Hey guys, I've been very interested in water source/ ground source cooling (not much heating needed down here, but it would be nice) for quite a while and A/C hacker has had me highly interested for years.

That said the relatively high labor barrier (time) of digging up a yard to bury a loop field has kept me out of the game. However, my camp is located on a small bayou Bayou - Wikipedia, the free encyclopedia that always flows a little, but often a bit and during large rain events a lot, never ever freezes, feels cool year round (sorry no numbers yet), is about 20 feet horizontal and 15 feet vertical from existing window units. A loop field in the bayou is essentially out of the question due to constant dredging, and the crawfish farmers across the bayou dropping their pumps on the bottom.

That leaves me with pumping bayou water to the A/C's and returning it with some of the camps heat. Unfortunately, the water is loaded with mud/ silt/ stuff that I've been afraid would plug up a conventional brazed plate heat exchanger pretty quickly requiring attention that I would like to avoid.

However I know that boats with water cooled A/c's often operate in similar water conditions, so what are they using? Quick google search lead me to these guys (and plenty others very similar) Self Contained Marine Air Conditioning Systems - Prices & Specifications is sure looks to me like approx 3/4 copper (they are using copper nickel for salt water resistance) with 1/4 ish A/c line in side it. The unit on the top of the page is 16,500 btu's and my quick estimation is that it has about a 12 foot long heat exchanger. I would think that it would be pretty difficult to plug up such a heat exchanger as long as I was running an inlet screen and kept the flow rate reasonably high. Any thoughts? I'm not sure how efficiant such a heat exchanger would be, but I can't see any reason not to just make it longer if it didn't exchange enough heat, I wouldn't think that the flow resistance would be dramatically higher than the tubing running to and from the bayou? Any thoughts?

So at the moment I'm thinking about building something similar to what they are selling(for more money than I can spend on such projects) out of an existing window unit.

Proposed steps.
1) remove condenser (or should I leave it so that if pumping fails I still have conventional A/C?)
2 ) if condenser is removed, cut fan off of shaft to reduce load on blower motor, hopefully countering some of the added draw of a pump.
3) build heat exchanger very similar to the marine units, it looks like copper is available in 30 foot coils, and I have 2 units, so I was thinking 15 feet each. More thoughts on this below.
4) Select pump install plumbing. I'm thinking that if I run the return pipe all the way down to bayou level my pump should only have to over come friction losses and counter the thermo siphon that will work against me since I'm heating on the top and cooling on the bottom. More thoughts below.
5) I'm thinking an expansion valve is the way to go here, any thoughts? There is an existing capilary tube, but I have no idea if it would be properly sized for new setup. Any ideas?
6) solder it together, add service ports charge. I'm pretty sure existing units are r-22, which I do have access to a gauge set, I also have a 2 stage vaccume pump(mine) so I just have to come up with a small quantity of r-22 unless I can figure out a good way to recover the existing refrigerant. Any easy ideas?

7) test. Plenty small enough for a kill-a-watt, and since I have 2 identical units, easy to gauge air vs water performance.






I'll have to measure, but I'm guessing 40 feet of plumbingeach direction to and from the bayou. Anybody have a calculator for pump sizing? I'd like to use the same pipe that A/C hacker uses in his field (cost, durability), but connection difficulties may change my mind (only 3-4 connections per A/C all of which are easily accessible so maybe mechanical would be ok?). The marine units want 500 gallons/ hour/ ton, so my 6000 btu's should want 250 ish gallons per hour (or 4 ish gallons per minute) through about 100 feet of tubing and a strainer basket. I'd like a pump that has the ability to make 15 foot head pressure so it could self prime, but I guess that isn't strictly necessary.
Any thoughts highly appreciated.





Although the 16,500 btu unit uses a shorter heat exchanger coil than I am considering AND I'm only 6,000 btu per unit, I'm not seeing virtually any efficacy information on the marine units, I realize it is hard to provide due to changing water temperatures, but I AM defiantly after some improvement in efficacy and the extra copper cost isn't all that much in the total cost. Any thoughts highly appreciated here. Anybody ever use / find info on such a heat exchanger?


Last edited by dremd; 04-13-13 at 12:24 PM..
dremd is offline   Reply With Quote
Old 04-13-13, 12:19 PM   #2
dremd
Need More Eco
 
dremd's Avatar
 
Join Date: Sep 2008
Location: Scott, La
Posts: 172
Thanks: 2
Thanked 6 Times in 6 Posts
Send a message via AIM to dremd
Default

First serious thought on the pump.
Little Giant PE-2.5F-PW Pond Pump 566612, Little Giant Pumps
Looks around 13 foot max lift (only needed to prime) and keeps my 250 gph up to 9 ft lift which seems excessive.

I'd like to do a bit more measuring, to get to 15 foot max head I'd be looking at 150+ watts running current, 80 actually seems a bit much, but I think would be acceptable.

I'm thinking of putting a 5 gallon bucket in the bank perforated with 1/4" (maybe smaller?) drill holes as super corse screen, and some sort of ridgid wire screen inside the 5 gallon bucket to keep most stuff out with the pump screen after that.
dremd is offline   Reply With Quote
Old 04-13-13, 05:18 PM   #3
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Dremd,

From what I could read in the specs, the units have a coarse SEER rating of 10.5 - 13 ish. This is about what a window AC unit has in terms of BTU cooling/power input.

I bet the efficiency could be WAY increased with little modification with a larger copper exchange coil instead of the keel cooler they use.

The concept of doing direct exchange has been around a long time. This simply means that instead of a long exchange tube, you substitute a shorter, but much more efficient tubing or plate.

A roll of copper tubing, as you suggest would work very well.

Then we need AC to look at it to determine how to better increase the EER. The unit has all the making of efficiency as it has a scroll compressor, co-axial heat exchanger - so it should not be hard.

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990

Last edited by stevehull; 04-13-13 at 05:20 PM..
stevehull is offline   Reply With Quote
Old 04-13-13, 10:06 PM   #4
dremd
Need More Eco
 
dremd's Avatar
 
Join Date: Sep 2008
Location: Scott, La
Posts: 172
Thanks: 2
Thanked 6 Times in 6 Posts
Send a message via AIM to dremd
Default

Stevehull, where did you find the SEER ratings on those marine units? I never could locate them.

Amazing what being sick can do for project planning, I just saw randens heat exchanger here http://ecorenovator.org/forum/geothe...-pressure.html and thought of a much cheaper heat exchanger than I previously proposed.
PEX on the outside, copper on the inside, use drilled pex plugs soldered to the evaporator line to keep the water side leaks away, and a simple T to feed/ remove bayou water from the heat exchanger. PEX is about 1/4 the price per foot, so I could run a much longer heat exchanger for the same $ if my selection is correct, I could make them for about $2/ ft, so 25-50 feet would not be out of the question. That said, with 1/4" refrigeration tube(my guess on stock size) a 25 ft exchanger would only have 1.6 square feet of exchange surface.
dremd is offline   Reply With Quote
Old 04-14-13, 01:49 AM   #5
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

dremd,
If it were me, I'd start out small to prove the effectiveness. Just spew water out of your pond pump pipe onto the existing evap somewhere it would only sling a little of water in the fan. Maybe up high near the top left corner? You could put in a vertical strip of something waterproof at the edge to block airflow. At a few gallons per minute, the drain hose for your window unit should be able to handle that volume of water. See if you gain any performance over air-only. My guess is that you will. Water conducts and carries heat MUCH better than air.

After preliminary testing, you can decide if you want to do better. The next step could be to add a txv where the capillary tube exists now. Then maybe add water cooling to the line between the condenser discharge and the txv. This way, you would get your existing air cooling plus water subcooling. Grab a small pack of the next tube size up from your existing line and a styrofoam 6-pack chest. Twist the tube up into some shape that will fit in the ice chest with room to run to the splice point, poke a few holes above water level to break out of the chest. Rig up an overflow drain to collect warm water, then figure out how to secure the chest before you cut or braze anything. With only 1/2 ton of heat flow, you would not need a very large exchanger.

Good luck, this stuff is addictive if you have the skill and patience!

jeff
jeff5may is offline   Reply With Quote
Old 04-14-13, 09:42 AM   #6
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Dremd,

A quick calculation of the SEER can be had by dividing the btu output by the power in watts input. Not perfect, but a close approximation.

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 04-14-13, 03:13 PM   #7
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Dremd,

Another thing to consider doing with the smaller units is using them in "reverse polish" mode. I have found that the heat exchangers in the smaller units can only be pushed so hard before they become the bottleneck in your quest for high efficiency.

The outdoor heat exchangers in these units are designed for massively more airflow and exchange area than the indoor coils. By installing the unit backwards in the window, reversing the connections at the compressor, and adding to the smaller (now outdoor) exchanger to gain heat transfer, you can run the unit at a lower speed to save motor energy while still pumping maximum btu's. This also has the benefit of being able to work on the unit indoors where it's a comfortable temperature. Most window openings are at a height where you can comfortably sit in a chair or barstool to do work and take measurements.

Don't laugh, this works, really! I am using this method to do testing of some suction line heat exchangers now. It really helps your patience factor when you're in a normal environment. No need to worry about rain, snow, wind, heatwave, frostbite, etc.

Last edited by jeff5may; 04-14-13 at 03:19 PM..
jeff5may is offline   Reply With Quote
Old 04-15-13, 01:30 AM   #8
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by dremd View Post
Hey guys, I've been very interested in water source/ ground source cooling (not much heating needed down here, but it would be nice) for quite a while and A/C hacker has had me highly interested for years.
dremd,

It sure would be useful if you could get some loops into the Bayou water. I certainly understand why you can't, but it sure would be useful.

So, as I understand it, you're 15 feet above and 20 feet back from the bayou, right?

So, your water table is 15 feet beneath your camp. Other than getting loops into the bayou, your answer is 15 feet below your feet.

Too deep to trench, but a rotary water drill just might work really fine.

You ought to do a little asking around about your soil conditions near your lodge. Ask well drillers, ask GSHP drillers (for use in A/C).

All of the drilling problems that I had personally, were due to rocks that were left after prehistoric recessions of ancient glaciers. In fact the other folks that I know in this area, who had problems drilling, had those problems because of fist-sized to football-sized rocks and cobbles. I just bet that it has been many, many, many millennia, since Louisiana has seen any glaciers.

I have heard of very easy drilling done by some of our Southern Brothers, who encountered nothing more serious than sand and clay... so before you pull the plug on the idea of drilling or trenching, tap into the knowledge of some of your local drillers.

They may tell you that it is truly unreasonable to DIY something like that, and that you need Very Big Power to punch holes in the ground. If that is the case, then don't proceed down that road.

But if you are not up against cobbles or bedrock... you could have a very good chance of success.

It's amazing how, once you start asking around, local lore on this issue starts to come out of the woodwork.

Some closed loops sunk down into the water table a pretty good way would sink a lot of heat, and you wouldn't need to worry about anything ever silting up or getting clogged by some kind of green swamp growth.

But then there's that bayou... how deep do they dredge it???

I don't know if you have gone over any of Brad_C's posts on EcoRenovator, but he is doing a DIY open loop A/C, in Perth, Australia. He isn't on a bayou, but he is utilizing flowing ground water, and he has had to deal with filtering out stuff that could clog his HXs (yes, he is using a huge brazed plate). Brad_C is Brad_C, and he seems to be pretty much unstoppable. But for you, a mortal, you are right, an open loop system is not the place for brazed plate HXs.

Acuario, over in Spain did some interesting work with homemade HXs... In fact I think he really started a DIY tube-in-tube trend.

Then it looks to me like randen, up near Toronto, Canada, took Acuario's idea of how to DIY a tube-in-tube and made it simpler and even better.

So, you can build your own tube-in-tube that wouldn't be prone to clogging.

Hope I've been able to get your gray matter bubbling just a little bit here...

And yeah, those marine units do look pretty nice, if you have the cash... but they still need water.

Good Luck!

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 04-15-13 at 01:32 AM..
AC_Hacker is offline   Reply With Quote
Old 04-15-13, 08:36 AM   #9
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

I woke up this morning thinking about your bayou camp cooling problem...

I realized that there are quite a few issues that I had assumed about your camp, that I really shouldn't have.
  • What is your inclination to DIY something? Some of the folks here on this forum absolutely revel in digging into the smallest detail and practically creating something out of nothing... and they either have the skills on tap, or are not inhibited in the least about acquiring the required new skills. But, in all honesty, you may not be one of these people. You might instead be interested in a turn-key solution that you can purchase, have it installed, and be done with it.
  • What is your budget? If you are a successful doctor or attorney or politician, and your goal is to maintain a bayou camp to entertain your clients and possibly family, you might have some serious loot to focus on the problem.
  • What does camp mean? When you say camp, I was imagining a humble, small, simple one or two room structure where you go on an occasional weekend... kind of a Louisiana version of a Russian Dacha. But it occurred to me that this might be a business venture for you, and that 'camp' really meant a spacious lodge where paying guests went for a weekend, and a full time maintenance man was on site to guard the property and keep up the equipment.
  • What amount of time do you you plan to use it? How much of the time do you, or your paying guests actually intend to use this camp? If it is a few times a year, for a few days at a time, that could justify one approach, and if it is for say, five months a year, or full-time for you and/or paying guests, then there would be entirely different solutions.

Please advise.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 04-15-13 at 08:39 AM..
AC_Hacker is offline   Reply With Quote
Old 04-19-13, 10:54 PM   #10
dremd
Need More Eco
 
dremd's Avatar
 
Join Date: Sep 2008
Location: Scott, La
Posts: 172
Thanks: 2
Thanked 6 Times in 6 Posts
Send a message via AIM to dremd
Default

Quote:
Originally Posted by stevehull View Post
Dremd,

A quick calculation of the SEER can be had by dividing the btu output by the power in watts input. Not perfect, but a close approximation.

Steve
Excellent, I honestly thought that the running watts was sort of a max continuous draw, not a norm draw (Im not very experienced in A/C ratings)

dremd is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:34 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design