Old 03-26-11, 10:48 AM   #1
rhino 660
Apprentice EcoRenovator
 
Join Date: Oct 2010
Posts: 105
Thanks: 0
Thanked 10 Times in 8 Posts
Default gshp in florida ac only

i have read most of the heat pump manifesto and joined the site because of it
i am the installer for a solar pv and thermal company.

my soil temp is 70* from 2' to 6' didnot go farther
my plan was to retrofit my existing ac system with a refrigerant to water heat exchanger on the condenser side like this one
www .aquasystemsinc. com/models_test.html Aqua Systems efficient Liquid to Refrigerant Heat Exchangers there only $140 for the 2 ton unit. the owner is very helpfull and has some geo thermal experience
and connect a slinky loop field to the exchanger and cool the condenser
but now i plan on using a FHP 24,000btu geothermal heatpump (Florida Heat Pump)
my house is 1000 sq ft and i have a 2 ton ac unit and resistance heating

i have plenty of space for a slinky coil trench and maybe free access to a backhoe.

my plan is to dig down 6' where the soil is very moist and lay my slinky.

the heat exchanger guy gave me a figure of 100' of trench per ton with 400' of pipe in the 100' trench

i have also heard that 600 foot of pipe slinky will fit in 65' of trench im guessing tighter spacing.

i was thinking of diging 3 trenches around 80' long 3' wide and 6' deep
and putting in around 750' of pipe in each trench. i located 800' roles of hdpe 3/4'' pipe which would leave me 25' extra on each input and output to reach my heat exchanger with no welds at all

any helpfull insite i think i have it figured out it seems simple
do you think i should see a large efficiency increase based on my soil temp of 70*


thanks joe
sebring fl 33876


Last edited by rhino 660; 02-16-12 at 09:23 PM..
rhino 660 is offline   Reply With Quote
Old 03-26-11, 03:34 PM   #2
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 960
Thanks: 188
Thanked 110 Times in 86 Posts
Default

Quote:
Originally Posted by rhino 660 View Post
my soil temp is 70* from 2' to 6' didnot go farther
[...]
i am only concerned with cooling my house there is plenty of heat outside lol
everything i have read is geared towards heating homes. anybody know about the cooling aspect of geothermal?
How cold do you want your house? Is a max of 72°-74°F enough? If you can live with that, then you don't need a heat pump, but instead you could cool with 70° water directly. This would greatly
  • increase the simplicity,
  • decrease the cost,
  • increase the efficiency,
of the set-up.

That temperature may also be low enough to dehumidify the air.
__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
Old 03-26-11, 05:59 PM   #3
rhino 660
Apprentice EcoRenovator
 
Join Date: Oct 2010
Posts: 105
Thanks: 0
Thanked 10 Times in 8 Posts
Default

i thought that even with the 70* ground loop temp i could only get the house to 78* or so
72* would be perfect but seems to good to be true
rhino 660 is offline   Reply With Quote
Old 03-26-11, 08:32 PM   #4
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

Quote:
Originally Posted by rhino 660 View Post
i thought that even with the 70* ground loop temp i could only get the house to 78* or so
72* would be perfect but seems to good to be true
That depends on the performance of your heat exchanger, and how quickly you need to remove heat from the house to hold that temperature.
RobertSmalls is offline   Reply With Quote
Old 03-27-11, 02:24 AM   #5
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 960
Thanks: 188
Thanked 110 Times in 86 Posts
Default

Yeah, either good thermal insulation of the house, or a good HX with a ground loop that can quickly take in the heat, would work. Of course, insulation is the better option.

I wonder if it would be possible to get rid of the ground loop's heat at night, say some outdoor HX?
__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
Old 03-27-11, 08:41 AM   #6
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

I wish that I had some 70F ground. My basement floor is holding at just under 50F these days...

If you had some surface freeze protection, you wouldn't even need a water-glycol mix.

Anyways, I wonder if you have any ground water in the area?
Otherwise some of that heat you are pumping into the ground might built up after a while.
Xringer is offline   Reply With Quote
Old 03-27-11, 10:24 AM   #7
rhino 660
Apprentice EcoRenovator
 
Join Date: Oct 2010
Posts: 105
Thanks: 0
Thanked 10 Times in 8 Posts
Default

Quote:
Originally Posted by Piwoslaw View Post
Yeah, either good thermal insulation of the house, or a good HX with a ground loop that can quickly take in the heat, would work. Of course, insulation is the better option.

I wonder if it would be possible to get rid of the ground loop's heat at night, say some outdoor HX?
i have thought of this and now that i have heard it from someone else, i think i will do it... maybe with a automotive style radiator and fan and have it automatically controlled by temp difference and as an assist under full load
rhino 660 is offline   Reply With Quote
Old 03-27-11, 10:32 AM   #8
rhino 660
Apprentice EcoRenovator
 
Join Date: Oct 2010
Posts: 105
Thanks: 0
Thanked 10 Times in 8 Posts
Default

Quote:
Originally Posted by Xringer View Post
I wish that I had some 70F ground. My basement floor is holding at just under 50F these days...

If you had some surface freeze protection, you wouldn't even need a water-glycol mix.

Anyways, I wonder if you have any ground water in the area?
Otherwise some of that heat you are pumping into the ground might built up after a while.
at 5' 6'' there is wet clay and i think somewhere around 6'-7' there is ground water
the guy i spoke to with the heat exchanger said that for my application wet ground is the best because the heat tries to drive the moisture away from the loop feild




my concerns really are with adapting my existing a/c unit
any thoughts
thanks for the replies
rhino 660 is offline   Reply With Quote
Old 03-27-11, 10:50 AM   #9
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Those heat exchangers have 2 inputs and outputs for the water.
That seems like some extra plumbing is going to be required.

What is your 'existing ac system'? What will be required to adapt it to connect to the new exchanger?
Xringer is offline   Reply With Quote
Old 03-27-11, 08:54 PM   #10
rhino 660
Apprentice EcoRenovator
 
Join Date: Oct 2010
Posts: 105
Thanks: 0
Thanked 10 Times in 8 Posts
Default

Quote:
Originally Posted by Xringer View Post
Those heat exchangers have 2 inputs and outputs for the water.
That seems like some extra plumbing is going to be required.

What is your 'existing ac system'? What will be required to adapt it to connect to the new exchanger?
yea just a little extra brazing on the water side.
my a/c system is 24,000 btu's with an outdoor and indoor air exchangers
hookup as far as i know will involve removing outdoor exchanger and brazing in the new water exchanger

rhino 660 is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 04:37 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design