01-29-13, 08:01 AM | #381 | ||
Helper EcoRenovator
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
|
Quote:
About cleaning, I think the best thing to do is installing at least a basic polyester filter, a specific HRV/ERV or furnace filter would be better. If you frame the plates like I did (forget the plywood caps, I'll change that with two metal sheets per core) you can wash the whole HX by immersing it to a tank of warm water and some mild soap. For a coplete sanitation add some specific detergent and rinse. Quote:
Just kidding, the small cores you see are the first ones I built to do some testings to see the aforementioned differences between the various materials and configurations. Once rejected the PP distanced version and confirmed the equality between PP and aluminum sheets I decided to use all the material I had and made up the two big cores I'm currently using in the HRV. |
||
01-29-13, 04:20 PM | #382 |
Helper EcoRenovator
Join Date: Dec 2011
Location: tigard, oregon
Posts: 42
Thanks: 0
Thanked 4 Times in 4 Posts
|
Thanks for the info.
The whole metrology problem is why I don't chase 100% efficiency. The goal is to subtract two equal numbers. But, as you approach that equality, the measurement error in the numbers gets dramatically worse. And air flow measurement is much worse. 20% error in the flows is a computational disaster. My toy HRV has no ducts, so it's nearly impossible for me to get accurate measurements under true operating conditions. Current inside/outside differential is only 14F. Makes no sense to attempt any measurements. If I understand correctly, you have one symmetrical core of aluminum and another that alternates coroplastic channels and wide-open areas. How much difference that makes to the relative air flows is back pressure and fan dependent. I tweaked mine for zero inside/outside pressure differential. The fan speeds are significantly different. I like the direct measurement approach. Measure what's important to you. For me, the bottom line is operating cost. If I had a ducted system like yours, here's what I'd do. I'd stick a heating element in the plenum inside the box at port4. I'd poke a 3/4" sense port in ducts 3 and 4 far enough away that turbulence has stabilized the air temperature. If you stick a velocity meter in the hole, you'll get a wide range of velocities depending on how far you stick it in. But if you go for the peak somewhere in the middle, you should be able to adjust the fans so that the air speed is equal in ports 3 and 4. Now, heat up the heating element until the temperatures are equal at the sense ports in 3 and 4. The amount of heat necessary to do that is a direct measurement of what it costs to operate. To be clear, I don't propose you heat the air. It's just a temporary measurement technique. Humidity measurement is another problem area. I have a decent humidity probe, but the settling time is about an hour. I have to keep the dew point above 43F or so or I get sinus problems. So my HRV dumps a lot of water. |
01-29-13, 04:24 PM | #383 |
Helper EcoRenovator
Join Date: Oct 2012
Location: Beuningen (Gld), the Netherlands
Posts: 64
Thanks: 4
Thanked 19 Times in 16 Posts
|
Some pictures from my build: Here
Some even come with comments. The whole album is in reverse since the forum thinks it is a splendid idea to put the latest picture first, so do start with the last one and then click on previous. There are more pictures on my camera, those will follow soonish. Last edited by Fornax; 01-29-13 at 04:37 PM.. |
01-29-13, 05:02 PM | #384 | |
Helper EcoRenovator
Join Date: Oct 2012
Location: Beuningen (Gld), the Netherlands
Posts: 64
Thanks: 4
Thanked 19 Times in 16 Posts
|
Quote:
100% * (T4-T1) / (T3-T1) == 88,2% For the other channel we would get: 100% * (T4-T2) / (T3-T2) == 68,6% <-- wrong formula 100% * (T3-T2) / (T3-T1) == 37,5% <-- correct It appears something was not symmetrical during your testing and it could be the mass of air through both channels. Warmer air is lighter, especially when one stream is 294 Kelvin and the other is 322 Kelvin (9,5% more density for the colder air.) but that alone doesn't account for the 28% difference. Were all the ductwork and the fans identical? With this unballance you do indeed get nice and warm air inside but you are exhausting more air out than re-enters, and the exhausted air is warmer than it should be. On top of that the surplus of exhausted air will be made up by air entering your house via other ways, unheated. ----- In your test the distanced PP core performed poorly. Due to it's construction the two channels in that one will definitely have a different resistance. If your fans cannot handle this different airpressure then you will get weird and unbalanced results, like 45%-ish efficiency in 1 channel. Kostas, could it be you overlooked something? I was as surprised as Ham789 was when you reported that the distanced PP performed so poorly when compared to the stacked PP. We feel it should be the other way around. If you still have that core and the other testing-equipment could you in some way repeat the test and report T1 - T4 (including T2) and then rotate the core 90 degrees and repeat the test? Last edited by Fornax; 02-05-13 at 02:03 PM.. Reason: Wrong formula used, corrected. |
|
01-30-13, 11:19 AM | #385 |
Helper EcoRenovator
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
|
I think the problem with those measurements were the fans I used. The models were similar (looked identical but had no tecnical label on them) and over 10 years old, so I guess the air flows were unbalanced.
There were no ducts except for a piece of pipe (120mm diameter, 1mt long) that i had to use for the hair dryer to prevent the polystyrene casing from melting down. As for the distanced PP core's performance I think the issue is the lack of small channels in the distanced flow which allows more air to pass through exchanging smaller amounts of temperature. Sorry but I no longer have this HX as I used the material to built up the bigger ones I currently use. @ ham789: thanks for your suggestions. I'm still waiting for that anemometer to arrive from the bay... I'll try to measure air flows as soon as possible. |
01-30-13, 01:00 PM | #386 |
Lurking Renovator
Join Date: Oct 2012
Location: Corvallis, Oregon
Posts: 19
Thanks: 1
Thanked 2 Times in 1 Post
|
I'm too am surprised at the low results from what is getting called the distanced PP core. One question that pops to mind is has anybody tried adding some air turbulators (on an aircraft's wing they are vortex generators) to the open channels? I know in some solar hot air collectors gains are observed on extracting the heat from the absorber sheet if a few (~10-20) turbulators are added to the back of a 4'x8' collector. My understanding is that in reducing laminar airflow the temperature gradient of the air at the heat exchanger interface skin is reduced. For these scale heat exchangers running course grit sand paper over the PP might suffice. Although that might increase dust buildup across the entire surface negating any positive change. These should also help to balance the air flow/pressure restriction between the two heat exchanger channels as well.
|
01-30-13, 07:10 PM | #387 |
Helper EcoRenovator
Join Date: Dec 2011
Location: tigard, oregon
Posts: 42
Thanks: 0
Thanked 4 Times in 4 Posts
|
My Toy HRV runs the air straight thru the coroplast
channels, but the open layers have side-exit at each end. That should give some turbulence to the flow. A relatively easy experiment is to cut some coroplast strips just wide enough to be mechanically stable and insert them off-angle into the open channels. That oughta add significant turbulence without reducing the surface area much. Poke a pair of thermocouples down into the one channel and see what difference it makes. A/C has some machine-cut black coroplast squares. Maybe we can convince him to do the experiment. FWIW, some recent construction plans for HRV have a block down the center of the open channels and a reversal space at the end. They run the air down one half and back up the other. That gives some temperature gradient that has some of the benefits of a full counter-flow exchanger. And it's easier to route the ports. I have a very crude thermal imager that was made for firemen to find cold bodies in a flaming building. It won't focus up close, so may not yield useful results, but next cold spell, I'm gonna break it out and see if I can learn anything about the thermal profile from the outside of the exchanger. |
01-31-13, 05:36 PM | #388 |
Lurking Renovator
Join Date: Jan 2013
Location: England
Posts: 1
Thanks: 0
Thanked 0 Times in 0 Posts
|
Hi,
I see lots of good info on here to help me save the heat from the bathroom go out the window. I need to vent the steam out now three girls now take for ever in there. Looking at all the options open to me. I have a flue from a gas warm air/water heater that I would like to incorporate into the system to boost the heat entering the rooms. (just thinking about it). I have a 2.3Kw solar system on my south west roof to offset the power of the motors. Thinking of using the excess solar power to preheat my water to my immersion tank - but that's another project. |
02-01-13, 06:12 AM | #389 |
Helper EcoRenovator
Join Date: Dec 2012
Location: Venice, Italy
Posts: 89
Thanks: 15
Thanked 41 Times in 19 Posts
|
I was working on the operational part of my DIYHRV.
In this hypothesis I used Fornax's Comair motors and tried to figure how the various apparatus I'd like to use generally fit and combine. Here is a first draft: You can also see a small design concept video I uploaded on the Tube: Here is the parts description 1.Fresh air entrance (from roof) 2.Filters chamber (insect metal screen and fine dust or furnace filter). I was also planning to install a small UVC insecticidal lamp here, but it's still a maybe. 3. Pre heating exchanger (low power, hooked on my propane home heater by a separate circuit) 4. Dual coe HX 5. Condense drain metal sink 6. Post heating exchanger (as n.3 but with more power, like 2Kw or so) 7. Humidifier system (don't know how yet, maybe a free dropping water system) 8. Inlet motor 9. In house plenum 10. To the inlet ducts (living room and bedrooms) 11. Stale air plenum and filters (from bathrooms, kitchen and corridor) 12. Exhaust motor 13. Air exit (to the roof). Ducts n.1 and 13 will be obviously much more distant from each other (3mts) Another option would be to intersect them (1 to 13) by a motorized valve for the recycling mode. In winter I'm planning to pre and post heat the incoming air using my heater as long as it takes to change all the air in the house. Pre heating is mandatory to prevent frosting and the post heating fills the temperature gap between the HX outlet and the house ambient. After that the system would switch to the recycling mode for an equal distribution of the internal heat (no pre and post heating). Same work in the summer, when it's hot and humid outside and with the A/C on in the house. (obviously heating is off). If i'ts cooler and less humid outside then motor n.12 goes off and lets only fresh cool air enter the house. What do you guys think? Last edited by Piwoslaw; 02-01-13 at 09:14 AM.. |
02-01-13, 08:24 AM | #390 |
Helper EcoRenovator
Join Date: Dec 2011
Location: tigard, oregon
Posts: 42
Thanks: 0
Thanked 4 Times in 4 Posts
|
Very nice work. What tools did you use to make the drawings?
I think you have a fundamental air flow problem. You want the ports exposed to the outside to be on the same end of the exchanger. If the air doesn't flow in opposite directions, you're giving up the efficiency improvement due to dual cores. You want the greatest possible temperature difference everywhere in the system. Then drive that temperature difference toward zero across the board. I'll say the same thing differently. If you have a counter flow heat exchanger, you do just that. With a long path, you can approach 100%. If you reverse one air flow so they are in the same direction, your output temperatures will be half way between the two temps at the other end. You can't do any better than 50%. On the outside end, you want the outgoing air to flow upward through the wide-open channels so the water can condense and drain back into the warm area instead of toward the freezing end. This won't work so well if you put the air thru smaller coroplast channels because of surface tension and you don't have enough air pressure to blow the water uphill. If all of your channels are small, you'll want the air to flow downward to blow out the water...but I think that will have more freezing issues. Would be interesting to experiment with the plate spacing and surface tension to see what the minimum effective spacing might be. A counter-flow exchanger is intuitive because you can predict the temperature at various places in the core. For cross-flow, it's not so simple. In the output end of the system, the coldest part of the core is at the corner where the coldest incoming air is. Since there is a differential in the average temperatures at the ports, we know that the other corner has to be warmer. The objective is to not freeze up. The warmer air exiting is waste. And it's higher than the colder corner of the exchanger. We need some way to get that heat transferred back into the cold corner. That might be done with a temperature controlled path from the hot part back into the cold part. If you allow ALL the air to flow back, the system temperature will rise to the interior air temperature. So, there's some amount of flow that keeps the coldest corner of the core above freezing. This also affects where you put the fans so the pressures are right to make the air go where you want it. If you live in an area with moderate cold, that's the simplest and most efficient thing I can think of. You trade fresh air for defrosting. Do the math to see if it works in your climate. If you have to add heat, that's also the place to add it. Any more heat than the amount to keep the output port minimum temperature above freezing is wasted. But it's worth a lot of careful thought to verify that. I'd be interested in opposing views on optimum defrosting. I really have little more than intuition to support my claims. |