Quote:
Originally Posted by buffalobillpatrick View Post
refrigerant/water

6 gpm should be easy even with a low power pump like a Taco 006 with 1" x 10' pipes & no head loss on either ends at the tanks. The HX's have very little head loss @ 6 gpm.

6 gpm x 10* F delta x 500 = 30K btu/hr

I'm wondering about pulling the water out of the bottom of the solar tank?
More even temp. over more hours, & yes, I know it's normal to pump your hottest water into a HX, but in this case, maybe 180* water is too hot for heat pump?

BBP
This is why I mentioned using a thermostatic valve on the input to the HP from the solar tank. 180F will drive the head pressure crazy and the HP doesn't need it anyway. 100f max is more than hot enough.

Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (05-25-14)
Old 03-13-14, 05:27 AM   #82
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Quote:
Originally Posted by buffalobillpatrick View Post
http://ecorenovator.org/forum/attachment.php?attachmentid=4141&stc=1&d=139466771 2[/IMG]


This is evaporator 30 Bar 4.7 Ton, condenser not here yet = 40 Bar 9 Ton
Is there a distributor on the refrigerant inlet on the HX? Alfa Laval had a lot of problems years ago by not ensuring that the refrigerant was evenly distributed amongst plates. They had lots of freezeups and splits.

It is interesting that the Europeans are nearly entirely plate heat exchanger users and we are the other way around, using a coax HX. There must be a reason.
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (05-25-14)
Old 03-13-14, 08:22 AM   #83
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

I found this: Mueller 1/2" OD ACR Copper Tubing is rated to only 363psi.

Mikesolar, don't know? They are made in Germany sooo I assumed that they are the Shiznet.

BBP
buffalobillpatrick is offline   Reply With Quote
Old 03-13-14, 09:33 AM   #84
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

From another site:

"R290 and R22 have different liquid densities, and different enthalpy change in the evap. The result is that a TXV rated for R22 but used with R290 will have ~3.5 times the capacity"
buffalobillpatrick is offline   Reply With Quote
Old 03-13-14, 09:44 AM   #85
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

That's not correct. R290 is very close to a drop in replacement for R22, R433b even more so.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (05-25-14)
Old 03-13-14, 09:44 AM   #86
dhaslam
Lurking Renovator
 
Join Date: Oct 2012
Location: Co Tipperary, Ireland
Posts: 21
Thanks: 0
Thanked 11 Times in 11 Posts
Default

If the input water is hot enough it should be diverted into the heating circuit and bypass the heat pump. At intermediate temperatures the input temperature can be regulated by mixing the input with the return from the heat pump. I use a small buffer tank for the input side which keeps the input temperature stable and also allows a high flow rate.
dhaslam is offline   Reply With Quote
The Following User Says Thank You to dhaslam For This Useful Post:
buffalobillpatrick (03-13-14)
Old 03-13-14, 11:25 AM   #87
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

dhaslam, I agree & that is in my plan.

If Solar tank > 80*F, I will pull heat out via a HX of 3/4" x 500' loop of o2 barrier pex, this goes directly to Taco ODR TMV to radiant floor.

But there is more to it, this new heat pump will also be used to heat my Thermal Accumulator that is also my DHW tank.

An aqustat on Thermal Accumulator can call for heat from heat pump concurrently with the above, direct to radiant operation.

BBP
buffalobillpatrick is offline   Reply With Quote
Old 03-13-14, 11:47 AM   #88
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

interesting reads on R290:

http://www.danfoss.com/NR/rdonlyres/...ompressors.pdf

http://www.hydrocarbons21.com/news/view/3367

Last edited by buffalobillpatrick; 03-13-14 at 11:54 AM..
buffalobillpatrick is offline   Reply With Quote
Old 03-13-14, 02:02 PM   #89
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

It looks like 2 x parallel loops of 250' of 3/4" pex,

with flow of 3.65 gpm in each loop

at Delta T of 20* F , (tank vs. water inside pex)

should transfer about 15 Tons of heat = 180K btus

At a head loss of 7.65'

HL = K x C x L x F^1.75
K = .0034, C = .933, L = 250, F = 3.65

Way more than enough HX for radiant floors.

BBP

Last edited by buffalobillpatrick; 03-13-14 at 02:06 PM..
buffalobillpatrick is offline   Reply With Quote
Old 03-13-14, 02:42 PM   #90
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

If you split the loop into more parallel sections, you can reduce the pump power requirements.

__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (03-13-14)
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 05:56 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design