EcoRenovator  

Go Back   EcoRenovator > Improvements > Other Improvements
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 01-14-18, 10:44 PM   #1
Mukiwa
Lurking Renovator
 
Join Date: Sep 2015
Location: BC
Posts: 16
Thanks: 2
Thanked 0 Times in 0 Posts
Default Help me plan my DIY wood stove water heater

We are building a house with an insulated and hydronicly heated concrete slab as our floor and heat source. It will be heated with a propane boiler but I want to be able to hook it up to my woodstove in the future. Unfortunately the woodstove is not located beside the mechanical room so I have to run water line through the slab from the woodstove to the mechanical room. I will not be hooking up right away but I have to have the pipe in the slab before because once we pour the concrete I won’t have access to install a pipe later (obviously). What type of pipe should be used in the slab?

A few options:

Pex - I’m worried pex will melt with the heat of the woodstove,
Steel - I don’t really want to have threaded fittings where I can’t access them if they start leaking or something
Copper - $$$$$$

What would you use? And what size should the pipe be?

Mukiwa is offline   Reply With Quote
Old 01-15-18, 03:41 AM   #2
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

Pex. I think it's rated to something like 150°F at 100psi.
You could always make the first 5 or 10 feet out of copper incase of a rush of really hot water.
oil pan 4 is offline   Reply With Quote
Old 01-15-18, 09:47 PM   #3
Mukiwa
Lurking Renovator
 
Join Date: Sep 2015
Location: BC
Posts: 16
Thanks: 2
Thanked 0 Times in 0 Posts
Default

I wasn’t worried about the water temp but more the steel a loop running thru the woodstove conducting heat to the pex connection. How far away from the woodstove would the pipe get hot enough to melt pex... i am looking at the Hilkoil retrofit coil if anyone on here has any experience with this type of water heater.
Mukiwa is offline   Reply With Quote
Old 01-17-18, 12:08 AM   #4
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Mukiwa View Post
Pex - I’m worried pex will melt with the heat of the wood stove,
I think your concerns are well founded regarding PEX and your wood stove. PEX has a maximum temperature rating of 180 F. After that it's bursting strength drops. I have seen photos of burst PEX that was used for solar collectors.

Your gas boiler probably has built-in precautions to make sure the PEX temp doesn't get to the danger zone. I have no information about what water temperature you will get from your wood stove. But you should be aware of possible problems. In my experience, the heat from a wood stove can vary quite a bit.

Quote:
Originally Posted by Mukiwa View Post
Steel - I don’t really want to have threaded fittings where I can’t access them if they start leaking or something
Steel buried in concrete will eventually have problems. History is on your side!

Quote:
Originally Posted by Mukiwa View Post
Copper - $$$$$$
Copper buried in concrete is not good either because of corrosion.

Best of luck,

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 01-17-18, 03:30 PM   #5
Mukiwa
Lurking Renovator
 
Join Date: Sep 2015
Location: BC
Posts: 16
Thanks: 2
Thanked 0 Times in 0 Posts
Default

So all my ideas are a no go lol.. Maybe some conduit buried under the slab with copper pipe inside... I would probably be ok with a copper-pex connection under the slab after 10-15’ if it was in a 3” conduit that I could pull out and fix if there were any issues.. I’m thinking 7/8 or 1” Copper depending on what size it come in. I don’t know if pex goes that big so I may even have to use polly
Mukiwa is offline   Reply With Quote
Old 01-17-18, 03:34 PM   #6
Mukiwa
Lurking Renovator
 
Join Date: Sep 2015
Location: BC
Posts: 16
Thanks: 2
Thanked 0 Times in 0 Posts
Default

I’m pretty sure you only need 15-20 PSI for hydronic so I think over heating and bursting would be less of an issue but no one wants issues. I also don’t have endless funds and large diameter Copper isn’t cheap.. I probably have to go 25-30’ from the woodstove to the mech. room which isn’t ideal but it is what it is.
Mukiwa is offline   Reply With Quote
Old 10-14-20, 08:06 PM   #7
WillyP
Helper EcoRenovator
 
Join Date: Jul 2020
Location: Virginia
Posts: 30
Thanks: 8
Thanked 3 Times in 3 Posts
Default

I am curious how this turned out. Did you go with copper?
I just want to throw out there. I live in a seventy year old house with copper pipes inside the slab (for radiators) there has never been a problem with corrosion.
WillyP is offline   Reply With Quote
Old 10-26-20, 08:23 PM   #8
nibs
Apprentice EcoRenovator
 
Join Date: Jun 2010
Posts: 206
Thanks: 1
Thanked 18 Times in 17 Posts
Default

Put in a header tank on the hot side of the fire place & split the supply side line with a tee into the hot line with a water temperature controller. But the big danger is boiling the water in the firebox, that could run away and really hurt someone.

nibs is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:05 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design