Drainback system design
Here’s a website I found pretty useful when designing and building my solar hot water system (Solar Water Heater Design). Dr. Ben is a strong proponent for drainback systems due to their simplicity compared to pressurized glycol loops. The site has a focus on larger commercial systems, but the drainback system design is very scalable and there are a lot of useful tid-bits that apply to all systems.
A few of the items I picked up were methods of piping larger systems (importance of reverse-return, and a single high point), piping slope does not have to be quite as steep as commonly thought for drainback, and the limits on the length of a bank of collectors. |
11-06-13, 12:35 PM | #2 |
Helper EcoRenovator
Join Date: Mar 2012
Location: Warwick, Rhode Island
Posts: 92
Thanks: 22
Thanked 29 Times in 18 Posts
|
Esharp,
I've been all over his website as well as logged in to some of his live webinars. He is the person who inspired me to do a drainback system at my own house. One super smart guy there for sure! Glad you posted his location for all to enjoy. Take care, |
11-06-13, 04:22 PM | #3 |
Helper EcoRenovator
Join Date: Jan 2011
Location: South-East MI
Posts: 58
Thanks: 1
Thanked 6 Times in 4 Posts
|
Thanks for sharing. I never realized that the return side of a drain back system is the highest point. Learn something new everyday.
__________________
Jack of all trades, master of none. To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. |
11-07-13, 06:01 AM | #4 |
Helper EcoRenovator
Join Date: Mar 2012
Location: Warwick, Rhode Island
Posts: 92
Thanks: 22
Thanked 29 Times in 18 Posts
|
SimpleManLance,
Not sure if we should call it the 'Return side of the collectors actually, even though the water exiting the collector at it's highest point IS in deed the water returning to the storage tank??' The collectors on the roof are tilted a bit so when water is pumped up thru them the water is pushed from the lowest point of the collector / thru the collectors / and exiting the highest point of the collector piping. When the pump shuts down the water drains back to the storage tank. I installed the vacum release valve at the highest point of the piping which I am calling the 'return side' just for a reference point. I forgot to metion that I had to install insulation over the top of the vacum release valve also because in the winter cold months that valve will be sucking in ice cold air each time a vacum is created in the piping. Don't want ice cold air entering my piping so now it's covered with fiberglass wrap. I left an air space / air pocket under the insulation so the valve could still breathe/function ok.
__________________
Pat from Warwick, RI Please Note: Comments and/or suggestions I make here at the forums on 'your' projects as well as my own have all been carefully and scientifically calculated by 'the seat of my pants' To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. |
12-17-13, 10:23 AM | #5 |
Administrator
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
|
ESharp, do you have a thread here that shows/explains your solar hot water setup?
__________________
Current project - To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. & To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. |
12-18-13, 08:19 AM | #6 |
Helper EcoRenovator
Join Date: Mar 2012
Location: Warwick, Rhode Island
Posts: 92
Thanks: 22
Thanked 29 Times in 18 Posts
|
DAOX
not sure if I sent it to you or not previously but I have a pdf file showing my solar hot water system build I can give you/send you via email if anyone would like to see it.
__________________
Pat from Warwick, RI Please Note: Comments and/or suggestions I make here at the forums on 'your' projects as well as my own have all been carefully and scientifically calculated by 'the seat of my pants' To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. Last edited by solarhotairpanels; 12-18-13 at 08:23 AM.. Reason: update |
12-18-13, 08:01 PM | #7 |
Supreme EcoRenovator
|
|
The Following 2 Users Say Thank You to jeff5may For This Useful Post: |
12-19-13, 08:43 AM | #8 |
Administrator
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
|
Yes, you sent me your pdf solarhotairpanels. Thanks.
Thanks for finding that jeff5may.
__________________
Current project - To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. & To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts. |
12-19-13, 05:48 PM | #9 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Officially, the return of any heat producing system is the pipe going into the heat producer, in this case, the panels. Same with boilers, etc, etc.
|
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (06-09-14) |
12-19-13, 06:40 PM | #10 |
Steve Hull
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
|
It is CRITICAL that the return pipe be thick walled copper (rather than PVC).
Imagine if power shuts off on a sunny day. The collectors heat up to way past 300-400F with no water circulating. This can happen within 10-15 minutes in the middle of the day (brief power outage). Then power comes on (during the day). Water comes into panels and it flashes into super heated steam. This superheated steam simply turns PVC to a melted mess with water being pumped out. With copper, the superheated steam must heat up the copper and the heat is dissipated. PVC pipe does not do this. Don't ask me how I know of this . . . . Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990 |
The Following User Says Thank You to stevehull For This Useful Post: | buffalobillpatrick (06-09-14) |
|
|