Old 12-28-14, 02:11 PM   #301
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

I am not using the paddle wheel flow sensors, as I felt that they are trouble prone.
I'm using the analog pressure sensors that I referenced in post #232 above on both Source & Load water pumps.


Last edited by buffalobillpatrick; 12-28-14 at 02:14 PM..
buffalobillpatrick is offline   Reply With Quote
Old 12-28-14, 06:54 PM   #302
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by buffalobillpatrick View Post
I am not using the paddle wheel flow sensors, as I felt that they are trouble prone.
I'm using the analog pressure sensors that I referenced in post #232 above on both Source & Load water pumps.
I think this is a great idea. No moving parts.

Unless you need to do calculations that require precise flow measurement, like precise COP, knowing exact flow rate just isn't needed.

I suppose you could get an approximate measure through some testing and determine how pressure relates to flow in your system.

The programming for pressure sensors should be much easier, too.

Best,

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
buffalobillpatrick (12-29-14)
Old 12-28-14, 08:00 PM   #303
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default I sure missed that one!

Quote:
Originally Posted by buffalobillpatrick View Post
One of these on pipe at pump output:

30PSI Pressure Transducer or Sender for Oil Fuel Diesel Gas Water Air | eBay


Take pressure reading with pump off, turn on pump, take a 2nd pressure reading, calculate Delta, calibrate with good known flow.
That's a fuel pressure sensor! For what kind of vehicle might I ask? I bet you could find one of those bad boys at autozone for 8.99 if you knew what kind of car it went in. Ingenious.

I must have been working nonstop that month, I'm still playing catch-up today.

EDIT: OK, I'm caught up now. And here come the questions:

So for the water-source variant, the analog fuel pressure type sensor will be used for proving coolant flow downstream of the heat exchanger, yes? To me, this means an interrupt will not be needed to count flow pulses, which will greatly simplify debugging. A simple periodic sampling can be done instead, which can be used during the start-up routine to determine a baseline setting while the compressor is locked out.

Another detail comes to mind: do you still want temperature sensors in the same places as these pressure sensors also? And in other places also? Sounds like a lot of analog pins.

Last edited by jeff5may; 12-28-14 at 09:20 PM..
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (12-29-14)
Old 12-29-14, 10:01 AM   #304
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

No interrupt needed.

I measure 6 temperatures around the HP refrigerant loop:
1. Compressor Out / Condenser In
2. Condenser Out / IHX Hi Side In
3. IHX Hi Side Out / TXV In
4. TXV Out / Evaporator In
5. Evaporator Out / IHX Lo Side In
6. IHX Lo Side Out / Suction Line to Compressor

I also measure 4x water temps. Source In & Out, Load In & Out

Analog 0-5vdc pressure sensor on output pipe from water pump.
Code Steps:
1. With pump off, measure static OFF pressure.
2. turn on pump, wait X seconds, measure ON pressure.
3. The pressure delta between these 2 readings represents the plumbing back-pressure (head) that your water pump & plumbing stabilize at.

1 psi = 2.31 feet of head

This delta pressure won't vary unless pump stops working or a blockage condition.

My code, which I don't have access to on Holiday road trip, verifies that the pressure delta stays +- 10% for each water pump.

This is a Go/Nogo test, actual water flow is unknown, so COP can't be determined.

Last edited by buffalobillpatrick; 12-29-14 at 10:40 AM..
buffalobillpatrick is offline   Reply With Quote
Old 12-29-14, 11:05 AM   #305
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

16 analog sensors can be read via the 16 channel Mux chips that I have been using, but I have had one of them go bad. So I got a couple of Arduino Mega's to play with.
buffalobillpatrick is offline   Reply With Quote
Old 12-29-14, 04:01 PM   #306
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by buffalobillpatrick View Post
No interrupt needed.

I measure 6 temperatures around the HP refrigerant loop:
1. Compressor Out / Condenser In
2. Condenser Out / IHX Hi Side In
3. IHX Hi Side Out / TXV In
4. TXV Out / Evaporator In
5. Evaporator Out / IHX Lo Side In
6. IHX Lo Side Out / Suction Line to Compressor

I also measure 4x water temps. Source In & Out, Load In & Out

Analog 0-5vdc pressure sensor on output pipe from water pump.
Code Steps:
1. With pump off, measure static OFF pressure.
2. turn on pump, wait X seconds, measure ON pressure.
3. The pressure delta between these 2 readings represents the plumbing back-pressure (head) that your water pump & plumbing stabilize at.

1 psi = 2.31 feet of head

This delta pressure won't vary unless pump stops working or a blockage condition.

My code, which I don't have access to on Holiday road trip, verifies that the pressure delta stays +- 10% for each water pump.

This is a Go/Nogo test, actual water flow is unknown, so COP can't be determined.
BBP,

I'm curious why you want all the temp sensors? Seems like maybe 1 or 2 would cover most hazard situations. Are the rest for general data logging?

Also, it seems to me, regarding pressure sensors, that after the 'time period' the system should shut down to avoid damaging the circ pumps.

However, there needs to be some kind of over-ride provided through software or hardware, so that troubleshooting can be performed.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
buffalobillpatrick (12-29-14)
Old 12-29-14, 07:10 PM   #307
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

The 6 refrigerant sensors mostly are for my curiosity, I want to adjust Superheat via TXV measured after Lo side IHX to about 30*C and measure Sub-cooling.

I will have standard high & low pressure cut-out switches.

A/C Sure, shut down if water pump is not working as expected.

Last edited by buffalobillpatrick; 12-29-14 at 07:23 PM..
buffalobillpatrick is offline   Reply With Quote
Old 12-30-14, 03:16 AM   #308
takyka
Helper EcoRenovator
 
Join Date: Jul 2014
Location: Hungary
Posts: 34
Thanks: 0
Thanked 16 Times in 10 Posts
Default flow sensor

I'm using a flow sensor for one year now in my heatpump. It was running end of last winter, for one month during summer (for cooling). Was stopped for monthes. It was running from mid October, without any problems.

Suddenly it stopped to send out pulses a month ago. I tought, that's all...
I decided to unmount it out of curiosity, to see what went wrong. I found a small stone approx. 8mm jammed the padles. I don't know where it come from. Material is like chalk. Othervise the sensor looks like new. After reinstallation, sensor works flawlessly. If it happens again, I will install some rough filter to pipes.

To be ontopic. For me, the flow information is a must to be able to calculate heating power. It's mandatory to finetune the HP to maximum efficiency or to find problems. I have some nice graphs and conclusions to come...
Attached Thumbnails
Click image for larger version

Name:	blocking_stone.jpg
Views:	418
Size:	150.6 KB
ID:	4904  

Last edited by takyka; 12-30-14 at 03:21 AM..
takyka is offline   Reply With Quote
The Following User Says Thank You to takyka For This Useful Post:
buffalobillpatrick (12-30-14)
Old 12-30-14, 10:52 AM   #309
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Actually, flow can be approximated closely using a pump flow/head performance chart and your measured output pressure reading.

Many common pumps like Grundfos, Taco, etc. provide these charts.
1psi = 2.31' of head

Find your measured pressure on the pump curve & read flow on X axis.

Last edited by buffalobillpatrick; 12-30-14 at 10:56 AM..
buffalobillpatrick is offline   Reply With Quote
Old 01-05-15, 10:51 AM   #310
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

I just figured out how determine Flow for a Taco 008 pump from Head pressure in 12 lines of Arduino Code.

Uses an array & Interpolates between elements for higher accuracy.

I will post code after I have access to my computer back in Colorado.


Last edited by buffalobillpatrick; 01-07-15 at 09:19 AM..
buffalobillpatrick is offline   Reply With Quote
The Following User Says Thank You to buffalobillpatrick For This Useful Post:
AC_Hacker (01-06-15)
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:24 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design