Old 11-16-15, 06:47 AM   #11
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

As always, I am speaking from an experimental point of view. If the rig is meant to be permanent, by all means match everything up perfectly. Don't ask me what is perfect, as I am not a doctor of mechanical engineering or a licensed HVAC system configurator. But I can cobble some recycled junk together and make it work like something one would pay 4 figures for.

jeff5may is offline   Reply With Quote
Old 11-16-15, 07:32 AM   #12
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Jeff, would a change in the cap tube make this setup (air to air changed to water to air) markedly more efficient?

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 11-16-15, 09:46 AM   #13
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by stevehull View Post
Jeff, would a change in the cap tube make this setup (air to air changed to water to air) markedly more efficient?

Steve
That there is the 64 thousand dollar question. The answer is:

Yes, if you know what you are doing.

Most capillary tube metered systems are matched to the evaporator under certain (ASHRAE) design conditions. Air-source window aircon units are not meant to be operated below, say 60 degF ambient, and the evaporator will freeze up solid if forced to run. Contrary to common understanding, a colder evaporator is not always a better evaporator.More mass flow is better, as long as the compressor doesn't see any liquid.

For a water-source heating arrangement, a change in the cap tube will properly feed the evaporator with the proper mass of liquid to improve efficiency. Since water absorbs much more heat than air to force the same temperature change, a shorter cap tube will move more mass and heat. However, lots of trials must be run at various conditions to determine the length that is appropriate for the new arrangement. Unless you are dead broke or have an insatiable love for tweaking, swapping in a TXV is a cheap way to improve efficiency that takes a whole lot less time.

jeff5may is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:37 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design