Old 09-04-15, 07:09 AM   #1
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default 11,000 BTU DX GEO Heating

Howdy again, as some of you know I have a few projects that are still in the design stage, mainly due to money issues and an unsure time frame of a off grid dream.
This build is not limited by either one. And will help give me real data for the 4 ton DX system if I do ever decide to go through with it.

The Plan:
My greenhouse is 24 feet by 16 feet, and is built onto the front of my house so only 42 feet of liner wall space, 7-8 feet high, is triple walled 8mm poly panels. Same for the roof. I heated it with wood last year but I hate having 2 fires going plus I would like to heat my fish tank water in the aquaponics system.
The Idea:
The 17 feet deep 2-3 acre pond is 75 feet from the greenhouse. I want to run a loop of 300 feet (total 150' to and 150' back) of 1/4 or 3/8 copper into the pond. 75 feet of which will be buried 6-7 feet deep all the way to the pond, then the rest will be sunk 6 inches from the bottom of the pond.
I have a spare 6,500btu rotary window unit that I will be harvesting the compressor and evap coil/fan from. Here is where it get tricky. I want to put in a 3 way valve setup on a thermostat that is in the fish tank. It will bypass the evap coil to a non copper coil (copper bad for the fishes) in the fish tank.
Parts Needed:
Compressor I already have
Evap and fan I already have.
Thermostat I already have
300 feet of either 1/4 inch or 3/8 copper tubbing. (ideas? I thinking 1/4 should be ok, but that is a lot of resistance for a 6,500 compressor.)
Oil separator, Jeff5may, you posted a picture of a small oil separator in the 4ton thread, I'm having the worse luck finding one small enough for half ton. Do you happen to know where that image came from? Or does anyone know where to find one? I know they are used on extreme computer chillers but have been unable to find where they get them, because most are not built in the states. I found this one Q E HVAC R Refrigeration Oil Separator 1 2" ODS New | eBay but I know its too big and will probably not cycle the oil back at the right time/volume for a small compressor.
3 way valve. I'm thinking this will be fine, Ranco V3 310081 7GD B1227308 3 Way 1 2 Ton Reversing Valve 10283 | eBay

I will start building just as soon as parts arrive, I'm tired of keeping two fires going in the winter.

Thanks guys!

MEMPHIS91 is offline   Reply With Quote
Old 09-05-15, 01:16 AM   #2
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

You can use a bullet strainer as an oil separator. Supco no. SUD 115 is the common one. Two Tubes facing up, single tube facing down. Bottom tube feeds long, small diameter cap tube back to suction line.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
MEMPHIS91 (09-05-15)
Old 09-05-15, 11:17 AM   #3
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Jeff, Thanks I'm looking into that right now. I know I should have ordered more of those. I just used my last one. I can't seem to find this application of the SUD115 anywhere. Makes total sense though. Would 2 of them back to back be safer?

Shopping list.
Stainless steel coil for the aquaponics heat exchanger http://www.ebay.com/itm/304-304L-Sta...-/290552612112

45% Silver braze to braze the copper to the stainless http://www.ebay.com/itm/98102-Lucas-...item2357e81a0a

SUD 115 Modified drier/ Oil Separator http://www.ebay.com/itm/Copper-Liqui...item3f4eb94254

3 way valve http://www.ebay.com/itm/RANCO-V3-310...item3378ddafdf

I'm getting the 300 feet of 3/8 copper locally because its much cheaper that way. And I know what I'm getting.

Last edited by MEMPHIS91; 09-05-15 at 06:19 PM..
MEMPHIS91 is offline   Reply With Quote
Old 09-26-15, 11:46 AM   #4
marx290
Vapor Compression Goon
 
marx290's Avatar
 
Join Date: Mar 2013
Location: Portland, OR
Posts: 63
Thanks: 11
Thanked 22 Times in 11 Posts
Send a message via Yahoo to marx290
Default

Quote:
Originally Posted by jeff5may View Post
You can use a bullet strainer as an oil separator. Supco no. SUD 115 is the common one. Two Tubes facing up, single tube facing down. Bottom tube feeds long, small diameter cap tube back to suction line.
That is great! I wasn't sure if it would work. My best plan of attack for a oil return, was a sort of vortex separator on the discharge of the compressor, where oil would tend to fall to the bottom. A capillary tube would carry oil back to the compressor suction. I figure some sort of strainer would be advisable, in order to avoid plugging the capillary oil return line. I suspect that even a well designed system would compromise volumetric efficiency slightly, but would certainly be necessary for compressor health in some instances. Then again, keeping the heat exchanger walls cleared of oil, could improve thermal transfer too.

That's interesting. Thank you
__________________

To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
marx290 is offline   Reply With Quote
Old 09-26-15, 06:06 PM   #5
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

marx290, thanks for the links, the link was down, but I did find a google drive through that same site with a GOLD MINE of info.
https://drive.google.com/folderview?...DQ&usp=sharing

I am just now fully learning the P-H diagrams. I was always a try try try try til it fails then try try try again til it work kinda guy. But I am putting tons of research into this build. So I knew I needed to start with some basics of the math/science behind it all.
MEMPHIS91 is offline   Reply With Quote
Old 09-29-15, 06:19 PM   #6
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Progress has been made!
So I started just loose fitting things. First the discharge on the compressor to the intake on the oil sep, not the best idea I know, see below. -1/2"-

And the discharge of the oil sep into the reversing valve -1/2"-
.
I knew the discharge from the compressor would have too much vibration to have a straight run to the oi sep, so I fixed it with a big loop.

The evap(now the condenser) had 2 cap tubes, so 2 intakes, I saved the cap tube and brazed some 1/4" onto them.

Then I ran the 1/2" from one side of the discharge of the reversing valve to the 2 1/4" intakes on the condenser.

The 2 1/4" tubes fit perfectly inside the 1/2". BEFORE

Brazed thoroughly. DURING

I was going to clean it up and take another picture, but I decided to move it into place first, and of course picked up the still super hot 1/2" line...... needless to say I am pecking with 2 fingers in between icing the burns in between typing...

Any way, next question, how much oil do I add and do I add it to the oil sep or the compressor? All to poe was drained. I have been looking for a while for the answer, still searching now.
Also I'm think 1/4" is to large for oil return. Would 1/8" be better?
Attached Thumbnails
Click image for larger version

Name:	KIMG0207.jpg
Views:	1608
Size:	389.3 KB
ID:	5965   Click image for larger version

Name:	KIMG0208.jpg
Views:	1642
Size:	373.0 KB
ID:	5966   Click image for larger version

Name:	KIMG0210.jpg
Views:	1580
Size:	331.9 KB
ID:	5967   Click image for larger version

Name:	KIMG0211.jpg
Views:	1619
Size:	349.5 KB
ID:	5968   Click image for larger version

Name:	KIMG0212.jpg
Views:	1584
Size:	357.0 KB
ID:	5969  

Click image for larger version

Name:	KIMG0213.jpg
Views:	1408
Size:	314.5 KB
ID:	5970   Click image for larger version

Name:	KIMG0214.jpg
Views:	1467
Size:	339.8 KB
ID:	5971  
MEMPHIS91 is offline   Reply With Quote
The Following User Says Thank You to MEMPHIS91 For This Useful Post:
jeff5may (02-21-16)
Old 10-02-15, 07:37 AM   #7
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Howdy guys I got a lot more done thanks to the help of a GOOD friend.

First I swagged the 3/8" lines, its SO much easier than 1/4"


Then I laid out the line, brazed it all up, pulled a vaccum for several hours, made sure I had NO leaks, then zip tied about 20 bricks to the end that is going in the water.



Then the digging started, I got down to 9 feet deep in some places, but never less than 6 feet. When we got close to the pond the machine tried to slip and almost went for a swim, so I will have to dig about a 4 foot spot by hand.




I insulated 2 feet down as it came into the green house.
Attached Thumbnails
Click image for larger version

Name:	KIMG0216.jpg
Views:	1490
Size:	356.8 KB
ID:	5990   Click image for larger version

Name:	KIMG0217.jpg
Views:	1413
Size:	306.6 KB
ID:	5991   Click image for larger version

Name:	KIMG0219.jpg
Views:	1534
Size:	465.4 KB
ID:	5992   Click image for larger version

Name:	KIMG0220.jpg
Views:	1484
Size:	363.8 KB
ID:	5993   Click image for larger version

Name:	KIMG0221.jpg
Views:	1346
Size:	434.5 KB
ID:	5994  

Click image for larger version

Name:	KIMG0222.jpg
Views:	1420
Size:	387.8 KB
ID:	5995   Click image for larger version

Name:	KIMG0223.jpg
Views:	1446
Size:	391.9 KB
ID:	5996   Click image for larger version

Name:	KIMG0224.jpg
Views:	1398
Size:	425.9 KB
ID:	5997   Click image for larger version

Name:	KIMG0225.jpg
Views:	1494
Size:	334.9 KB
ID:	5998   Click image for larger version

Name:	KIMG0232.jpg
Views:	1351
Size:	327.6 KB
ID:	5999  

MEMPHIS91 is offline   Reply With Quote
Old 09-06-15, 11:28 AM   #8
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Here's a good article on oil separation:Oil management in a refrigeration system - Carly : the international expert in refrigeration components


If you use the service valve for your gas outlet, you can flare your stainless line and save some trouble.
jeff5may is offline   Reply With Quote
Old 09-06-15, 05:20 PM   #9
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Jeff, again awesome info. Seriously if you are ever in Oxford, look me up. I owe you a beer, and solar cooked organic homemade meal.
Just added this to this list of parts needed BC49X11 Supco Capillary Cap Tube 049 ID x 11 ft Series for Refrigerators AC | eBay

Sadly I will have to come out of the oil separator to a 3 way valve THEN into the stainless steel coil. So its all brazing looks like, but the %45 silver should flow really nice.
I'll be posting a diagram soon.

UPDATE: Found this quote from a really good read, "Actually it's just a "strainer" with nothing more then a screen inside. And yes the basic idea is that the larger internal volume of the strainer as compared to the 3/16"od tubing feeding into it, will allow the velocity to decrease, thereby letting the heavier liquid drop away from the gas. Same principle of any phase separator, this one just happens to be rather small (and cheap).

Of course an even better phase separator has the refrigerant entering from the side, taking advantage of centrifugal force (not just gravity) to separate the liquid from the gas."

-http://www.xtremesystems.org/forums/showthread.php?144007-Morphing-Air-Conditioner-into-Autocascade-System

Last edited by MEMPHIS91; 09-07-15 at 04:25 PM..
MEMPHIS91 is offline   Reply With Quote
Old 09-12-15, 11:17 AM   #10
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by MEMPHIS91 View Post
Jeff, again awesome info. Seriously if you are ever in Oxford, look me up. I owe you a beer, and solar cooked organic homemade meal.
Just added this to this list of parts needed BC49X11 Supco Capillary Cap Tube 049 ID x 11 ft Series for Refrigerators AC | eBay

Sadly I will have to come out of the oil separator to a 3 way valve THEN into the stainless steel coil. So its all brazing looks like, but the %45 silver should flow really nice.
I'll be posting a diagram soon.

UPDATE: Found this quote from a really good read, "Actually it's just a "strainer" with nothing more then a screen inside. And yes the basic idea is that the larger internal volume of the strainer as compared to the 3/16"od tubing feeding into it, will allow the velocity to decrease, thereby letting the heavier liquid drop away from the gas. Same principle of any phase separator, this one just happens to be rather small (and cheap).

Of course an even better phase separator has the refrigerant entering from the side, taking advantage of centrifugal force (not just gravity) to separate the liquid from the gas."

-http://www.xtremesystems.org/forums/showthread.php?144007-Morphing-Air-Conditioner-into-Autocascade-System
The two or three main posters in the cited thread are regulars on the xtreme forum. They do this refrigeration "alchemy" for a living, so they can be a great help to you and the rest of us. Unlike other forums, these people have no problem with giving a straight answer to the questions that we have difficulty with. Especially with respect to design parameters of an "unconventional" nature.Reading lots of threads over there, as well as asking the right questions of the individual experts, helped me immensely in understanding the theory behind how these rigs do what they do.
jeff5may is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:17 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design