Old 03-13-14, 03:52 PM   #91
dhaslam
Lurking Renovator
 
Join Date: Oct 2012
Location: Co Tipperary, Ireland
Posts: 21
Thanks: 0
Thanked 11 Times in 11 Posts
Default

That doesn't sound right. I use a calculation of about 6 watts per metre which would be about 7 watts per foot pipe run. I have 1/2 mile of pipe for a 2500 sq' bungalow. Of course being close to passive standard less than half if the circuits are used normally. South facing rooms and kitchen usually have enough passive heat.

dhaslam is offline   Reply With Quote
The Following User Says Thank You to dhaslam For This Useful Post:
buffalobillpatrick (03-21-14)
Old 03-13-14, 04:23 PM   #92
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by buffalobillpatrick View Post
From another site:

"R290 and R22 have different liquid densities, and different enthalpy change in the evap. The result is that a TXV rated for R22 but used with R290 will have ~3.5 times the capacity"
Is a TXV a density controlled device? No. It is controlled by pressure. Spring pressure + evaporator pressure vs. sensing bulb pressure. Bulb pressure drops at lower temps, thus the spring wins and the valve moves closed. Outdoor temperature rises, so evaporator pressure rises also; evaporator wins and valve opens until sensing bulb pressure rises. This maintains constant superheat at the sensing bulb, assuring the compressor is not starved or flooded.

Since R22 and Propane have very similar pressure vs. temperature (PT) values, the valve acts very much the same with either. At 0 degF, they are within 0.2 psi of each other. At 100degF, R22 is at 196 psi, where R22 is at 175 psi. At 40 degF (a value in normal range), R22 wins by 4 psi. So as temperature increases, a TXV tuned for R22 but running propane will show a teensy bit of rising superheat in the evaporator. This actually works in our favor. Since propane has higher heat capacity than R22, it doesn't superheat as much in the compressor.

The author of the quote referenced probably got his refrigerants confused. R600 (butane) has around 1/3 the static vapor pressure of R290 or R22. So if you had an imaginary heat pumping thing that ran off butane and put propane in it (and didn't blow something up), it would use more energy, be less efficient, and have more capacity. Kind of like taking an R22 heat pump and filling it full of R410a. If the pipes didn't burst, and the compressor could survive the increased head pressure and compression ratio, and you could adjust the TXV enough to work, you would move more heat.

The more common and logical thing to do is to go the other way. Take a unit designed for R410a with a random problem, but a good compressor and change the gas and TXV. At reduced pressure and compression ratio, the compressor would use less power. You would lose capacity, but with oversized heat exchangers (originally designed for the higher capacity), efficiency (AKA COP, HSPF, SEER) would soar.

Last edited by jeff5may; 03-13-14 at 04:51 PM..
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (03-13-14)
Old 03-13-14, 05:14 PM   #93
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

In the first cited article, in the paragraph directly below table 1, it states R22 pressure is roughly 350% of R600a at -25 degC. Thus the statement is invalid and proves my previous rhetoric. Na na boo boo.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (03-13-14)
Old 03-13-14, 06:05 PM   #94
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Quote:
Originally Posted by jeff5may View Post
The more common and logical thing to do is to go the other way. Take a unit designed for R410a with a random problem, but a good compressor and change the gas and TXV. At reduced pressure and compression ratio, the compressor would use less power. You would lose capacity, but with oversized heat exchangers (originally designed for the higher capacity), efficiency (AKA COP, HSPF, SEER) would soar.
I have done just that with great success. The main efficiency advantage is that the evaporating temperature can be much higher than usual. In a heat pump water heater application, getting the 140F or so needed for washing dishes would not put very much stress on the compressor.
http://ecorenovator.org/forum/geothe...ssor-r290.html
It's also a good fix for an oversized system.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (03-13-14)
Old 03-13-14, 06:15 PM   #95
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

So it would be good for a DHW system, especially one with a high temperature split. I was considering this for a heat pump water heater that ran off an outside air source. When it gets cold outside, the temp split could rise to above 100 degF. How much do you derate an R410a compressor to match R290/R22 capacity?
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (03-13-14)
Old 03-13-14, 07:45 PM   #96
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Something like 2/3 the original capacity, but note that it would be able to operate at higher evaporating temperature than a conventional design, at which point there would be less capacity loss.

If it might operate in below zero conditions, hot gas defrost would be more efficient than a reversing valve.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following 2 Users Say Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (03-21-14), jeff5may (03-14-14)
Old 03-13-14, 07:59 PM   #97
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Quote:
Originally Posted by buffalobillpatrick View Post
It looks like 2 x parallel loops of 250' of 3/4" pex,

with flow of 3.65 gpm in each loop

at Delta T of 20* F , (tank vs. water inside pex)

should transfer about 15 Tons of heat = 180K btus

At a head loss of 7.65'

HL = K x C x L x F^1.75
K = .0034, C = .933, L = 250, F = 3.65

Way more than enough HX for radiant floors.

BBP
3.65gpm is a bit high for 3/4" tubing. I would make it 3 -4 loops and drop the flow rate. Your reynolds numbers will still be good for heat transfer and the head will drop a lot.

Sorry if I am way back of the pack conversation, haha
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (03-13-14)
Old 03-13-14, 09:09 PM   #98
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

I found this today:

35* C liquid: R290 has 43% lower viscosity & 21% better thermal conductivity than R22

-20* C vapor: R290 has 34% lower viscosity & 62% better thermal conductivity than R22

R290 will allow my 2T scroll R410a compressor to run cooler, draw less amps, & put out less pressure. Coupled with my huge HX's I should get pretty good COP ?

BTW, I need to size the High Pressure Cutout switch, should I get 360psi (just below 363psi stated capicity of 1/2" Mueller ACR soft) ?

BBP
buffalobillpatrick is offline   Reply With Quote
The Following User Says Thank You to buffalobillpatrick For This Useful Post:
jeff5may (03-14-14)
Old 03-13-14, 09:14 PM   #99
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

You should be able to find a grade of 1/2" with a higher working pressure.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (03-13-14)
Old 03-13-14, 09:50 PM   #100
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Surplus City

These gauges look pretty good for 80 cents:

2" DIAMETER HIGH PRESSURE GAUGE, RANGE: O TO 600 PSI, INCLUDES MOUNTING BRACKET

SCL # : 11199

MFG : ASHCROFT

MFG # : 733-16

Alt Part # : R5891

buffalobillpatrick is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:20 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design