Old 06-19-11, 07:20 PM   #51
strider3700
Master EcoRenovator
 
Join Date: Dec 2008
Location: Vancouver Island BC
Posts: 745
Thanks: 23
Thanked 37 Times in 30 Posts
Default

I was doing a little research and I'm thinking about going with a conventional 60 gallon water heater rather then one of those lifetime plastic heaters I had originally planned on. I can get a 60 6 year which will need some basic upgrades and better insulation for $370. upgrades will be about 100 with superinsulated box. a 12 year is $550 and will still need some more upgrades and more insulation. plastic lifetime tank is $1400...

I need to decide if a bottom inlet is better then top for the cold. I'm thinking it makes the plumbing a bit easier but this is without drawing it out.

strider3700 is offline   Reply With Quote
Old 06-29-11, 11:34 PM   #52
strider3700
Master EcoRenovator
 
Join Date: Dec 2008
Location: Vancouver Island BC
Posts: 745
Thanks: 23
Thanked 37 Times in 30 Posts
Default

I'm getting ready to make some fins for my water heating collectors and was hoping to use a bunch of "old" aluminum I have lying around. I have some 12" roll flashing. some 18" valley flashing, some 12" L flashing, some 8" L flashing and a Bunch of 7.5" step flashings.

I was thinking just go with 6" cut the big stuff down to 6" and leave the 8" and 7.5" stuff big with some overlap but after forming it for my 1/2" pipe that means the width is going to be somewhere between 4 and 4.5" which seems tight. my glass which sets the collector size is 34"x76" so that's 8x76"(minus frame/gap/header) risers or 18x 34" risers depending on if I go vertical or horizontal for the glass. Horizontal is more stealth for my location(guerilla install) but it's a bunch more 1/2" 3/4" T's.

Any thoughts or suggestions?
strider3700 is offline   Reply With Quote
Old 06-30-11, 09:54 AM   #53
GaryGary
Apprentice EcoRenovator
 
Join Date: Nov 2008
Location: SW Montana
Posts: 139
Thanks: 1
Thanked 21 Times in 15 Posts
Default

Quote:
Originally Posted by strider3700 View Post
I'm getting ready to make some fins for my water heating collectors and was hoping to use a bunch of "old" aluminum I have lying around. I have some 12" roll flashing. some 18" valley flashing, some 12" L flashing, some 8" L flashing and a Bunch of 7.5" step flashings.

I was thinking just go with 6" cut the big stuff down to 6" and leave the 8" and 7.5" stuff big with some overlap but after forming it for my 1/2" pipe that means the width is going to be somewhere between 4 and 4.5" which seems tight. my glass which sets the collector size is 34"x76" so that's 8x76"(minus frame/gap/header) risers or 18x 34" risers depending on if I go vertical or horizontal for the glass. Horizontal is more stealth for my location(guerilla install) but it's a bunch more 1/2" 3/4" T's.

Any thoughts or suggestions?
Hi,
Whether 4 or 5 inch total width is overkill or not depends on the thickness of your aluminum. You need about 0.018 thick aluminum to have an efficient fin that is 6 inches wide. You can run the fin efficiency for the alum you have here: FinEficCalc.xlsx

On the 3/4 by 1/2 T's, PEXSupply.com usually has a good price on the bags of 25. But, if the collector is not too wide, you really don't need 3/4 inch header -- a half inch header with standard half inch T's is fine -- like this one:
Experimental Solar Collector Using Hybrid Copper/Aluminum Construction

I tested the flow distribution for the half inch header collector and its fine:
Copper/Aluminum Solar Collector Flow Distribution Test

The test collector is only 4 ft wide, but I think you could go somewhat wider before needing the 3/4 inch heaer.

Some people have worked out ways to join small risers to big header without using T's -- one example is Ken's system:
Homemade Tee-Extractor for Solar Collectors

Gary
GaryGary is offline   Reply With Quote
Old 07-15-11, 10:43 PM   #54
strider3700
Master EcoRenovator
 
Join Date: Dec 2008
Location: Vancouver Island BC
Posts: 745
Thanks: 23
Thanked 37 Times in 30 Posts
Default

fin making is slowly continuing when both kids are awake and happy and outside and there is nothing ultra dangerous around forcing me to watch them every second.

For the rest of the time we started digging the hole to put the tank in. I decided the easiest way to go was to sit the lid in place add some space for insulation and just remove the grass. myself the 1 and 3 year old then started digging. They are actually pretty good at softening an area up. We only got maybe 6" down across the entire thing before rain called a halt to the fun.

Since the lid was off the tank I took some internal measurements and worked out 164.57 gallons if I leave the water level 2" below the lid joint.

Having put this much work into everything I do have to admit I felt a small twinge of concern reading in the flyers tonight that $1700+tax buys a brand new certified 20 evacuated tube collector, pump, 60 gallon storage tank, flat plate heat exchanger, and controller from a local hardware store so it should be no shipping.

It would need to be installed by a pro to qualify for tax credits which would probably make it break even but It looks a lot like $2000 would get you a warrantied approved system.

What I don't know is how 20 evacuated tubes will compare to a 136"x76" fin and tube flat plate collector. And I have more then double the storage and data logging as well as far more advanced control of the pumps. The add also said starting at so who knows what they hammer you with.

we'll see. No going back now
strider3700 is offline   Reply With Quote
Old 07-16-11, 05:12 AM   #55
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default

Strider 3700

I had built my own panels 6 pcs Copper fins 3/8 tube risers aluminum box tempered glass. Materials about $1200.00 cnd. What I think I save in labour I spend in better materials. Do they work better than evacuated tubes, don't really know. I had found a couple sites where it seamed Flat Plate offered up more BTUs but at a lower temp than EV's. What I can tell you that here in southwestern Ontario we have enough domestic hot water for everything. We have the electric back-up disabled except when we have more than 2 days no sun we will flip it on. Almost completely 2 months solely solar. In the winter when the sun is low hitting the panels more direct as they are on vertical walls and we get a full day of sun we can actually heat the house for 24 hrs. Be persistant the reward is there.

Randen
randen is offline   Reply With Quote
Old 07-16-11, 04:49 PM   #56
strider3700
Master EcoRenovator
 
Join Date: Dec 2008
Location: Vancouver Island BC
Posts: 745
Thanks: 23
Thanked 37 Times in 30 Posts
Default

Doing a bit or research a 20 tube system typically has 20 sqft of actual tube coverage collecting energy. my system will have closer to 72 sqft. evacuated tube isn't anywhere near 4 times as efficient so I should be well ahead on heat collected and have 100 gallons more to store that in.

that makes me feel a little better
strider3700 is offline   Reply With Quote
Old 07-16-11, 09:26 PM   #57
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Evacuated tube is only more efficient if there is a very large difference in collector temperature vs ambient. The crossover point on the image below shows the flat plat is vastly better until the delta T hits 100F.

Gary has this info on builditsolar:

__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 07-16-11, 09:47 PM   #58
GaryGary
Apprentice EcoRenovator
 
Join Date: Nov 2008
Location: SW Montana
Posts: 139
Thanks: 1
Thanked 21 Times in 15 Posts
Default

Quote:
Originally Posted by Daox View Post
Evacuated tube is only more efficient if there is a very large difference in collector temperature vs ambient. The crossover point on the image below shows the flat plat is vastly better until the delta T hits 100F.

Gary has this info on builditsolar:

The SRCC site has the tested efficiency curve intercept and slope values for all the collectors they certify, including lots of flats and lots of evacs:
SRCC Ratings

One interesting thing is that the evac tube collector efficiency curves vary a lot for each other, but as Tim says they all tend to start with fairly low maximum efficiencies, but the their efficiency curves are very flat, and at some high temperature they tend to intersect with the flat colelctor efficiency curves.

Gary
GaryGary is offline   Reply With Quote
Old 07-17-11, 09:26 PM   #59
Solaris
Uber Effecient
 
Solaris's Avatar
 
Join Date: Feb 2011
Location: Vancouver Island
Posts: 18
Thanks: 0
Thanked 2 Times in 2 Posts
Default Flat Plate Collectors

It is true that flat plate collectors are generally more efficient for heating domestic hot water, which is a moderate temperature application. Vacuum tubes can be better when small quantities of hotter water are needed closer to boiling point, but at those temperatures the Glycol breaks down into an acid and can destroy a presurrized system in a short time. Too much heat is the biggest design problem with some solar (unless it is drainback), high heat cuts the life of the sytem in half.

Here is a good list from Heatspring Magazine's 2011 review:
Top 50 Most Efficient Solar Thermal Collectors on the Market
Top 50 Most Efficient Solar Thermal Collectors on the Market | HeatSpring Magazine
48/50 are flat panel collectors, only Sunda in spots 21 and 24 are vacuum tube.

There is also a lot to be said about durability and longevity of flat panel collectors working in the field for more than 30 years. Chinese tubes that I have seen turn cloudy after just a few years, and are disposable after 10 years.

Strider, I am guessing the add you saw was from Slegg, I know they are blowing Chinese tube crap out to upgrade to better Austrian flat panels.
__________________
Solaris

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Solaris is offline   Reply With Quote
Old 07-17-11, 11:50 PM   #60
Solar Mike
Helper EcoRenovator
 
Join Date: Apr 2010
Location: Wellington, New Zealand
Posts: 61
Thanks: 0
Thanked 6 Times in 5 Posts
Default

Many of the newer design evac tube collectors use a heat pipe to collect the heat from the fin and move it to the water in the header condenser section. This mechanism isnt as efficient st collecting heat as a flat panel with the same area at lower temperatures, because the heat pipe, which typically contains a few cc of water inside an evacuated tube doesn't contain enough water vapor to convey much heat until the pipes warm up to > 50 Celsius.

Sales people will try to tell you they are more efficient, which they are, but only at much higher temperatures than you really require.

From my experience, if you use the evac tubes systems, then for a family of 4 and a 300 liter water cylinder you require 50 tubes. The quality of some of the cheaper tubes are unknown and possibly suspect. The failure normally being loss of vacuum in the glass envelope or the evacuated heat pipe loosing its vacuum and thus failing to move any heat. Quality components should last the distance. The same can be said for flat plate collectors, here in NZ many commercial systems over the past 10 years have failed completely, see Solar Water Heating - Corrosion and Performance Issues in New Zealand

At least DIY flat panels can be easily built from quality components that you have control over, this cannot be said for cheaper commercial systems.

Solar Mike is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:08 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design