You must have had it set to Moscow, OH, because Moscow RS (UUEE), at 56°N, had 8805 HDD (ref 65°F) last year. That reconciles nicely with the 20" of wall thickness.

56°N... that's awfully close to the arctic circle. It has to be tough to be passive when the sun is 10° above the horizon at noon on the solstice.

RobertSmalls is offline   Reply With Quote
Old 04-28-11, 07:43 PM   #32
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by RobertSmalls View Post
You must have had it set to Moscow, OH, because Moscow RS (UUEE), at 56°N, had 8805 HDD (ref 65°F) last year. That reconciles nicely with the 20" of wall thickness.

56°N... that's awfully close to the arctic circle. It has to be tough to be passive when the sun is 10° above the horizon at noon on the solstice.
This is the data set I used:
>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> >>>
Description:,"Fahrenheit-based 5-year-average (2006 to 2010) heating degree days for a base temperature of 65F"
Source:,"www.degreedays.net (using temperature data from www.wunderground.com)"
Accuracy:,"No problems detected"
Station:,"Airport: Moscow Vnukovo, RS (37.27E,55.65N)"
Station ID:,"UUWW"

,HDD
Jan,1517
Feb,1376
Mar,1072
Apr,663
May,325
Jun,160
Jul,97
Aug,134
Sep,353
Oct,694
Nov,979
Dec,1253
Total,8623 <===============
>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>>> >>>

...try something else.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 04-28-11, 08:40 PM   #33
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
The second-last data point here, the one that does not fit the curve, corresponds to Moscow and should have around 9000HDD, not 4500. I bet your correlation coefficient would go from "meh" to "aha!" if you were to correct that. That's all I'm getting at here.
RobertSmalls is offline   Reply With Quote
Old 04-28-11, 10:00 PM   #34
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

NOTE: data error in post # 26 has been repaired

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 04-29-11, 01:40 AM   #35
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 960
Thanks: 188
Thanked 110 Times in 86 Posts
Default

Quote:
Originally Posted by RobertSmalls View Post
56°N... that's awfully close to the arctic circle. It has to be tough to be passive when the sun is 10° above the horizon at noon on the solstice.
The angle at which the sun's rays hit the window is much closer to perpendicular. But yes, the sun is above the horizon for no more than 6-7 hours, plus the rays of sunlight have to travel through a thicker layer of atmosphere. Here in Warsaw (52°N) the amount of energy from the sun in the winter is 4 times less than in the summer (~350 W/m2 vs ~1300 W/m2). I believe that passivhaus design for locations close to the polar circle is geared towards thermal mass, to hold as much of summer's/autumn's heat for as long as possible, and towards using heat produced by the inhabitants, cooking, and waste heat from electronics. "Don't unplug that wall wart or we'll freeze!"
__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
Old 04-29-11, 03:56 PM   #36
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
NOTE: data error in post # 26 has been repaired

-AC_Hacker
Aha! An r-value (the correlation coefficient, not the insulation value) like that proves that Passivhaus wall thickness is in fact linear with annual HDD.

Looking at the third plot, I see I fall in with most of the rest of the EcoRenovators, around 6000HDD/yr. This suggests an insulation thickness of 14". Hmm, that's an awful lot.

AC_Hacker, you mentioned that you would do cellulose instead of foam if you could do it over again. Would you recommend cellulose over a CFC-free (e.g. CO2) blown foam as well?

Quote:
Originally Posted by Piwoslaw View Post
"Don't unplug that wall wart or we'll freeze!"
Hah... I've been there.



Viceroy have sent me a pricelist and specification sheet for their houses... they also mentioned that their houses are well sealed, and many customers install a ventilation heat recovery system. I like everything I've seen about them so far, except the fact that new construction is a fair bit more expensive than buying used. But the opportunity to get the house I want, in the right location, sited correctly, is pretty compelling.
RobertSmalls is offline   Reply With Quote
Old 04-29-11, 04:38 PM   #37
S-F
You Ain't Me
 
S-F's Avatar
 
Join Date: Nov 2009
Location: Northampton MA
Posts: 662
Thanks: 6
Thanked 71 Times in 58 Posts
Default

Quote:
Originally Posted by RobertSmalls View Post
Aha! An r-value (the correlation coefficient, not the insulation value) like that proves that Passivhaus wall thickness is in fact linear with annual HDD.

Looking at the third plot, I see I fall in with most of the rest of the EcoRenovators, around 6000HDD/yr. This suggests an insulation thickness of 14". Hmm, that's an awful lot.

AC_Hacker, you mentioned that you would do cellulose instead of foam if you could do it over again. Would you recommend cellulose over a CFC-free (e.g. CO2) blown foam as well?

Hah... I've been there.



Viceroy have sent me a pricelist and specification sheet for their houses... they also mentioned that their houses are well sealed, and many customers install a ventilation heat recovery system. I like everything I've seen about them so far, except the fact that new construction is a fair bit more expensive than buying used. But the opportunity to get the house I want, in the right location, sited correctly, is pretty compelling.
Just putting this out there:

You seem to be looking for something particular.

You give the word and I'll be there in 3 days with a 16 man framing crew to do your job for less than what you are looking at. And it will be done right.

PM me if you want.

Last edited by S-F; 04-29-11 at 04:45 PM..
S-F is offline   Reply With Quote
Old 05-02-11, 09:57 PM   #38
MN Renovator
Less usage=Cheaper bills
 
MN Renovator's Avatar
 
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 939
Thanks: 41
Thanked 116 Times in 90 Posts
Default

Quote:
Originally Posted by RobertSmalls View Post
With some spray foam insulations claiming twice the stabilized R-value of cellulose, it might be doable with 8-9" walls with no thermal bridging, e.g. with steel studs. I wonder, would the increased cost of spray foam insulation be made up for by the savings in lumber, framing labor, window and door trim, and per-square-foot taxes?

Vacuum insulated triple glazing and 18" walls would be nice, but I view them as very expensive toys. I'm inclined to go with a very efficient, 2x6-framed, well sealed house with ventilation heat recovery and good, south-facing double-pane windows. Who knows; it might be passive nine months out of the year, and pretty close in August, January, and February.
There may be an increased cost in spray foam insulation if you use it but if you go with Structural Insulated Panels with new construction, you avoid the framing labor, get a thinner wall than using fiberglass or cellulose. Since it is rigid foam inside, you have a built-in vapor barrier and air sealing that is hard to mess up too. Doing a little reading to see if these can be bought thick and it seems Wikipedia mentions that they can be 12" thick. If the stuff is polystyrene, which I think is R-5 per inch, it would be about R-60, right? Since there is no framing members, no thermal bridge, you would just need to worry about the air sealing and thermal bridging of penetrations like doors and windows.

It was my impression after watching a television show on prefab houses about 5 years ago, Build one place, ship somewhere else and assemble. The show I was watching explained how instead of using nails and screws, attaching components with adhesives were used instead to speed up the process. I thought it was fascinating. I thought they used SIPs in the construction.
MN Renovator is offline   Reply With Quote
Old 05-03-11, 06:32 AM   #39
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

http://www.ecosteel.com/tech/insulatedpanels.pdf

EcoSteel offer a 4" structural insulated panel with R-14, and a 3" insulated panel with R-24. A 10" stack of SIP + IP + IP would have R-62, and a 13" stack would have R-86. As EcoSteel are happy to remind you, these are "whole wall performance" figures, including thermal bridging effects. So a 12" SIP would be a serious performer, perhaps even overkill for any application other than a northern Passivhaus.
RobertSmalls is offline   Reply With Quote
Old 05-03-11, 09:49 AM   #40
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by RobertSmalls View Post
AC_Hacker, you mentioned that you would do cellulose instead of foam if you could do it over again. Would you recommend cellulose over a CFC-free (e.g. CO2) blown foam as well?
Yes.

Fine Homebuilding mag from the early part of this year, has an article on foam + cellulose, and they even talk about the minimum foam thickness required to prevent condensation.

-AC_Hacker

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:26 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design