Default HPWH improvement

OK dudes and dudettes,
Since people have been having success with the heat pump water heaters from old window shakers, I have designed a mod that will make it more usable.

The issue results from the fact that trying to heat up a 60-80 gal tank with a 1-2kw heater takes a long time. The element (condenser) in the bottom has to heat up and mix the whole body of water before the top gets warm enough to use. We have this problem in solar all the time with indirect tanks.

The solution is to set up a thermosyphon system with a sidearm HX, as shown in the drawing. The condenser will heat up the small volume of water which will move directly to the top of the tank and is replaced by cold water at the bottom. This will create usable hot water in the shortest time, and eliminate the need to make a special fitting for a tank (although a fitting will be needed for the HX) and the issue of getting the coil into the tank is eliminated.

Just thought I would share this.


Attached Thumbnails
Click image for larger version

Name:	hpwaterheater.jpg
Views:	703
Size:	18.1 KB
ID:	4487  
Attached Files
File Type: pdf HPWH side armHX.pdf (5.4 KB, 508 views)

Last edited by Daox; 07-11-14 at 09:54 AM..
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
AC_Hacker (08-09-14)
Old 07-11-14, 07:44 PM   #2
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Take it a step further by adding a pump and then you can put the unit where the added cooling would be more useful. That's the design I adopted.

Another solution is to add a second coil near the top of the tank and connect it as a desuperheater. The commercially available units likely use a design like that.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 07-13-14, 09:20 AM   #3
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

But what if the hot and cold water pipes are both at the top of your water heater tank? Most newer units are built this way.
jeff5may is offline   Reply With Quote
Old 07-13-14, 10:03 AM   #4
Fordguy64
Journeyman EcoRenovator
 
Join Date: Oct 2011
Location: Cincinnati ohio
Posts: 338
Thanks: 40
Thanked 35 Times in 31 Posts
Default

Just use the drain.. A lot of the outdoor wood furnace guys use this idea for heating water
Fordguy64 is offline   Reply With Quote
Old 07-13-14, 10:29 AM   #5
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

The added thermal resistance would likely reduce efficiency unless you added a pump to keep it very low.

How often is it that additional cooling right at the tank would be a benefit? I most often see hot water tanks in the attic or garage in my area, so it would be trying to uselessly cool unconditioned space.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 07-13-14, 10:55 AM   #6
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

No need to use any pump on this system. The the water in the HX won't start to rise until it reaches the temp higher than the water above it and it will need to be quite warm to get to the top. This is where you want the heat to be but a convection current will only happen if the HX is at the bottom. A pump will just force what may be cooler water up to dilute the already warm water at the top of the tank so it is less useful. Having the HX at the bottom is natural protection and gets the best efficiency from the system and I have done it 100s of times with solar.

I always disconnect the top intake and use the drain. One electric tank manufacturer did some tests and showed a 10% improvement in efficiency by doing this. Also, the dip tubes do wear out.
Mikesolar is offline   Reply With Quote
Old 08-09-14, 07:50 AM   #7
Zooomer
Lurking Renovator
 
Join Date: Aug 2014
Location: Grand Rapids MI
Posts: 12
Thanks: 0
Thanked 2 Times in 1 Post
Default

Quote:
Originally Posted by Mikesolar View Post

I always disconnect the top intake and use the drain. One electric tank manufacturer did some tests and showed a 10% improvement in efficiency by doing this. Also, the dip tubes do wear out.
Can you elaborate on that statement? How do you get 10% more efficiency out of a resistive heater?
Zooomer is offline   Reply With Quote
Old 08-09-14, 10:56 AM   #8
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Mikesolar View Post
OK dudes and dudettes,
Since people have been having success with the heat pump water heaters from old window shakers, I have designed a mod that will make it more usable.
[* I do seem to recall someone who posted an idea similar to yours, but as I recall, he wanted to spiral-wrap his tube-in-tube HX around the outside of the water heater. I don't recall him ever reporting back that he'd had success (or not). *]

Mikesolar,

I think that this is an excellent idea. I can see every reason why it would work well.

You are correct in that it solves the condenser-inside-the-tank issue. However the condenser inside the tank does have the advantage that there is almost zero lost energy, as all the heat goes into the water. Therefore your external circuit would need to be excellently insulated to be competitive.

The next step would be experimental proof...


-AC

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:13 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design