Old 02-18-15, 12:45 PM   #31
buffalobillpatrick
I convert function input parameter "float PSI" into array index:
//convert PSI to array index
work = ((PSI - 30.0) / 10.0);
I = work; //drop decimals to get array index,
//I is an int (whole number) work is a float (decimals)
I use the decimal portion to interpolate between array elements:
decimals = work - I; //restore decimals for interpolation between array points
Val = R290_Saturation_Temp[I]; //get array value
Next_val = R290_Saturation_Temp[I+1]; //get Next array value
Span = Next_val - Val; //Calc Span
Saturation_Temp = Val + (Span * decimals);//interpolate between array points
Code:
float calc_R290_Saturated_Temp(float PSI, int Which_sensor)
//Array element [0]  contains Saturation_Temp *F for 30PSI,
//Array element [1]  contains Saturation_Temp *F for 40PSI,...................>
//Array element [27] contains Saturation_Temp *F for 300PSI,
//Array element [28] contains Saturation_Temp *F for 310PSI
float R290_Saturation_Temp[] =
     {7.93, 18.80, 28.42, 36.91, 44.59, 51.63, 58.13, 64.21, 69.90, 75.27,
      80.35, 85.18, 89.78, 94.19, 98.41, 102.50, 106.40, 110.20, 113.80,
      117.30, 120.80, 124.10, 127.30, 130.40, 133.50, 136.50, 139.40, 142.20,
      145.00};
float Val, Next_val, Span, Saturation_Temp, decimals, work, low, hi;
int I;
  if (Which_sensor == Sensor_150){ low = 30.0; hi = 150.0; }
  else{ /*Sensor_300*/             low = 60.0; hi = 300.0; }
  if ((PSI >= low) && (PSI <= hi)) //Bounds check
  // in bounds, continue
                         //I is an int (whole number) work is a float (contains decimals)
  return (Saturation_Temp);
  }  //end if in bounds
  else {return (-1);}       // error return, out of bounds
}  // end calc_R290_Saturated_Temp
Old 02-18-15, 01:00 PM   #32
Default PT Chart
BBP,
OK, it didn't take as long as I thought, I had saved data from before.
Here is the heart of the matter, if you need me to make it into a line of code, let me know.
4th Degree Polynomial Fit: y=a+bx+cx^2+dx^3...
Coefficient Data:
a = -4.03085122205E+001
b = 1.81496452942E+000
c = -1.01201804003E-002
d = 3.05234258195E-005
e = -3.37963005786E-008
Right now, mandolin is calling me...
buffalobillpatrick (02-18-15)
Old 02-18-15, 01:23 PM   #33
Originally Posted by buffalobillpatrick View Post
"The Emerson EX2 pulse modulated electric valve is an electrically driven expansion valve that provides precise temperature control. It is designed for use with R-12, R-22,
R-134a, R-404A, R-407C and R-502 refrigerants. - See more at: http://www.emersonclimate.com/en-US/products/valves/expansion_valves/Pages/electronic_expansion_valve.aspx#sthash.AodE1Cgy.dp uf"
Did anyone read the link in post #21 ?
Yup, and I know it is made for liquid injection purposes. I haven't seen any reference to it being used as a main EEV. It needs the solenoid to activate it and it is a normally closed valve like most solenoid. Without power to it, it will be closed. Not what you want from an EEV but fine for injection.
Old 02-18-15, 01:32 PM   #34
Yep, EEV for HVAC must be stepper (or servo, which would be too expensive, with no added benefit).
Tell me more about what you have in mind for the EEV?
There is a way to control a heat pump based solely on subcooled liquid temp. I would like to try to make the EEV measure the subcooled temp just before it goes to the evap. The control only has to look at one internal temp (liquid line) and try to compare it to the outdoor ambient (and I am not sure this is necessary) to adjust the valve.
It is called a flooded evaporator.
Old 02-18-15, 01:40 PM   #35
BBP,
I haven't read every post here, but I think that you need an incrementally-variable EEV.
The PWM thingy wants square-wave input with varying duty cycle, in order to 'mimic' analog control.
I think that an incrementally variable (analog) valve would be better.
The EEVs I've seen use a little teeny stepper motor that turns the adjustment screw.
Old 02-18-15, 01:42 PM   #36
BBP,
Yes, I have one in my hands. A Sporlan SER-B
Old 02-18-15, 01:45 PM   #37
Then on with the show...
Old 02-18-15, 01:47 PM   #38
Now to just get a program that will monitor subcooling and adjust the valve accordingly. It also has to open it a bit at start up till the temps settles.
Old 02-18-15, 02:01 PM   #39
buffalobillpatrick
A/C did I get this right?
How did you come up with such an accurate formula??
Code:
float calc_R290_Saturated_Temp(float x)
float a = -4.03085122205E+001;
float b = 1.81496452942E+000;
float c = -1.01201804003E-002;
float d = 3.05234258195E-005;
float e = -3.37963005786E-008;
 return (a + (b * x) + (c * x*x) + (d * x*x*x) + (e * x*x*x*x));
If so, either the formula or the table are off by a little bit.
OR Arduino floating point math is a bit in-accurate.
I would bet on this option, as Arduino does floating point by actually doing integer add operations.
This one line of code: y = ( a + (b * x) + (c * x*x) + (d * x*x*x) + (e * x*x*x*x));
Produces 348 bytes of Arduino object code.
At 30PSI: formula = 5.83*F, table = 7.93*F, difference = -2.1*F
At 300PSI: formula = 143.75*F, table = 142.2*F, difference = +1.55*F
Old 02-18-15, 06:05 PM   #40
Here is your datasheet for the ex2. It seems to be a damped solenoid valve with a period of about 15 seconds from full shut to full on. A 6 second period on a pwm would not make it walk around much between pulses.
http://www.emersonclimate.com/europe...EX2__35016.pdf
The EX3 and up to EX8 are true stepper motor driven designs. All these EX series valves seem to be PRICEY, if they can be found.