Folks, the thread by Xringer has at last tipped me over the edge to go ahead and try my own DIY install of our mini-split system.

I will skip the contractor part as the prices quoted to me were close to double of my equipment + parts costs combined.



The outdoor model which we bought is a LG LMU245HV










The indoor models for our evaporator are LMAN095HV X 2 (for our 2 bedrooms) and LMAN125HV X 1 (for our living room)












In our rated configuration, these units will have the following efficiency numbers

* Cooling
o EER = 12.5
o SEER = 18.7
* Heating
o COP = 2.6
o HSPF = 9.6

Chaaru is offline   Reply With Quote
Old 01-26-10, 02:13 AM   #2
Chaaru
Lurking Renovator
 
Join Date: Jan 2010
Posts: 12
Thanks: 0
Thanked 1 Time in 1 Post
Default

Service manual for LMN245HV

Installation Guide









After a thorough research on what would suite our needs, we ended up with agreeing on purchasing a LG Heat Pump mini-split AC with 3 zones. This would meet all our requirements that we had and this unit was capable of heating as well as cooling. The specs look decent and efficiency was also great. This combination qualified for the 30% federal tax credit as well. Additionally this unit had the good looks compared to the off-white/cream looks of the evaporators of other models.

The Heat Pump Indoor and the outdoor units were bought online. These were shipped promptly viz Fedex freight and reached us in about a weeks time. It was a big pallet weighing close to 180 lbs. The shipping was free and it was dropped off in our garage.

The unit details are LG Outdoor unit LMU245HV and 3 total indoor units ( 2 - LMAN095HV and 1 - LMAN125HV). The units were packed well and there was no sign of exterior damage. After the package was inspected for damage it was signed-off and we decided to unpack it to inspect it for any defects. Fortunately everything looked good. Here are some pics
















In the picture below you can see that one of the fastening screws (L1) is missing. I wasn't too happy with what I could consider a poor QC. Hope the unit itself works well.




















Chaaru is offline   Reply With Quote
Old 01-26-10, 11:21 AM   #3
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Quote:
Originally Posted by Chaaru View Post
It looks like it uses an impedance source inverter since the PFC inductor is split into two parts.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 01-26-10, 08:21 PM   #4
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default Nice looking ASHP!!

Maybe by seeing how the Sanyo valves are set up, you can get a better understanding of the LG setup..
Hopefully, the systems aren't too different. (I'll delete these when they aren't useful anymore).


Here's a pic of the nitrogen pressure test hook up. (See Fig. 60a below).

If you remove the two brass caps, you can insert the allen wrench and release the R-410A.
That step is the last thing you do before final testing..
I think maybe both your valves (Gas & Liquid) are about the same as my wide tube valve.
(I only have one schrader valve and I think you might have two).
But, where my line-set connections on the right, goes up to the indoor unit,
yours goes left, inside the unit to a 3-way splitter. (2 of them).


(Note: The artist drew the valves upside down, Compared to my unit).


The 3-way type valve (right column) is like both LG valves.

The pressurized R-410A comes in at the bottom of the valve. When the valve screw-cylinder- is screwed down (CW), it seals off the R-410A inside the outdoor system.


I took a quick look at your install manual and it seems like the line-set hookup
looked more like a Sanyo, than it does your LG.. Is it an out of date manual?

Do you plan on doing a pressure test of the line sets?

"With the main valve closed (before R410A release), can I pressure test the system with the schrader valve (service valve) ?"

Yes you can. If a valve is opened, the refrigerant will come out of the outdoor unit.
So, always leave those in the 'shipping' posistion until the end of the install.

When you hook up the nitrogen bottle to pressurize, nitrogen comes into the schrader,
and flows over the top of the valve screw-cylinder and directly into the line-set(s).

When you pressure test, remove the other cap, so it's schrader will be tested too.

When you finish pressure testing (all 3 line sets simultaneously),
and want to vacuum the linesets, replace the other cap.
Since the schrader with allow outside air to leak into the lines. It's only designed to hold pressure inside.

Or, you could put the nitrogen bottle on one schrader and the gauge set on the other schrader..

~~
Are those factory cap-lines are really air-tight? You can do a quick vacuum check and find out.
If they are tight, then you can test each line-set as you install it.
Instead of trying to test all of them at once.

Last edited by Xringer; 01-27-10 at 08:32 AM.. Reason: Reply to below:
Xringer is offline   Reply With Quote
Old 01-27-10, 01:26 AM   #5
Chaaru
Lurking Renovator
 
Join Date: Jan 2010
Posts: 12
Thanks: 0
Thanked 1 Time in 1 Post
Default

Thanks Rich for the pictures and suggestions.

Your explanation about the valve design now makes sense.

I will open up the two valve covers and see what's behind them, over the weekend. The manual when compared to Sanyo and Mr Slim is poorly written, which has led to quite some confusion.

I do plan to do the pressure test with Nitrogen. With the LG valve design it appears that I just have to hook up my manifold gauge to the gas service valve and pressure the system which will pressurize all 3 line sets.

With the main valve closed (before R410A release), can I pressure test the system with the schrader valve (service valve) ?
Chaaru is offline   Reply With Quote
Old 01-27-10, 01:41 AM   #6
Chaaru
Lurking Renovator
 
Join Date: Jan 2010
Posts: 12
Thanks: 0
Thanked 1 Time in 1 Post
Default

Here are the list of parts I ended-up buying for my install

Slimduct
Drain Hose
Lineset Tubing (25 ft) X 3
Condensate pump for LG
Wire Whip
Service Disconnect
Control Wire
R410A Refrigerant Gauges W/ Hoses & Manifold
Micron Gauge SVG2
Nylog Blue sealant
Robinair 15150 Vacuum Pump
R410A adapter kit
Robinair vacuum oil
Riser Base


Coming soon - some pics of the parts

Last edited by Chaaru; 04-12-10 at 12:41 PM..
Chaaru is offline   Reply With Quote
Old 03-09-10, 11:36 AM   #7
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default How's your install going??

Quote:
Originally Posted by Chaaru View Post
Here are the list of parts I ended-up buying for my install...

[etc]

[etc]

[etc]
Chaaru,

Your install thread was vividly clear and was going so well, I'm quite interested to know how your install progressed.

Any possibility of an up-date?

Best Regards,

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 03-26-10, 08:05 PM   #8
Beaker
Lurking Renovator
 
Beaker's Avatar
 
Join Date: Mar 2010
Location: Cocoa Beach, FL
Posts: 6
Thanks: 0
Thanked 0 Times in 0 Posts
Default

I am building a super insulated dome house, and I am considering a mini-split system. The whole dome will cool adequately with a 12K btu Window A/C in summer, so I don't need much capacity. I have heard of the mini-splits but have never talked to anyone who's used one for any length of time...if you could tell about your experiences with mini-splits that would be great!
Beaker is offline   Reply With Quote
Old 03-31-10, 11:29 PM   #9
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 724 Times in 534 Posts
Default Mini-Split Experiences...

Quote:
Originally Posted by Beaker View Post
...if you could tell about your experiences with mini-splits that would be great!
Well, I've use one for about a year...

I live in a small house (aprox 700 sq ft), built about 120 years ago, and never insulated until I moved in. My insulating project has spanned a couple of decades and several code changes, so I have upgraded my insulation procedure as I have progressed. I'm now realizing I'll have to remove some of the insulation I put in, in the beginning to meet code.

I'm currently layering rigid foam in the walls, sealing at every layer. Insulation is really important, no matter what your heat source.

So about a year ago I embarked on a DIY ground source heat pump, which is still in progress, and I got a small (3/4 Ton) mini-split to keep me warm while the GSHP is still in development.

I really like my mini-split...

Previously, I was trying to reduce my heating costs by reducing the area I heated using a Nat Gas furnace with forced air (scorched air).

Closing off vents and rooms that weren't in use didn't work so well for me because my furnace only has one rate of heat output, so it short cycled and blasted me with frequent gusts of hot air. Not a pleasant situation.

The mini-split I got is an 'inverter type' Sanyo, and it is able to evenly modulate it's heat output to suit the situation. It's quiet, comfortable and cheaper to run than natural gas. Not only has my gas use gone down drastically (I still have NG cooking and NG demand hot water) but my electric use is not much higher than it was before the mini-split. In fact my gas use is so low that some months the fee to be hooked up to NG is higher than the gas I use. I'm even considering going to Propane, because at the small volume I use, it might even be cheaper.

So far the mini-split has performed as advertised, and I haven't needed to repair or replace anything.

I installed it myself. I didn't think to document my experience. Another blogger here at Ecorenovator named Xringer installed his own, and I shared with him what I had learned in doing mine. He took lots of photos of his install and did a dandy write-up.

Hopes this helps...

Regards,

-AC_Hacker
AC_Hacker is offline   Reply With Quote
Old 04-05-10, 04:40 PM   #10
Chaaru
Lurking Renovator
 
Join Date: Jan 2010
Posts: 12
Thanks: 0
Thanked 1 Time in 1 Post
Default I am back to document my install

Folks, I have been busy with work and related travel, hence never got a chance to update this thread on my progress. In-fact there wasn't much progress at all. I just got a few things done over the past couple of weekends and plan to post the details of my progress.

I will restart where I had left off.

Folks who have left me PM's, I can't respond to you directly as I don't have enough posts (hopefully that will go away soon)

Xringer - I saw your note + post today, thanks for your explanation. I will follow your advise and document my game plan before I embark on the vacuum and pressure test.
Chaaru is offline   Reply With Quote
Reply


Tags
diy, ductless, heat pump, mini-split

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:17 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design