Old 03-25-14, 08:28 PM   #271
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Does this thing work well? It's got good 5 star reviews.
Compressor Saver CSR U1 Hard Start Capacitor

http://www.amazon.com/Compressor-Sav...productDetails



http://ecorenovator.org/forum/attach...1&d=1395797278

Attached Thumbnails
Click image for larger version

Name:	IMG_2666.jpg
Views:	730
Size:	500.9 KB
ID:	4190  

Last edited by buffalobillpatrick; 03-25-14 at 08:55 PM..
buffalobillpatrick is offline   Reply With Quote
Old 03-25-14, 09:08 PM   #272
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

My Copeland compressor ZP24K5EPFV830
RLA = 13.4A, LRA = 64A, Copeland stays Inrush current = LRA

Last edited by buffalobillpatrick; 03-26-14 at 01:33 PM..
buffalobillpatrick is offline   Reply With Quote
Old 03-26-14, 03:51 AM   #273
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Straight from emerson:
http://www.emersonclimate.com/Docume...TLE_Series.pdf

I like the supco hard start kits myself. They use a potential relay to switch the start cap.

If you are going to use a VFD, you won't need a hart start kit.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (03-26-14)
Old 03-26-14, 05:19 AM   #274
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Hard start kits are used for pots that are outdoors in the cold or have had design issues where they are having trouble getting going. A well designed system won't need it.

A soft start is better because it is used where you have a limited current supply or low line voltage such as in some residential situations but, as Jeff says, there is no need for either if you have a VFD.

Unless you have an old 60Amp service and don't like dimming lights when the pot starts, you shouldn't need either one.
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (03-26-14)
Old 03-26-14, 08:26 AM   #275
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

If you do get a hard start kit, the 5-2-1 (or any based on a potential relay) would be your best bet. It's unlikely you'll actually need one as R290 would mean less pressure to start against.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (03-26-14)
Old 05-25-14, 05:49 PM   #276
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Mikesolar, on page 12 your:

"3.65gpm with a 20F dT is 36,500btu x 2 loops is 73Mbtu. I don't know where 180Mbtu comes from"

We are looking at this wrong, I want the delta-T between the solar tank / water coming out of pex HX to be as SMALL as possible.

I reduced the flow to 2gpm based on the small 53W 240VAC .22A pumps I bought.

Head Loss @ 2gpm through 3/4" pex 250' long:

HL = K x C x L x F^1.75
K = .0034, C = .933, L = 250, F = 2gpm (2^1.75 = 3.3636)
HL = 2.67'

Based on Gary's 20*F delta-T @ 2gpm with 300' of 1" pex,
I should get about 15.6*F delta-T

So if my heat pump takes 10*F (10*F is just a guess)
out of this HX 4 x 500 x 10 = 20,000 btu
buffalobillpatrick is offline   Reply With Quote
Old 05-25-14, 06:09 PM   #277
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

The dT through the HP is totally different than through the load (floor) and having the buffer tank means the two are hydraulicly disconnected. You can run the HP and the floor at different flow rates. You want to have a particular drop over a set length for comfort reasons. If you have set load and you are trying to have only a really low dT, your flow rate will have to be ridiculously high especially for the standard 250' loop length. There is nothing wrong with 15 or 16F dT or anywhere from 10F to 25F but remember that if you double the pump speed you will quadruple the needed pump power. It is a balancing act.
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (05-25-14)
Old 05-25-14, 06:48 PM   #278
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

"We are looking at this wrong, I want the delta-T between the solar tank / water coming out of pex HX to be as SMALL as possible."

I'm not talking about the floors, I'm talking about the pex HX inside the 1,000g solar tank that will feed the HP.
buffalobillpatrick is offline   Reply With Quote
Old 05-25-14, 06:55 PM   #279
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Sorry about that. 6F is a reasonable dT for a HP but some of this will be trial and error and I doubt 2 GPM will be enough to provide the proper cooling for the HP. It is typically around 3GPM/ton
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (05-25-14)
Old 05-25-14, 07:31 PM   #280
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

It will be 2gpm minimum in each loop, possibly 3gpm in each of the 2 loops, sooo 4-6gpm total.

I plan to put 2 of these 53W pumps in series on the evaporator and 2 in series on the condenser. I got them for $40 each + shipping


Last edited by buffalobillpatrick; 05-25-14 at 07:33 PM..
buffalobillpatrick is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:01 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design