Ok so I pulled the compressor today and zipped it open.

*** Warning sensitive content! Not for the faint of heart! Will be viewing a completely naked compressor! If you can not control your lust please hit your back button now! Continue at your own risk! ***

This is with the top off, the rotor turns freely, no sign of oil.

This is with the bottom off, when I turned her upside down about 2 tsp of oil was in the case.

And the is the inside with the cover off. NO OIL, not even a thin film.


I would have guessed there would be a lot more oil needed to make the compressor run. I was confused though because I saw NO reason why the rotor would not turn. Unless I shorted out a winding due to over heating.

So basically I have only a hint that I should find another compressor and add more oil.

Any ideas guys?

Attached Thumbnails
Click image for larger version

Name:	KIMG0399.jpg
Views:	817
Size:	332.0 KB
ID:	6286   Click image for larger version

Name:	KIMG0400.jpg
Views:	827
Size:	310.7 KB
ID:	6287   Click image for larger version

Name:	KIMG0401.jpg
Views:	805
Size:	315.0 KB
ID:	6288  
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Old 11-23-15, 02:08 PM   #102
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

How would you feel if you only had a bad start capacitor? It could be a possibility. Since the motor was tripping out under high current, the other possible causes are locked rotor and bad windings. These rotary pots are pretty tolerant of ingesting liquid in small amounts.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
stevehull (11-23-15)
Old 11-23-15, 03:09 PM   #103
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Another possibility is that the current source is not high enough to supply the compressor windings under load. High power draw drops voltage, amps go up and result is burned out coil.

Capacitor is a very easy check as well as continuity of coils with proper resistance .


Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 11-23-15, 03:46 PM   #104
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Jeff, Steven, I SURE HOPE NOT!

It was loading with 40 amps on my meter and would turn on, then off, then on then off, then blow a fuse.

I was able to grab a 7,500 BTU compressor today. 35 LRA. I think I like this size better anyway.

Gonna get it on tonight.

How do I check the cap?
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Old 11-23-15, 05:01 PM   #105
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

The best way to check a capacitor is to use "a capacitor checker". Ha! These have an output in Farads (mF or uF) and you can compare the meter with the plate descriptor on the cap. Not an expensive meter.

For a quick check, I use an ohmmeter and then reverse the lead polarity. One way it charges, the other way it doesn't. A shorted cap is truly dead with either polarity.

One mean way to check it is to put on two metal leads, one to each terminal - charge it up and toss it to a "friend". Depending on the scream, you know the capacity . . . .

But the best way is to replace.

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990

Last edited by stevehull; 11-23-15 at 06:03 PM..
stevehull is offline   Reply With Quote
Old 11-23-15, 05:32 PM   #106
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Didn't know I had one but I do!
It is rated for 60uf, it reads 1.7nf.......... Yep its dead. So the compressor was probably ok, BUT I'm glad it happened because it would have died from lack of oil anyway.
Dang, always always check first.
Another good thing that came out of this was I now FULLY understand what is going on in those little compressors now.
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Old 11-23-15, 05:56 PM   #107
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

My go-to dmm has a cap checker on it. It's a "lowly" fluke 12. It doesn't read current, though. I have learnt my lesson in that regard: if I really need to measure amps on something, a non-contact clamp won't blow a fuse in my meter. I have had more meters than I would like to count, but this one refuses to get lost or stolen, and has survived everything I have done to it. I really appreciate a good tool (sniff)...

That compressor really could have had more oil in the sump. Do you think you can weld it back together?
jeff5may is offline   Reply With Quote
Old 11-23-15, 06:12 PM   #108
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Memphis,

Remember you can "create" a 60uF capacitor out of two 30 uF or three 20 uF capacitors. When I need a specific one, I typically can't find that exact value, but I can almost always put a few capacitors in parallel and create the necessary value. A bit higher is also OK, but never less capacity.

Any voltage rating ABOVE the rating on the original capacitor will work.

Once the motor works, I then order the exact replacement from eBay.

Then, only minutes later, (after the order is placed), the specific value single capacitor is found in the junk box . . . . and in the exact correct physical configuration.

Why is that - or does it only happen to me?

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 11-23-15, 06:49 PM   #109
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Jeff, so you are agreeing it looks as though more oil is needed!
If I could get ask the metal shavings out of the windings I would sure give welding it back up a try. Lol

Steven, thanks! I have plenty of capacitors laying around, I should have the right one. This small 7,500 btu only needs 30uf.

I went ahead and made my oil return line to all 1/4", it was half 1/4" and half 1/8". I will also be running larger wire to the entire machine.

Vacuuming the system now.
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Old 11-24-15, 05:25 PM   #110
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

I got a lot to update on so bare with me. I put on the 7,500 (39.5 LRA) compressor and as expected it worked, just didn't do much heating. It stayed on all night to keep up. Use 6.5 kwh of power and only kept it at 58F.

I have been thinking and thinking, here is what I came up with. I remembered how someone mentioned in my heat pump water heater build that I needed the suction line to get cold in order to cool the compressor. This was also when I noticed the water getting hot much faster.
My conclusion is that my evap (DX loop) IS TOO BIG. No matter how cold (20F), or how big a compressor (11,000 BTU) the return line stays no less than 65F. I believe this to be other reason for the last compressor failure.
So I started looking for a big compressor, and as luck would have it I did a call for a HVAC guy today and was given this beauty. Friedrich PDE15K5SF-A Friedrich PDE15K5SF 15 000 BTU Packaged Terminal Air Conditioner with 5 0 KW Electric Heat
http://www.sylvane.com/media/documen...ers-manual.pdf



I hope this will get enough flow through the DX loop to chill the suction line. If not I have a 2 ton compressor I can put on it.

Problem being I don't have 220V in the greenhouse, but that can be solved because I will need 220V in there when I doing the house geothermal system anyway.
So some thing to consider..... This thing is R410A, so I will either have to drain the oil and use mineral oil for R290 or I can drain my oil separator and use R410A. I think I will gain capacity (BTUS) by switching to R290. Thoughts? Or am I totally wrong?
Also should I use the existing evap or condenser? The condenser looks bigger but doesn't have the cool squirrel cage, speed adjustable fan. Plus it has a air filter.
Next should I try to hack the existing controls and just use the one thermostat for the fish tank? Or should I just slap on the controls like I have them now?

Tons to consider, tons to research. But this time this machine is going to work. (I HOPE).
Thanks guys for your help and time!

Attached Thumbnails
Click image for larger version

Name:	KIMG0410.jpg
Views:	801
Size:	303.5 KB
ID:	6299   Click image for larger version

Name:	KIMG0411.jpg
Views:	797
Size:	301.8 KB
ID:	6300  
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 10:15 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design