EcoRenovator  

Go Back   EcoRenovator > Improvements > Geothermal & Heat Pumps
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 10-07-09, 02:19 PM   #21
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
I was gonna recommend a cheaper alternative, but I just looked online and they were about $100, so go for it.

Your unit may use different fittings than mine, just wait until your stuff arrives and measure it at that time.

You do know that you should use a tubing cutter that uses tiny knife-sharp wheels to do the jub, right? You don't want to use a saw and leave bits of copper to float about in your system.

Your tubes will also have lengths of foam insulation that you'll need to shorten. You can slide the insulation over the end of the tube and make your cut with scissors, then snug the end down to the tube with nylon tie-wraps.

Your tubing will have little plastic caps that keep dirt out of the tubes. The tube is not pressurized or 'filled' or anything. After you cut your tube and slip your flare nut (use the ones that are already on the tube) over the tube, then make the flare.

Then put the little caps back on the tube until you're ready to do the deed.

Regards,

-AC_Hacker
The install manual tells you to ream the end of the tube while it's
pointed downwards (page 17).
http://sanyohvac.com/assets/document..._72_Series.pdf

I would still be worried about getting metal particles inside it.
I was thinking maybe stuff some non-lint fabric up in there,
to block the tube up, and then blow it out with a blast of dry air
from the other end.?.

I have two pipe cutters that I use for cutting copper water tubing.
I think the smaller one might be good for this job. It's pretty sharp.
At work, I use a super fine jeweler's saw and a fixture to cut off
0.141 OD hardline coax cable. That will be my backup method,
if my small tube cutter fails to perform. I can make fixture blocks on my Chinese mill.

The manual says "the ideal (or target) vacuum condition is around 10 mmHg abs."
(What does that equal to? Is that 10 Torr? (10 Torr=10,000 Micron?)..

That MasterCool pump does 75 Microns. Will that do the job??
Mastercool Inc., Vacuum Pumps

Xringer is offline   Reply With Quote
Old 10-07-09, 05:30 PM   #22
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by Xringer View Post
The install manual tells you to ream the end of the tube while it's
pointed downwards (page 17).
Copper is pretty malliable stuff... After you cut off the excess tube from your line set, there may be a bit of a 'burr'. But before you start stuffing things inside the tube, use your flare tool and do a practice flare or two on the line you just cut off. I'd be very surprised if there was any burr after you make a flare.

Quote:
Originally Posted by Xringer View Post
I would still be worried about getting metal particles inside it.
I was thinking maybe stuff some non-lint fabric up in there,
to block the tube up, and then blow it out with a blast of dry air
from the other end.?.

I have two pipe cutters that I use for cutting copper water tubing.
I think the smaller one might be good for this job. It's pretty sharp.
At work, I use a super fine jeweler's saw and a fixture to cut off
0.141 OD hardline coax cable. That will be my backup method,
if my small tube cutter fails to perform. I can make fixture blocks on my Chinese mill.
Probably will not be an issue.

Quote:
Originally Posted by Xringer View Post
The manual says "the ideal (or target) vacuum condition is around 10 mmHg abs."
(What does that equal to? Is that 10 Torr? (10 Torr=10,000 Micron?)..

Quote:
Originally Posted by Xringer View Post
That MasterCool pump does 75 Microns. Will that do the job??
Mastercool Inc., Vacuum Pumps
Should work just great... If you have a micron gauge, you'll know for sure it's working great.

But remember to change the vacuum pump oil just before you do a pump-down. By design, vacuum pump oil absorbs atmospheric water.

Even though your vacuum pump has never been used, it's been sitting and absorbing atmospheric water. Change the oil.

My friend, Bruce-the-Pirate bought a two gallon jug of vacuum oil for some kind of low price. Big mistake. Every time he opens the jug, he's introducing more atmospheric water. Personally I would throw the jug away. But he wears an eye patch and will probably use it anyway.

Buy a small one-shot or two-shot bottle and don't open it until you're ready to use it.

I bought a small plastic two-shot bottle, used half of it, capped the bottle tightly back up and left it on the shelf for a couple of weeks. Now the sides are all caved in because the oil has been sucking the moisture out of the air that was trapped inside the bottle. Pretty amazing. You want that kind of oil to be working for you!

Regards,

-AC_Hacker

P.S.: And remember, I'm not an HVAC technician. In fact, I'm just barely a hacker.

%%%%%%%%%%%%%%%%%%%%%%%%%%%%
AC_Hacker is offline   Reply With Quote
Old 10-07-09, 06:04 PM   #23
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

I saw this one on Ebay.. JB DV-22N DV-24N Digital Vacuum Micron Gauge with Case - eBay (item 300353500817 end time Oct-09-09 18:03:08 PDT)

Looks like a nice unit.. 20 to 9000 Microns, What do you think?


And, I have a printout of that table right here, but I still didn't know if
I was reading it right.. Until I looked up "Hg" and found it's the
modern chemical symbol for mercury.. LOL!! I'm so forgetful these days!
Or, maybe I never knew that!

I might end up needing to cut off about 4 feet of line-set, and that
tech guy at Ductless HVAC Supply also advised me to practice on
the extra cable. He said after you do about 10 flares, you will likely
do a better job than some AC tech who is in a hurry..


Re: malleable stuff
That tech guy also said I could use a 45 degree flare tool. He said
when you tighten down the nuts real good, it will come down to 37 degs
without a hitch. Just loosen and re-tighten to normal pressure afterwards.
No probleMoe.. I expressed some doubts and he
assured me it works, because the tubing is so malleable..

What do you think?

Yeah, I know you are a hacker like me. But, I also know that a lot of the
Experts I've seen aren't always doing and expert job..
Xringer is offline   Reply With Quote
Old 10-07-09, 06:22 PM   #24
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by Xringer View Post
I saw this one on Ebay.. JB DV-22N DV-24N Digital Vacuum Micron Gauge with Case - eBay (item 300353500817 end time Oct-09-09 18:03:08 PDT)

Looks like a nice unit.. 20 to 9000 Microns, What do you think?
Looks real pretty.

Mine cost me about $137, bought it from a local supplier. If you can get that one for less, you are that much further ahead.

Quote:
Originally Posted by Xringer View Post
Re: malleable stuff
That tech guy also said I could use a 45 degree flare tool. He said
when you tighten down the nuts real good, it will come down to 37 degs
without a hitch. Just loosen and re-tighten to normal pressure afterwards.
No probleMoe.. I expressed some doubts and he
assured me it works, because the tubing is so malleable..

What do you think?
Well, I didn't know about the angles, that's good to know...

I do know that copper is very forgiving.

Best Regards,

-AC_Hacker

%%%%%%%%%%%%%%%%%%%%%%%%%%%%%%
AC_Hacker is offline   Reply With Quote
Old 10-08-09, 12:33 AM   #25
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Here's a link to the assembly lube I used.

http://refrig.com/Product/Sealants/N...ylog_blue.html

This is the stuff they referred to as 'snot'.

Regards,

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 10-08-09, 02:40 PM   #26
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
Here's a link to the assembly lube I used.

Refrigeration Technologies: Products: Nylog Blue

This is the stuff they referred to as 'snot'.

Regards,

-AC_Hacker
I'm just going to ask for it by it's brand name..
It looks like just the stuff I need. May have to get it on-line, since
these distributorships don't like selling stuff to DIYers.

Anyways, are your Sanyo flare nuts metric or SAE??
Since I'm thinking of ordering a kit of 3/8 size flare nut crowfeet..
Xringer is offline   Reply With Quote
Old 10-09-09, 02:59 PM   #27
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Wow! I've got to read more.. Just found out about the time required to dehydrate your system
takes longer if it's cold out..
Refrigeration Vacuum Pumps

Really shows the need for a good vac meter.

It's 60 here today, so it would take 36 hours! Wow.. Longer than I expected.


How does the HVAC tech do these Mini-Split Install jobs and turn
on the system in just a few hours???
Xringer is offline   Reply With Quote
Old 10-09-09, 03:26 PM   #28
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default

Quote:
Originally Posted by Xringer View Post
How does the HVAC tech do these Mini-Split Install jobs and turn
on the system in just a few hours???
That's why you are doing it yourself...

Regards,

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 10-09-09, 04:32 PM   #29
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
That's why you are doing it yourself...

Regards,

-AC_Hacker

I guess you kinda have to DIY.. Otherwise the labor cost would be more
than the hardware cost!

Reminds me of Solar PV installations.. LOL!
Xringer is offline   Reply With Quote
Old 10-11-09, 06:00 AM   #30
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Found a place locally that sells this 2-stage pump..

Robinair 15150 Vacuum Pump, 1.5 CFM, Two Stage, 110V

Robinair 15150, 15300, and 15500 1.5, 3, and 5 CFM VacuMaster Vacuum Pump - on Sale at the Test Equipment Depot

They have a pretty good price, even with the taxes..

Xringer is offline   Reply With Quote
Reply


Tags
air conditioner, diy, heat pump

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:29 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design