03-25-14, 08:28 PM | #271 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
Does this thing work well? It's got good 5 star reviews.
Compressor Saver CSR U1 Hard Start Capacitor http://www.amazon.com/Compressor-Sav...productDetails http://ecorenovator.org/forum/attach...1&d=1395797278 Last edited by buffalobillpatrick; 03-25-14 at 08:55 PM.. |
03-25-14, 09:08 PM | #272 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
My Copeland compressor ZP24K5EPFV830
RLA = 13.4A, LRA = 64A, Copeland stays Inrush current = LRA Last edited by buffalobillpatrick; 03-26-14 at 01:33 PM.. |
03-26-14, 03:51 AM | #273 |
Supreme EcoRenovator
|
Straight from emerson:
http://www.emersonclimate.com/Docume...TLE_Series.pdf I like the supco hard start kits myself. They use a potential relay to switch the start cap. If you are going to use a VFD, you won't need a hart start kit. |
The Following User Says Thank You to jeff5may For This Useful Post: | buffalobillpatrick (03-26-14) |
03-26-14, 05:19 AM | #274 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Hard start kits are used for pots that are outdoors in the cold or have had design issues where they are having trouble getting going. A well designed system won't need it.
A soft start is better because it is used where you have a limited current supply or low line voltage such as in some residential situations but, as Jeff says, there is no need for either if you have a VFD. Unless you have an old 60Amp service and don't like dimming lights when the pot starts, you shouldn't need either one. |
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (03-26-14) |
03-26-14, 08:26 AM | #275 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
If you do get a hard start kit, the 5-2-1 (or any based on a potential relay) would be your best bet. It's unlikely you'll actually need one as R290 would mean less pressure to start against.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
The Following User Says Thank You to NiHaoMike For This Useful Post: | buffalobillpatrick (03-26-14) |
05-25-14, 05:49 PM | #276 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
Mikesolar, on page 12 your:
"3.65gpm with a 20F dT is 36,500btu x 2 loops is 73Mbtu. I don't know where 180Mbtu comes from" We are looking at this wrong, I want the delta-T between the solar tank / water coming out of pex HX to be as SMALL as possible. I reduced the flow to 2gpm based on the small 53W 240VAC .22A pumps I bought. Head Loss @ 2gpm through 3/4" pex 250' long: HL = K x C x L x F^1.75 K = .0034, C = .933, L = 250, F = 2gpm (2^1.75 = 3.3636) HL = 2.67' Based on Gary's 20*F delta-T @ 2gpm with 300' of 1" pex, I should get about 15.6*F delta-T So if my heat pump takes 10*F (10*F is just a guess) out of this HX 4 x 500 x 10 = 20,000 btu |
05-25-14, 06:09 PM | #277 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
The dT through the HP is totally different than through the load (floor) and having the buffer tank means the two are hydraulicly disconnected. You can run the HP and the floor at different flow rates. You want to have a particular drop over a set length for comfort reasons. If you have set load and you are trying to have only a really low dT, your flow rate will have to be ridiculously high especially for the standard 250' loop length. There is nothing wrong with 15 or 16F dT or anywhere from 10F to 25F but remember that if you double the pump speed you will quadruple the needed pump power. It is a balancing act.
|
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (05-25-14) |
05-25-14, 06:48 PM | #278 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
"We are looking at this wrong, I want the delta-T between the solar tank / water coming out of pex HX to be as SMALL as possible."
I'm not talking about the floors, I'm talking about the pex HX inside the 1,000g solar tank that will feed the HP. |
05-25-14, 06:55 PM | #279 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Sorry about that. 6F is a reasonable dT for a HP but some of this will be trial and error and I doubt 2 GPM will be enough to provide the proper cooling for the HP. It is typically around 3GPM/ton
|
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (05-25-14) |
05-25-14, 07:31 PM | #280 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
It will be 2gpm minimum in each loop, possibly 3gpm in each of the 2 loops, sooo 4-6gpm total.
I plan to put 2 of these 53W pumps in series on the evaporator and 2 in series on the condenser. I got them for $40 each + shipping Last edited by buffalobillpatrick; 05-25-14 at 07:33 PM.. |
|
|