent 5x7 mm board from ebay. The board will hold 2 rows of four mov's.
The wires are 10 awg because I had some short pieces of USE-2 wire after rewiring my solar panels for a lower voltage. 12 AWG THHN wire is my usual choice. The mov legs are wrapped around the 10 awg wire and then soldered. The manufacturer suggest using a heat sink between the mov and the soldering. Apparently excessive heat will destroy them. Imagine that!

The photos show one side of both rows soldered together to a common green taped ground wire. The other two wires can go to a hot wire and neutral for 120 volt circuits. For 240 volt split phase, the wires both go to hot.

The metal lid is drilled and fitted with a 1/2 inch emt screw connection. Then I fill it with silicon. The metal ring and lid
are painted for outdoor use.
I like to use 150 volt RMS version on mains voltage and 84 volts DC version for my 65 volt solar panels.

Keep in mind this device is not UL listed. Insurance companies might frown on them. I don't know. I'd rather explain this to them than explain how one of my building burned.

philb is offline   Reply With Quote
Old 09-14-16, 09:33 PM   #2
philb
Apprentice EcoRenovator
 
Join Date: Nov 2010
Location: Oklahoma City
Posts: 155
Thanks: 58
Thanked 17 Times in 14 Posts
Default

There are TMOV'S out to help prevent thermal run away. I dont see that as a problem when they're enclosed in a glass jar.

The white sheet also details how to install a led to tell when the tmov needs replacing.

Last edited by philb; 09-15-16 at 08:45 AM..
philb is offline   Reply With Quote
Old 09-14-16, 09:47 PM   #3
philb
Apprentice EcoRenovator
 
Join Date: Nov 2010
Location: Oklahoma City
Posts: 155
Thanks: 58
Thanked 17 Times in 14 Posts
Default

I'll try the photos again.





Attached Thumbnails
Click image for larger version

Name:	20160913_184249-1-800x612.jpg
Views:	1107
Size:	126.5 KB
ID:	7238   Click image for larger version

Name:	20160913_185827-800x450.jpg
Views:	1093
Size:	113.2 KB
ID:	7239   Click image for larger version

Name:	20160913_185713-800x450.jpg
Views:	1079
Size:	113.4 KB
ID:	7240  

Last edited by Daox; 09-15-16 at 11:40 AM..
philb is offline   Reply With Quote
Old 09-15-16, 09:24 AM   #4
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

I would also add some 10-40uF or so motor run caps from the hot(s) to neutral to suppress small surges without wearing out the MOVs. And also a choke upstream of the protector and load although that might not be practical for high current loads.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 09-15-16, 11:15 AM   #5
philb
Apprentice EcoRenovator
 
Join Date: Nov 2010
Location: Oklahoma City
Posts: 155
Thanks: 58
Thanked 17 Times in 14 Posts
Default

Yes, I agree with you NiHaoMike. There are several items that can be added to the basic circuit that are environment specific.

My normal fair is MAINS – FUSE – INDUCTOR – MOV's – LOAD. The inductor is usually 2 or 3 strands of the electrical wire wound in a 12 inch circle and put in a metal box. The ends of the loops make a 90 degree bend when entering and exiting the box. It's a good idea to get the 90's to touch the box. Lightning does not like to conduct through tight turns. That's not much of an inductor, but it usually gives the fuse time to blow.

The entire jelly jar surge protection cost me $12.00 with all new parts mostly from Ebay. I would be hesitant to add run caps because of cost. If I had a low power factor, I'd be first in line for them. Just from here. If you happen to have them on hand or have a cheap source, it's worth the effort.

The mov's do need to be changed out periodically. The 150 volt mov's I used are V150LA10CP. They are rated for 10 surges at 3KA and 80 surges at 750A.

Last edited by philb; 09-15-16 at 11:17 AM.. Reason: typos
philb is offline   Reply With Quote
Old 02-12-17, 06:44 PM   #6
philb
Apprentice EcoRenovator
 
Join Date: Nov 2010
Location: Oklahoma City
Posts: 155
Thanks: 58
Thanked 17 Times in 14 Posts
Default

Update:
The jelly jar surge protector I posted did its job. The electronics and major appliances are fine. I can't say the same for protector though.


Attached Thumbnails
Click image for larger version

Name:	20170212_182946-800x450.jpg
Views:	921
Size:	83.0 KB
ID:	7614  

Last edited by Daox; 02-14-17 at 03:34 PM..
philb is offline   Reply With Quote
The Following User Says Thank You to philb For This Useful Post:
stevehull (09-13-17)
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:02 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design