Default Turning a window unit into a mini split?

I have an office I am trying to build an approximately 10k BTU heat pump for. I've been wanting to do a simple backwards air conditioner, but I'm running into more problems than I would like in my test. I'll need to break open the refrigerant circuit to make it do what I really want...

So, I've been thinking homemade mini split. It would be nice if I could mount the compressor outside of my office, I notice the back side of the air conditioner makes a lot more noise than the front!

I'm thinking I could take a 10K BTU window unit, and plumb both evaporator and condenser in parallel. Then run a line set into my office where I would build an indoor unit with an evaporator and a fan. Hopefully it would be more efficient due to having a larger outside coil. The original window unit fan would blow on both coils.

Is this something that might work? How far would I be able to extend the lines between inside/outside units, and what size would I use? The "outdoor" unit is actually going inside a shop area, so it doesn't need to be weather proof.

F357 is offline   Reply With Quote
Old 11-04-14, 09:52 AM   #2
theoldwizard1
Apprentice EcoRenovator
 
Join Date: Oct 2014
Location: SE MI
Posts: 105
Thanks: 3
Thanked 12 Times in 9 Posts
Default

Quote:
Originally Posted by F357 View Post
I have an office I am trying to build an approximately 10k BTU heat pump for. I've been wanting to do a simple backwards air conditioner, ...
Do you want a true heat pump that both heats and cool ? There are a lot of additional parts required. Study this diagram.



Even if you ONLY want heat from your homemade mini-split, 2 fans are likely going to be required.
theoldwizard1 is offline   Reply With Quote
Old 11-04-14, 05:17 PM   #3
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

IT CAN BE DONE. I am considering doing the same thing with a prefab window unit. Run the two heat exchangers in SERIES (not parallel) by swapping the cap tube out for a straight pipe. Pipe the condenser end of the series connected assembly into the reversing valve, and install a txv and check valve (in parallel) on the evaporator end. The arrow on the check valve should point away from the evaporator. This way, the condenser will not burp liquid or fog into the compressor in heating mode. The inlet to the TXV and the outlet of the check valve should merge, then that pipe would be the liquid line running indoors. The gas line of the set connects to the other open pipe on the reversing valve outside.

ECOMODDED has started a thread recently, asking about the same basic idea, on a smaller scale. He is planning on doing this with a dehumidifier as an indoor unit. For outdoors, he plans on using an automobile condenser.

You are correct in assuming that running both heat exchangers together will be more efficient. The more surface area and airflow you have, the more heat you can harvest from outdoors. How much more efficient? No one knows yet.

Indoors, a much larger heat exchanger takes longer to heat up (or cool down) as the cost of higher efficiency. Some like it, but most don't. The "warm" air the unit is spewing out the first few minutes at super-high efficiency doesn't warm the soul like a buck stove. I understand the first two minutes (while the liquid is building up in the hx) and the last two minutes (while the fan cools the hx after the pot stops spinning) are when the unit saves me the most money. To mom and the kids, that air just isn't warm enough.

Last edited by jeff5may; 10-01-17 at 09:38 AM..
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
TechShop (09-30-17)
Old 11-06-14, 12:15 AM   #4
F357
Helper EcoRenovator
 
Join Date: Sep 2014
Location: Oregon
Posts: 30
Thanks: 0
Thanked 1 Time in 1 Post
Default

Quote:
Originally Posted by theoldwizard1 View Post
Do you want a true heat pump that both heats and cool ?
Yeah, I will definitely try to put a reversing valve in the mix.

Quote:
Originally Posted by jeff5may View Post
Indoors, a much larger heat exchanger takes longer to heat up (or cool down) as the cost of higher efficiency. Some like it, but most don't.
My goal here will be to keep my office at roughly the same temp all the time, so I don't have to swing it up and down all the time. Can't do that with my electric heater now, takes too much to run. Need some more insulation also.

I'm thinking the easiest way to build an inside unit would be to just gut another window unit. Take the compressor out of this one and use both the evaporator and condenser again.

Do you think I could get away with 30-40 feet of tubing between the units, if I go a size larger than what they come with? I'm thinking I could put the "outdoor" unit in an attic area, which stays a few degrees warmer in the winter.

I'm glad I'm not the only one who lays awake in bed at night thinking about air conditioners. In November.

Last edited by F357; 11-06-14 at 12:17 AM..
F357 is offline   Reply With Quote
Old 11-06-14, 10:59 AM   #5
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Sounds like it would work to me. The easiest way would be to use a small unit indoors and a larger unit outdoors. Stick a txv and a check valve in each unit and plumb them to each other. If the indoor unit is too loud, a speed control could be rigged up to quiet it down.
jeff5may is offline   Reply With Quote
Old 12-09-14, 10:28 AM   #6
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Any updates on this project?
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 12-17-14, 09:15 AM   #7
8307c4
Guest
 
Posts: n/a
Default

Unless you're HVAC certified and have the equipment I personally wouldn't be fooling with air conditioning units that involve working with connecting high pressure tubes, not like that... The pressures going inside these units frequently exceed 100 psi and the stuff really is dangerous.

That having been said...

I believe you can purchase a unit such as those used in a motel room already made, for under a thousand dollars. They're called PTAC's and doing a search on Google reveals several between $500 and $900, might even get a little break in price if you can find reconditioned / refurbished PTAC units.

They're quite efficient, with EER ratings of around 11+
Granted that's not much to compete with newer heat pumps but for single rooms and as a supplement to older HVAC systems it could be quite the money saver over the years.

Last edited by 8307c4; 12-17-14 at 09:26 AM..
  Reply With Quote
Old 12-17-14, 10:49 AM   #8
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by 8307c4 View Post
Unless you're HVAC certified and have the equipment I personally wouldn't be fooling with air conditioning units that involve working with connecting high pressure tubes, not like that... The pressures going inside these units frequently exceed 100 psi and the stuff really is dangerous...
8307c4,

Hate to burst your tepid bubble, but this forum is rich with examples of hearty hackers, from all over the world, who have gleefully and successfully violated every part of your warning.

You might want to check out THIS_LINK.

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 12-17-14 at 12:03 PM..
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
pinballlooking (12-17-14)
Old 12-17-14, 11:12 PM   #9
8307c4
Guest
 
Posts: n/a
Default

Quote:
Originally Posted by AC_Hacker View Post
8307c4,

Hate to burst your tepid bubble, but this forum is rich with examples of hearty hackers, from all over the world, who have gleefully and successfully violated every part of your warning.

You might want to check out THIS_LINK.

-AC_Hacker
No, not at all, if you'd rather take that risk and fool around with a project that might not even work over what a few hundred dollars would have already purchased please, be my guest. My time is worth money and so is my safety but I wouldn't want you to say I was holding you back now, just don't come around expecting much sympathy later.

Last edited by 8307c4; 12-17-14 at 11:15 PM..
  Reply With Quote
Old 12-20-14, 02:39 AM   #10
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

If I wanted a premade system, I could do one of two things to save myself gobs of cash:

1. Find a used system on the internet from a private seller or enterprising HVAC contractor, do most of the labor to install, and have a moonlighting contractor commission the system.

2. Call parts houses pricing new units, find a bargain, and have them shipped to my door. Follow option 1 to install.

I understand that an HVAC tech spent lots of money and time to learn the trade, but I'm not willing to pay double for my system components, plus 500 dollars a day for labor. Sorry, find someone rich and lazy.

8307,

While I understand your reasoning, you are obviously in the wrong forum. Where you want to be is the refrigeration engineer or the hvac talk forum to bash people for doing what we speak of here. There, you will find like-minded professionals who will support your opinions.

If I ever get in over my head on a project that isn't an experiment, all I have to do is pick up a phone book. I can immediately find one of you to come save me for a price. As to the nature of these calls I ever make, they usually involve things like sledgehammers and shovels and crawling around in the tight wet darkness.


Last edited by jeff5may; 12-20-14 at 03:50 AM..
jeff5may is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off