03-13-14, 03:52 PM | #91 |
Lurking Renovator
Join Date: Oct 2012
Location: Co Tipperary, Ireland
Posts: 21
Thanks: 0
Thanked 11 Times in 11 Posts
|
That doesn't sound right. I use a calculation of about 6 watts per metre which would be about 7 watts per foot pipe run. I have 1/2 mile of pipe for a 2500 sq' bungalow. Of course being close to passive standard less than half if the circuits are used normally. South facing rooms and kitchen usually have enough passive heat.
|
The Following User Says Thank You to dhaslam For This Useful Post: | buffalobillpatrick (03-21-14) |
03-13-14, 04:23 PM | #92 | |
Supreme EcoRenovator
|
Quote:
Since R22 and Propane have very similar pressure vs. temperature (PT) values, the valve acts very much the same with either. At 0 degF, they are within 0.2 psi of each other. At 100degF, R22 is at 196 psi, where R22 is at 175 psi. At 40 degF (a value in normal range), R22 wins by 4 psi. So as temperature increases, a TXV tuned for R22 but running propane will show a teensy bit of rising superheat in the evaporator. This actually works in our favor. Since propane has higher heat capacity than R22, it doesn't superheat as much in the compressor. The author of the quote referenced probably got his refrigerants confused. R600 (butane) has around 1/3 the static vapor pressure of R290 or R22. So if you had an imaginary heat pumping thing that ran off butane and put propane in it (and didn't blow something up), it would use more energy, be less efficient, and have more capacity. Kind of like taking an R22 heat pump and filling it full of R410a. If the pipes didn't burst, and the compressor could survive the increased head pressure and compression ratio, and you could adjust the TXV enough to work, you would move more heat. The more common and logical thing to do is to go the other way. Take a unit designed for R410a with a random problem, but a good compressor and change the gas and TXV. At reduced pressure and compression ratio, the compressor would use less power. You would lose capacity, but with oversized heat exchangers (originally designed for the higher capacity), efficiency (AKA COP, HSPF, SEER) would soar. Last edited by jeff5may; 03-13-14 at 04:51 PM.. |
|
The Following User Says Thank You to jeff5may For This Useful Post: | buffalobillpatrick (03-13-14) |
03-13-14, 05:14 PM | #93 | |
Supreme EcoRenovator
|
Quote:
|
|
The Following User Says Thank You to jeff5may For This Useful Post: | buffalobillpatrick (03-13-14) |
03-13-14, 06:05 PM | #94 | |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
Quote:
http://ecorenovator.org/forum/geothe...ssor-r290.html It's also a good fix for an oversized system.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
|
The Following User Says Thank You to NiHaoMike For This Useful Post: | buffalobillpatrick (03-13-14) |
03-13-14, 06:15 PM | #95 |
Supreme EcoRenovator
|
So it would be good for a DHW system, especially one with a high temperature split. I was considering this for a heat pump water heater that ran off an outside air source. When it gets cold outside, the temp split could rise to above 100 degF. How much do you derate an R410a compressor to match R290/R22 capacity?
|
The Following User Says Thank You to jeff5may For This Useful Post: | buffalobillpatrick (03-13-14) |
03-13-14, 07:45 PM | #96 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
Something like 2/3 the original capacity, but note that it would be able to operate at higher evaporating temperature than a conventional design, at which point there would be less capacity loss.
If it might operate in below zero conditions, hot gas defrost would be more efficient than a reversing valve.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
The Following 2 Users Say Thank You to NiHaoMike For This Useful Post: |
03-13-14, 07:59 PM | #97 | |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
Quote:
Sorry if I am way back of the pack conversation, haha |
|
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (03-13-14) |
03-13-14, 09:09 PM | #98 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
I found this today:
35* C liquid: R290 has 43% lower viscosity & 21% better thermal conductivity than R22 -20* C vapor: R290 has 34% lower viscosity & 62% better thermal conductivity than R22 R290 will allow my 2T scroll R410a compressor to run cooler, draw less amps, & put out less pressure. Coupled with my huge HX's I should get pretty good COP ? BTW, I need to size the High Pressure Cutout switch, should I get 360psi (just below 363psi stated capicity of 1/2" Mueller ACR soft) ? BBP |
The Following User Says Thank You to buffalobillpatrick For This Useful Post: | jeff5may (03-14-14) |
03-13-14, 09:14 PM | #99 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
You should be able to find a grade of 1/2" with a higher working pressure.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
The Following User Says Thank You to NiHaoMike For This Useful Post: | buffalobillpatrick (03-13-14) |
03-13-14, 09:50 PM | #100 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
Surplus City
These gauges look pretty good for 80 cents: 2" DIAMETER HIGH PRESSURE GAUGE, RANGE: O TO 600 PSI, INCLUDES MOUNTING BRACKET SCL # : 11199 MFG : ASHCROFT MFG # : 733-16 Alt Part # : R5891 |
|
|