EcoRenovator  

Go Back   EcoRenovator > Improvements > Geothermal & Heat Pumps
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 06-29-12, 11:46 PM   #11
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

My problem now is figuring out Where to install a tank..
This evening, I went down and looked at the back of my boiler.
There a 3/4" nipple sticking out (on the rear left side) that has a T&P valve on it.

I think it would be a quick install, if I skipped buying a tank (HW heater).
Just build a little shelf for the A7, beside the boiler and run the HX loop into the 3/4" hole.
I can install the T&P elsewhere.

If the HX loop was fed into the rear left side (3/4 from bottom), it would intermingle with existing domestic HW HX coil..

The water jacket hold 72 gallons of blackish water..

The main problem with the idea is the thin insulation, and leakage up the chimney..

__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 06-29-12, 11:49 PM   #12
S-F
You Ain't Me
 
S-F's Avatar
 
Join Date: Nov 2009
Location: Northampton MA
Posts: 662
Thanks: 6
Thanked 71 Times in 58 Posts
Default

I like this idea because you can disconnect the heat pump in the winter.
__________________
My project:


To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.


Chipping away on a daily basis.

Quote:
You know you're an ecorenovator if anything worth insulating is worth superinsulating.
Quote:
S-F: "What happens when you slam the door on a really tight house? Do the basement windows blow out?"

Green Building Guru: "You can't slam the door on a really tight house. You have to work to pull it shut."
S-F is offline   Reply With Quote
Old 06-30-12, 07:31 AM   #13
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

It's easy to add a by-pass to a tank. I had that on my old Solar HW tank.
In case of leakage, you always want to install a pair of cut-offs in/out of the tank.
So, just add one more cut-off before the pair for a total by-pass ('H' manifold?).

New model electric HW heaters have very good insulation. It's two inches of good foam.
The GE user guide said, NOT to add an insulation wrap kit to the tank. It won't help.
And, it might effect the warranty.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 06-30-12, 07:46 AM   #14
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default



Notice the A7 has a 120vac outlet on it's back-panel. The manual warns not to exceed 1 amp.
Seems like a good place to plug in a run-time timer...

But, another idea popped into my head..

What if you plugged in a GTI? With a 200w PV panel connected?
http://i46.photobucket.com/albums/f1...Solar/l005.jpg

Might give the A7 some help during the sunny parts of the day...

If AC power out of the GTI remained less than 368 watts, it wouldn't feed power back onto the grid (not legal in some places)..
Since the A7 would consume all the PV power provided, and shut down the GTI, when the thermostat opened the circuit.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 06-30-12, 07:54 AM   #15
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Found a 40gal tank in stock at HD. $258
GE40M06AAG | GEŽ Electric Water Heater | GE Appliances
For another 80 bucks you can get 10 more gallons..
Since we are a low demand family, I'm voting for the 40 gal.. Comments?

Dang, this thing weights over 100 pounds! My back is already killing me..


Edit:
I noticed this unit has two 4500 watt elements (at 240vac), I wonder if you put these two elements in series,
4500/240=18.75 amps. 240/18.75=12.8 ohms x2=25.6 ohms. 240/25.6 =9.375A x 240=2.25 KW... (or 1.124 KW at 120vac)..?.


I'm thinking that burning 1KW might be useful to keep the tank luke warm,
during those extra cold January days when the A7 is dropping the basement to 40F !!

~~~Edit~~~
I was just thinking about what Vlad said "This elements have 2 thermostats. They never work together"..
I misunderstood. Now I look closer at the diagram, I can see that one element will work at a time..
Which means that: Unmodified, the total load is always going to be 12.8 ohms. 120/12.8 = 9.4 amps. 120v x 9.4a = 1128watts..
In series, that power would drop to half. 564w..
But, if I wired them to run simultaneously, 2.256 kw! (@120vac).

I'm thinking that 1128w (3849 BTUh) would be less work.
It's around half the heating of the A7 and might not be too hard to pay for.
If it was on 10 hours a day, that's $1.78, a little bit less than oil..
Attached Thumbnails
Click image for larger version

Name:	themo.jpg
Views:	5209
Size:	44.4 KB
ID:	2412  
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..

Last edited by Xringer; 07-08-12 at 06:03 PM.. Reason: Math error correction
Xringer is offline   Reply With Quote
Old 06-30-12, 08:23 PM   #16
Geo NR Gee
Journeyman EcoRenovator
 
Join Date: Jan 2011
Location: Seattle
Posts: 326
Thanks: 109
Thanked 23 Times in 18 Posts
Default

Please post when you get it hooked up and how long it comes on if you can check that? Could you plug it into one of the new electicity usage meters that you posted about? I think that new meter shows how many minutes and hours the device operates.
Geo NR Gee is offline   Reply With Quote
Old 06-30-12, 10:40 PM   #17
Vlad
Apprentice EcoRenovator
 
Join Date: Aug 2010
Location: Windsor ON Canada
Posts: 229
Thanks: 4
Thanked 30 Times in 22 Posts
Default

Quote:
Originally Posted by Xringer View Post
Found a 40gal tank in stock at HD. $258
GE40M06AAG | GEŽ Electric Water Heater | GE Appliances
For another 80 bucks you can get 10 more gallons..
Since we are a low demand family, I'm voting for the 40 gal.. Comments?

Dang, this thing weights over 100 pounds! My back is already killing me..


Edit:
I noticed this unit has two 4500 watt elements (at 240vac), I wonder if you put these two elements in series,
4500/240=18.75 amps. 240/18.75=12.8 ohms x2=25.6 ohms. 240/25.6 =9.375A x 240=2.25 KW... (or 1.124 KW at 120vac)..?.

Using those elements at 1.124 kw puts 3835 BTUh into the tank..
Not much, but that's not bad, considering the A7 sends around 6500ish BTUh to the tank during normal operation.

I'm thinking that burning 1KW might be useful to keep the tank luke warm,
during those extra cold January days when the A7 is dropping the basement to 40F !!
This elements have 2 thermostats. They never work together. Check manual. I installed electric HWT with the same 2 elements 4.5 KW each. Here is how they wired :

How to wire water heater thermostat
Vlad is offline   Reply With Quote
Old 06-30-12, 10:59 PM   #18
Vlad
Apprentice EcoRenovator
 
Join Date: Aug 2010
Location: Windsor ON Canada
Posts: 229
Thanks: 4
Thanked 30 Times in 22 Posts
Default

So this hot water heater requires separate HWT. Also it makes sens only to use it in summer time, or you will have walk-in cooler-basement. It is not bad if plan to store beer or wine or meat. There is no magic if you get BTUs you have to make them or steal them. Using this unit in heating season will eventually steal your heat from your heated space. It is just matter of time.

Because it will work properly only in warm season I would get condensing unit from split AC (and just revers it) or HP and put it outside. Also outside thermostat can control start HP or just use regular elements. If outside goes bellow efficiency point (too cold) your electric elements kick in or you start using hot water from whatever heater you might have (it can be oil boiler or on demand gas heater). As soon as you above efficiency point (worm weather) your thermostat switches back to HP.

I gave my example with ground loop but you can use air. You don't have to dig tranches for this. Just make your system smart enough to choose the source of heat.

Capacity or this unit is very low, you can use it only as supplementary heater if you have family of 2 plus 2 kids.

AC/HP split could be 2-3 ton capacity and this is enough for DHW.

In my opinion this unit is a waste of money and potential trouble maker.
Vlad is offline   Reply With Quote
Old 07-01-12, 12:01 AM   #19
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by Vlad View Post
This elements have 2 thermostats. They never work together. Check manual. I installed electric HWT with the same 2 elements 4.5 KW each. Here is how they wired :

How to wire water heater thermostat
I looked at the manual again, but I can't see any reason why both heating elements can't be re-wired in series, and be controlled by just one thermostat.
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 07-01-12, 12:27 AM   #20
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by Vlad View Post
So this hot water heater requires separate HWT. Also it makes sens only to use it in summer time, or you will have walk-in cooler-basement. It is not bad if plan to store beer or wine or meat. There is no magic if you get BTUs you have to make them or steal them. Using this unit in heating season will eventually steal your heat from your heated space. It is just matter of time.

Because it will work properly only in warm season I would get condensing unit from split AC (and just revers it) or HP and put it outside. Also outside thermostat can control start HP or just use regular elements. If outside goes bellow efficiency point (too cold) your electric elements kick in or you start using hot water from whatever heater you might have (it can be oil boiler or on demand gas heater). As soon as you above efficiency point (worm weather) your thermostat switches back to HP.

I gave my example with ground loop but you can use air. You don't have to dig tranches for this. Just make your system smart enough to choose the source of heat.

Capacity or this unit is very low, you can use it only as supplementary heater if you have family of 2 plus 2 kids.

AC/HP split could be 2-3 ton capacity and this is enough for DHW.

In my opinion this unit is a waste of money and potential trouble maker.

Our demand for hot water is very low (A retired couple).
Right now, we run the oil burner for 1/2 hour once a day. (1/2 gallon of oil or about $2).

People are actually using this type of (slow recovery) ASHP system to heat hot water.
And, maybe it won't be as effective during the colder months, but it does work.

If December comes and I find it's getting too cold in the basement,
it will be very simple to switch back to oil burner for 30 minutes a day.

__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:42 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design