Default windowshaker heat pump controls hacking

I have a happy little frigidaire FFRH0822R1 - that's an 8k cap tube window mounted heat pump.

it works great down to 40F, where it switches over to the 1kW strip heat, providing less heat, and using more energy than it needs to. I can't fathom a reason they didn't implement defrost other than to save the cost of one additional motor, and an extra ten cents on the control chip.

I plan to re-do the controls (and the outdoor side fan) so that it can operate down to whatever point it is no longer useful. to do this I plan on ditching the factory controls entirely, and switching it over to 24VAC controls.
If anyone sees a flaw in my plan, please point it out to me.



I will be using a Honeywell prestige thermostat, because I like them. YTHX9421R5085WW

I have this defrost board 47D01U-843 due to a friend picking it up for his home system and then upgrading to an inverter split system, so I got a great deal.
It has a number of defrost modes, including a couple of demand modes, so I'll give it a go.

Please note that I do NOT want to open the refrigeration circuit. it's a dual cap tube currently, and has no issues working above 40F, so I see no benefit to messing with the charge/refrigerant choice. That's another idea, for another time in another thread.

Thermostat inputs
User demand
return temp
supply temp
outdoor temp

Thermostat outputs
Y (comp call)
O/B (reversing valve)
G (fan)
W (aux heat)

defrost board inputs
Y
O/B
air temp
coil temp

defrost board outputs
Y
O/B
ODU Fan relay
W for defrost heat

Logic provided by thermostat / demand defrost board
aux heat lockout
compressor lockout
defrost of outdoor coil
short cycle protection
outdoor coil temp sensing
outdoor air temp sensing

Things I won't have without further logic/sensors
protection against strip heat without fan (airflow proving)
low pressure cutout (no plans to implement)
high pressure cutout (no plans to implement)
outdoor coil fan (plan to cut off shaft and add in a 12V radiator fan(due to cost, ease of mounting, availability, and small diameter selection) that will be controlled by the defrost board fan relay.

I think they only remaining tasks will be swapping out the 120VAC reversing valve coil for a 24V coil, and adding a couple relays to trigger the 120V components.

Thoughts?

u3b3rg33k is offline   Reply With Quote
Old 04-23-18, 10:49 PM   #2
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Sounds like your control system is going to be worth more than the unit it is controlling. But who am I to tell you what you can spend in your project? If you wire everything correctly, it should work like a charm!
jeff5may is offline   Reply With Quote
Old 04-24-18, 03:34 PM   #3
u3b3rg33k
Apprentice EcoRenovator
 
Join Date: Mar 2018
Location: Rustbelt, USA
Posts: 114
Thanks: 5
Thanked 10 Times in 9 Posts
Default

Quote:
Originally Posted by jeff5may View Post
Sounds like your control system is going to be worth more than the unit it is controlling. But who am I to tell you what you can spend in your project? If you wire everything correctly, it should work like a charm!
That's quite possible - I'm doing this because I want to repurpose something I own already, it's cheaper than buying a minisplit, or a traditional split system - and it won't require me to pull any permits or get licenses, and I like to tinker, so here I am.
Even it isn't the least expensive way to go about it, I'm thinking my ROI vs resistance heat should be pretty decent. I did that a bit this winter and it was not kind to my electric bill. I might even learn a bit in the process.
u3b3rg33k is offline   Reply With Quote
Old 05-07-18, 09:01 PM   #4
bpatton
Lurking Renovator
 
Join Date: Oct 2017
Location: Tampa, Fl
Posts: 10
Thanks: 2
Thanked 1 Time in 1 Post
Default

Sounds like you have it all tacked down. I've considered doing something similar for a future project. Do post updates when you get it all put together!
bpatton is offline   Reply With Quote
Old 05-08-18, 10:42 AM   #5
u3b3rg33k
Apprentice EcoRenovator
 
Join Date: Mar 2018
Location: Rustbelt, USA
Posts: 114
Thanks: 5
Thanked 10 Times in 9 Posts
Default

so far the high power relays and control board/thermostat are here. I have confirmed fan behavior (on while compressor/strips active) is as needed, so no additional logic for that needs to be built.
u3b3rg33k is offline   Reply With Quote
Old 06-17-18, 04:10 PM   #6
u3b3rg33k
Apprentice EcoRenovator
 
Join Date: Mar 2018
Location: Rustbelt, USA
Posts: 114
Thanks: 5
Thanked 10 Times in 9 Posts
Default

A little progress on disassembly:


a picture of the heat strips:



and because I was wondering if it actually had limit switches:


I plan on removing the exterior fan blade and replacing it with a Spal type car radiator fan (not sure if I can find a 120V fan that's suitable) for defrost, and retaining the stock motor and blades for the interior section. the only minor concern is the motor is an air-over motor, so a failure of the external fan would be bad. not an issue for the winter, as i can't imagine the motor would need extra cooling, but it would be bad if the condenser fan failed to operate in the summer. I can fit about a 12" fan in there without significant modifications to the shroud. I'll set it for intake (like one would a normal full size split) so it's easier to clean the coils without full disassembly.
Attached Thumbnails
Click image for larger version

Name:	disassembly.jpg
Views:	815
Size:	273.8 KB
ID:	8249   Click image for larger version

Name:	heat strips.jpg
Views:	791
Size:	287.4 KB
ID:	8250   Click image for larger version

Name:	limit switches.jpg
Views:	775
Size:	194.2 KB
ID:	8251  
u3b3rg33k is offline   Reply With Quote
Old 06-29-18, 02:59 PM   #7
u3b3rg33k
Apprentice EcoRenovator
 
Join Date: Mar 2018
Location: Rustbelt, USA
Posts: 114
Thanks: 5
Thanked 10 Times in 9 Posts
Default

I've run into a minor hiccup - all of the reasonably priced 12V fans I can find are brushed motors, which means shorter lifespan. anyone have a good idea for a long life fan that might fit at a decent price?

a used SPAL fan would run me $50. a new one $200+
u3b3rg33k is offline   Reply With Quote
Old 06-29-18, 03:00 PM   #8
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

What about replace the indoor fan with a few 120mm computer fans? It's the indoor fan you want variable speed for optimum dehumidification.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 06-29-18, 05:28 PM   #9
u3b3rg33k
Apprentice EcoRenovator
 
Join Date: Mar 2018
Location: Rustbelt, USA
Posts: 114
Thanks: 5
Thanked 10 Times in 9 Posts
Default

it's already got a 3 speed fan. since it's not ECM, I assume the low speed tap without the outdoor fan load will run at a higher RPM than before, so i likely won't want it faster than that. the other issue with replacing the inside fan is fabricating a mount will be more difficult.

to entertain the idea of an indoor fan swap, i'd need a high ambient rated fan motor, since the fan is after the condenser and heat strips when in heat mode. if both are active I anticipate 50C+ air temps.

if I abandon the idea of a used fan for the outdoor half and pay full price, this may suffice:
https://www.supplyhouse.com/Packard-...ly-w-Fixed-RPM
however i will also have to abandon the idea of reversing the airflow through the condenser for ease of cleaning. it will have to push out through the condenser as it's only rated for 40C.
u3b3rg33k is offline   Reply With Quote
Old 06-29-18, 11:48 PM   #10
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

A lot of computer fans are rated for surprisingly high temperatures, because it can get that hot on the exhaust side of a heatsink. But maybe you could add the fans on the inlet side?

I suggest adding a SSR to control the heat strips so it's literally only used as much as it needs to be. In heating mode, you'll want the fans going at high speed because that gives better efficiency. In defrost, slow the indoor fans down so they run just enough to stop the indoor coil from freezing and apply just enough power to the heat strips to counter the little little cold air that comes out. (Or not use them at all if the room temperature is within a few degrees of the setting.)

__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
jeff5may (08-02-18)
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:52 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design