Old 07-06-14, 08:13 AM   #21
stef110
Helper EcoRenovator
 
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
Default

yesterday i received a vacuum meter and a schrader valve so that i can make an extra service port.
The problem is that with my current vacuum pump i reach about 1000 microns of vacuum will this be enough?
I also made a little movie of the brazing i did to day.



stef


Last edited by Daox; 07-15-14 at 04:42 PM..
stef110 is offline   Reply With Quote
Old 07-06-14, 08:55 PM   #22
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

I don't know if other people are have trouble with your brazing video, but I had to go to "page source" and hunt down the URL, so I am re-posting it here...




But back to your micron gauge issue, in my opinion, 1000 microns is not so good.

I have found that fresh vacuum pump oil is extremely important. If you didn't do it already, I would recommend completely draining your vacuum pump, and replacing the oil with new, fresh vacuum pump oil that is being poured out of a newly-opened container.

I have seen fresh vacuum pump oil bring a vacuum pump to life.

Good luck!!

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 07-15-14, 02:34 PM   #23
stef110
Helper EcoRenovator
 
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
Default

I replaced the vacuum oil and cleanup the vacuum sensor.
Today i reached 300 microns will this also bee acceptable?
or should i search for a better pump?

stef
stef110 is offline   Reply With Quote
Old 07-15-14, 04:13 PM   #24
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

I read 500 microns or better are acceptable .

God bless
wyr
WyrTwister is offline   Reply With Quote
Old 07-15-14, 04:31 PM   #25
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by stef110 View Post
I replaced the vacuum oil and cleanup the vacuum sensor.
Today i reached 300 microns will this also bee acceptable?
or should i search for a better pump?

stef
You're OK.

Pull your vacuum, and keep an eye on the gauge you'll probably see it go down to it's minimum... keep pumping... you may see the readings 'jump' a bit... this is water vaporizing out.

You should keep pumping for maybe an hour. Vacuum pumps are built for that kind of use.

Get a good book to read while you're waiting.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-15-14 at 04:35 PM..
AC_Hacker is offline   Reply With Quote
Old 07-16-14, 12:02 AM   #26
stef110
Helper EcoRenovator
 
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
Default

I managed to get this reading after 2 hours, with also running a cooling fan on the pump.
On the internet I already found a second handed dual stage yellow jacked pump.
The gauge I use had some leds, and not a digital value to read.


Stef
stef110 is offline   Reply With Quote
Old 07-16-14, 02:14 PM   #27
stef110
Helper EcoRenovator
 
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
Default

Pump is running as we speak for about 4 hours and it stil stuck at 300 microns.
Even when i close the valves to unit so i only suck at the hose between pump and meter set, it stays at 300 microns.

On a manual if found it says, if you reach 400 microns and you close valve at pump side and the vacuum will go from 400 to about 600 a 700 microns in two minutes your system will be oke. Is this correct?

Will this be oke? if yes or no please tell me then can reject or accept the buy of the new pump.


stef110 is offline   Reply With Quote
Old 07-16-14, 02:37 PM   #28
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by stef110 View Post
Pump is running as we speak for about 4 hours and it stil stuck at 300 microns.
Even when i close the valves to unit so i only suck at the hose between pump and meter set, it stays at 300 microns.

On a manual if found it says, if you reach 400 microns and you close valve at pump side and the vacuum will go from 400 to about 600 a 700 microns in two minutes your system will be oke. Is this correct?

Will this be oke? if yes or no please tell me then can reject or accept the buy of the new pump.


I think you're good to go.

You should charge it up now...

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
stef110 (07-21-14)
Old 07-21-14, 12:58 PM   #29
stef110
Helper EcoRenovator
 
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
Default

Today i finally released the gas in to the circuit.
For a fast test i hooked up a water pump and a bucked of water to test it and it worked



A question the 4-way valve when should you switch it? at the same time the compressor starts en when do you cut if off? when the compressor quits?

stef
stef110 is offline   Reply With Quote
Old 07-21-14, 01:18 PM   #30
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by stef110 View Post
Today i finally released the gas in to the circuit.
For a fast test i hooked up a water pump and a bucked of water to test it and it worked


Welcome to the Club of Obsessed Madmen!


Quote:
Originally Posted by stef110 View Post
A question the 4-way valve when should you switch it? at the same time the compressor starts en when do you cut if off? when the compressor quits?

stef
It's a bit difficult to understand your setup from your photo, etc.

How do you plan to use your heat pump?

To warm?

To Cool?

To do both?

Your 4-way valve probably has a "default" position that it goes to when it is not energized (no volts applied). Set up your heat pump so that the defalut position of your 4-way valve will result in the configuration you want to use most often.

Then energize the 4-way valve when you desire the opposite (less often used) functioning.

And yes, your 4-way does not need to be energized when the compressor is not running.

-AC

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...

Last edited by AC_Hacker; 07-21-14 at 01:21 PM..
AC_Hacker is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 05:48 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design