It is interesting that the Europeans are nearly entirely plate heat exchanger users and we are the other way around, using a coax HX. There must be a reason. |
|
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (05-25-14) |
03-13-14, 08:22 AM | #83 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
I found this: Mueller 1/2" OD ACR Copper Tubing is rated to only 363psi.
Mikesolar, don't know? They are made in Germany sooo I assumed that they are the Shiznet. BBP |
03-13-14, 09:33 AM | #84 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
From another site:
"R290 and R22 have different liquid densities, and different enthalpy change in the evap. The result is that a TXV rated for R22 but used with R290 will have ~3.5 times the capacity" |
03-13-14, 09:44 AM | #85 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
That's not correct. R290 is very close to a drop in replacement for R22, R433b even more so.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
The Following User Says Thank You to NiHaoMike For This Useful Post: | buffalobillpatrick (05-25-14) |
03-13-14, 09:44 AM | #86 |
Lurking Renovator
Join Date: Oct 2012
Location: Co Tipperary, Ireland
Posts: 21
Thanks: 0
Thanked 11 Times in 11 Posts
|
If the input water is hot enough it should be diverted into the heating circuit and bypass the heat pump. At intermediate temperatures the input temperature can be regulated by mixing the input with the return from the heat pump. I use a small buffer tank for the input side which keeps the input temperature stable and also allows a high flow rate.
|
The Following User Says Thank You to dhaslam For This Useful Post: | buffalobillpatrick (03-13-14) |
03-13-14, 11:25 AM | #87 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
dhaslam, I agree & that is in my plan.
If Solar tank > 80*F, I will pull heat out via a HX of 3/4" x 500' loop of o2 barrier pex, this goes directly to Taco ODR TMV to radiant floor. But there is more to it, this new heat pump will also be used to heat my Thermal Accumulator that is also my DHW tank. An aqustat on Thermal Accumulator can call for heat from heat pump concurrently with the above, direct to radiant operation. BBP |
03-13-14, 11:47 AM | #88 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
interesting reads on R290:
http://www.danfoss.com/NR/rdonlyres/...ompressors.pdf http://www.hydrocarbons21.com/news/view/3367 Last edited by buffalobillpatrick; 03-13-14 at 11:54 AM.. |
03-13-14, 02:02 PM | #89 |
Master EcoRenovator
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
|
It looks like 2 x parallel loops of 250' of 3/4" pex,
with flow of 3.65 gpm in each loop at Delta T of 20* F , (tank vs. water inside pex) should transfer about 15 Tons of heat = 180K btus At a head loss of 7.65' HL = K x C x L x F^1.75 K = .0034, C = .933, L = 250, F = 3.65 Way more than enough HX for radiant floors. BBP Last edited by buffalobillpatrick; 03-13-14 at 02:06 PM.. |
03-13-14, 02:42 PM | #90 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
If you split the loop into more parallel sections, you can reduce the pump power requirements.