Default purging non-condensable gas from a storage cylinder

I found this information in a pdf www.robinair.com/sites/default/files/25175B.pdf
On page 7. It's also in the manual for my new RG3. (No pdf).

Anyways, I wonder how much this decontaminates R410a that has some air mixed in??

__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 12-28-16, 09:38 AM   #2
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

It works for purging the lineset for refrigerant gauges.

I guess it all depends on your standards of purity. The more air and the lower the tank level, the more headspace gas you will need to pull to remove the air. If the gas is stratified well, most of the air will come out first. Yadda yadda. Better than wasting the whole tank IMO.

The other factor to consider is this: the volume of R-410a that is outgassed to remove air will contain the lightest fraction of the mixture. In effect, you will be distilling out a fraction of the mixture, which could throw off the properties. Just as in distilling moonshine, the heads come out first. In this case, any lost booze is bad. You can use it, but it will not be the perfect blend.
jeff5may is offline   Reply With Quote
Old 12-28-16, 10:27 AM   #3
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Thanks for the reply. I've been thinking about the process of pulling out the charge,
checking it's weight, and then using it to recharge the system..
But, maybe it would be safer to use brand new R410A..?.

I guess the main point of bleeding off the non-condensable gas, is to keep the pressure 'normal'.
So you can keep using the recovery tank without fighting with it's pressure..

I saw this 'guide' to preparing a new tank. Getting rid of all that nasty nitrogen, before use..
https://youtu.be/E6-DDjWvHHU
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 12-29-16, 05:01 PM   #4
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

A method of getting rid of air in a recovery tank is pump the liquid off the bottom
of the tank, into another tank.. https://youtu.be/pDxRnEqSFyE
Too bad, I only own one recovery tank..
__________________
My hobby is installing & trying to repair mini-splits
EPA 608 Type 1 Technician Certification ~ 5 lbs or less..
Xringer is offline   Reply With Quote
Old 01-04-17, 05:35 PM   #5
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

I have seen refrigerant purge systems on R11 centrifugal chillers . In operation , the were running less than 1 atmosphere suction pressure and some what above 1 atmosphere on the high pressure side .

So , the plant operator was more concerned with air ( and water vapor ) being sucked in with a leak on the low side ( raises head pressure + the problems associated with water vapor ) . Than a leak on the high side loosing refrigerant .

The purge unit ran continuously ( small electric motor ) , pulling air + refrigerant gas from the top of the chiller vessel . The compressed mixture was run through a condenser coil , then into a small vessel . Liquid refrigerant would collect in the bottom of this vessel & the non condensables remain above the condensed refrigerant .

The vessel had a float & when liquid refrigerant reached a certain level , it would be discharged back into into the main chiller vessel .

The non condensables would be " burped off " periodically , maybe responding to pressure ? In theory , this would be mostly air and water vapor ?

God bless
Wir
WyrTwister is offline   Reply With Quote
Old 01-04-17, 10:28 PM   #6
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by Xringer View Post
A method of getting rid of air in a recovery tank is pump the liquid off the bottom
of the tank, into another tank.. https://youtu.be/pDxRnEqSFyE
Too bad, I only own one recovery tank..
That's what empty propane bottles are for....

Right side up, gas comes out. Upside down, liquid comes out. Hmmmmm...

jeff5may is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 09:00 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design