Old 02-20-14, 09:10 AM   #81
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Mini-splits with 'Inverter Technology' start their motors slowly with DC pluses.
There is no instant high power surge with inverter tech.
Brushless DC electric motor - Wikipedia, the free encyclopedia

Motor speed control firmware is written so that M/S motors turn on with a 'Soft Start-up'.


So, I think in the case of a modern Inverter mini-split, the 'LRA' is the actual
AC Amps the mini-split system would draw (via the AC to DC converter),
if the motor locked and couldn't turn.

__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
The Following User Says Thank You to Xringer For This Useful Post:
buffalobillpatrick (05-27-14)
Old 02-20-14, 12:54 PM   #82
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

Quote:
Originally Posted by Xringer View Post
Mini-splits with 'Inverter Technology' start their motors slowly with DC pluses.
There is no instant high power surge with inverter tech.
Brushless DC electric motor - Wikipedia, the free encyclopedia

Motor speed control firmware is written so that M/S motors turn on with a 'Soft Start-up'.


So, I think in the case of a modern Inverter mini-split, the 'LRA' is the actual
AC Amps the mini-split system would draw (via the AC to DC converter),
if the motor locked and couldn't turn.
I am sure you are correct . My 13 SEER mini split has the old technology in which the compressor cycles off & on . So I have no experience with the DC inverter technology .

I have worked with 3 phase AC Variable Frequency Drives . I am guessing the end result is pretty much the same ?

As far as insulating the service fittings and the final few inches of the line set , this is what I used .

https://www.johnstonesupply.com/stor...ep?pID=G21-515

I insulated the small and large lines myself . I could not find a factory made line set in town , in stock .

Before I used the cork tape , the uninsulated large line ( summer operation ) was sweating up a storm . Can not remember if the small one was too ? On mini splits , the expansion device is in the condenser unit , not at the fan coil unit .

By the way , my 13 SEER 12,000 BTU mini split is hooked up with #14/2/WG Romex & feed with a single pole 15 amp circuit breaker ( 120 VAC ) .

God bless
Wyr
WyrTwister is offline   Reply With Quote
The Following User Says Thank You to WyrTwister For This Useful Post:
buffalobillpatrick (05-27-14)
Old 02-20-14, 01:19 PM   #83
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

I wonder how much current it takes to actually pop a 15 amp HACR type breaker?
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 02-20-14, 08:38 PM   #84
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Quote:
Originally Posted by Xringer View Post
So, I think in the case of a modern Inverter mini-split, the 'LRA' is the actual
AC Amps the mini-split system would draw (via the AC to DC converter),
if the motor locked and couldn't turn.
Every inverter drive compressor I have come across uses a sensorless drive as it's expensive to add extra sealed passthroughs for the resolver. As such, it would actually draw very little current trying to start a stalled motor, much less than normal operating current. Most likely it's an equivalent for the capacitive inrush.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (05-27-14)
Old 02-21-14, 02:15 AM   #85
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

Quote:
Originally Posted by Xringer View Post
I wonder how much current it takes to actually pop a 15 amp HACR type breaker?
Reasonable , simple question .

The answer is not quite so simple .

First of all , for continuous load , loads extending 3 hours or longer , or that may extend for that time period . Calculate 80% or the rated amperage for the wire or for the over current device .

80% x 15 amps = 12 amps continuous load .

For non continuous load , m15 amps would be legal , but I would never recommend it .

Now , you have traditional motor start up ( non inverter , soft start , VFD , etc. ) . Wire is sized as stated above . as far as the over current device , when you wade through all the verbiage , it boils down to this .

In a worst case situation , the over current device is allowed to be up sized as much as necessary for the motor to successfully and reliably ride through the motor start inrush .

Lastly , you have instantaneous trip rating . This would be a situation of a direct short to earth ground , hot to neutral or phase to phase ( hot to hot ) .

Different types of fuses and / or circuit breakers are better at dealing with motor inrush , than others . Same for instantaneous trip rating .

Much better to use over current devices for motor applications , that are designed to ride through the inrush , that to use devices that have to be greatly over sized .

HVAC rated circuit breakers should be OK for motor inrush , at least in a residential environment .

All this is rated / calibrated at a " standard " ambient temperature .

My 4 ton central A/C condenser is rated max fuse / circuit breaker 45 amps . Can not remember the min circuit capacity ( which is calculated at 125% of the max running current , to accommodate continuous load ) .

I have 45 amp " slow blow " fuses in the disconnect . Start load is about 45 amps , which falls to around 19 amps or less . It is wired with # 8 copper wire . No problems .

Resistive loads , like resistance heat , or even incandescent lamps , have an inrush , but not as dramatic as motor start inrush . Resistance heat is almost always treated as continuous load , also .

Sorry for being so long winded . :-(

God bless
Wyr
WyrTwister is offline   Reply With Quote
The Following User Says Thank You to WyrTwister For This Useful Post:
buffalobillpatrick (05-27-14)
Old 02-21-14, 08:35 AM   #86
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

I've only seen one breaker pop in my life. It was many years ago.
I had one of the breakers labeled badly and I turned off the wrong breaker.

When I started to work on the outlet box, I did a safety check
and deliberately shorted the hot side to ground (the box).
It melted a little bit off my screw driver and popped the 15A breaker..


Before I built my own electronic breakers, I tried using 15 and 10A breakers on a run-away Sanyo.
The Sanyo would shut itself down at around 3.6 kW (15A @ 240vac),
but the breakers never popped..

Those 10 and 15A breakers weren't the HACR type.. They should have popped, IMHO..
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
The Following User Says Thank You to Xringer For This Useful Post:
buffalobillpatrick (05-27-14)
Old 02-21-14, 09:41 AM   #87
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

Quote:
Originally Posted by Xringer View Post
I've only seen one breaker pop in my life. It was many years ago.
I had one of the breakers labeled badly and I turned off the wrong breaker.

When I started to work on the outlet box, I did a safety check
and deliberately shorted the hot side to ground (the box).
It melted a little bit off my screw driver and popped the 15A breaker..


Before I built my own electronic breakers, I tried using 15 and 10A breakers on a run-away Sanyo.
The Sanyo would shut itself down at around 3.6 kW (15A @ 240vac),
but the breakers never popped..

Those 10 and 15A breakers weren't the HACR type.. They should have popped, IMHO..
what was the time duration ? 15 amp on a 15 amp circuit breaker ? Theoretically could hold in there for up to 3 hours , depending on ambient temperature .

Some CB's are more magnetically activated , than thermally activated . Those are less affected by ambient temp .

God bless
Wyr
WyrTwister is offline   Reply With Quote
The Following User Says Thank You to WyrTwister For This Useful Post:
buffalobillpatrick (05-27-14)
Old 02-22-14, 07:22 PM   #88
nokiasixteth
Journeyman EcoRenovator
 
Join Date: Jan 2014
Location: Earth
Posts: 348
Thanks: 43
Thanked 14 Times in 13 Posts
Default

Waiting on my 220 volt kw meter to come in to check on everything . So far everything is workin good . Only had one prob . Leaked some . But had a kink in the water hose i had cut the hose runnin perfectly. Havin to run ac now been pretty warm now .
nokiasixteth is offline   Reply With Quote
Old 02-23-14, 05:19 AM   #89
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

Please forgive me , but you completely went over my head concerning the water hose ?

Did you cut up a water hose for the condensate drain ?

God bless
Wyr
WyrTwister is offline   Reply With Quote
Old 02-23-14, 06:07 AM   #90
nokiasixteth
Journeyman EcoRenovator
 
Join Date: Jan 2014
Location: Earth
Posts: 348
Thanks: 43
Thanked 14 Times in 13 Posts
Default

Quote:
Originally Posted by WyrTwister View Post
Please forgive me , but you completely went over my head concerning the water hose ?

Did you cut up a water hose for the condensate drain ?

God bless
Wyr
Yeah. I had one that the end got cut off. So i just used it. Works good.

nokiasixteth is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:37 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design