Old 04-06-13, 09:41 AM   #1
kfreeman
Lurking Renovator
 
Join Date: Apr 2013
Location: Sonora,Ky
Posts: 1
Thanks: 0
Thanked 0 Times in 0 Posts
Default Old Janitrol heat pump

I have an old Janitrol heat pump that keeps burning out the compressor start capacitor. I can replace and it will melt one of the red wires from compressor and damage the capacitor. What would be a good approach to troubleshooting this problem? Could I poosibly be using too small a capacitor. A service person from a local company replaced the first one and I have had trouble ever since.

kfreeman is offline   Reply With Quote
Old 04-06-13, 12:00 PM   #2
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by kfreeman View Post
I have an old Janitrol heat pump that keeps burning out the compressor start capacitor.

NOTE: If you try to repair your own heat pump, you might kill yourself or destroy your heat pump... only a fool would proceed.

* * *

Before you mess with your heat pump unit, be absolutely sure that power has been cut. Turned "OFF" is not good enough.

The capacitor thing isn't rocket science. The capacitor is there to give the single-phase compressor an initial startup kick... after that, it does nothing. In general, all compressors of a particular Tonage rating (1/2-Ton, 1-Ton, 3-Ton, etc.) and the same voltage (110v, 220v) should be pretty much the same, so their starting capacitors will be pretty much equivalent.

If you can get hold of a parts list for your unit, it will spell out the correct part... that is the part it should have.

Otherwise, the capacitor specs are dictated by the compressor's requirements. That compressor would be used in many different heat pumps, all of them using pretty much the same capacitor. The capacitor call-out for any of them should do it.


In many units, the same capacitor will be doing double duty to help the compressor to start and also to help the fan to start, so it's really two separate capacitors of different sizes in one can. There is the possibility that your previous repairman switched the leads incorrectly. I would think that the smaller capacitance should go to the fan and the larger capacitance should go to the compressor. You could follow the wires to see where they go to. If you are sure that the capacitor was correctly hooked up correctly, copy that hook-up. If you are not sure, find a schematic.

As a last gasp, the cap will be specified by it's capacitance and also for it's voltage. you might get one for a higher voltage... the capacitance should remain the same (assuming your tech got that part right).

So, you really need to find out the correct part call-out before you start subbing in different parts.

Finally, and least likely, your compressor could be dying and drawing too much current... in which case, it should be given a proper burial...


R.I.P.


-AC
Attached Thumbnails
Click image for larger version

Name:	capacitor.jpg
Views:	3574
Size:	17.5 KB
ID:	3133   Click image for larger version

Name:	skull.gif
Views:	1508
Size:	7.2 KB
ID:	3134   Click image for larger version

Name:	RIP.gif
Views:	1224
Size:	9.5 KB
ID:	3135  
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 04-06-13 at 04:52 PM..
AC_Hacker is offline   Reply With Quote
Old 04-06-13, 03:58 PM   #3
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Replace it with one of the same capacitance and a higher voltage rating. Also check the start relay if there is one.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 04-07-13, 12:41 PM   #4
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

AC makes great points with excess current draw clearly causing the red lead to burn out.

I would certainly test the capacitor and this is where the "death head" comes up.

Capacitors store charge and a good capacitor can store a REAL hefty charge for several days (or longer). Before you do anything, remove the AC power and short the capacitor terminals to each other. You should see a big spark and the snap of a high current pulse.

When uou can't find the exact capacitance value, get two capactors and put them in parallel. This placement allows you to simply add capacitances. The voltage rating is not critical so long it is ABOVE the stated voltage on the original capacitor. In this application, it is NOT critical if the total capacitance is a bit larger, the key is not to have it be too small.

Now the interesting way to test . . . . yeah, not with small kids or animals around.

Disconnet the leads to the compressor and put main voltage (120 240, etc) on the unit. Most times this is via a circuit breaker. Just a minute or two is sufficient - then turn off power.

Now get an insulated screwdriver and short the terminals of the capacitor together. The louder the snap, and the vigorous the light pulse indicates the amount of stored energy. A VERY quick and dirty test, but if there is a weak spark, thern you know the capacitor is likely bad.

In enginering grad school, we would take a much smaller capacitor, wrap the leads around the non-metalic capacitor body (leads not touching) charge it up - and then toss it to someone who just walked in to "catch".

The auditory responses were quite impressive . . . . .


Steve

__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:27 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design