Doing a little homework on hydronics in the South. It can be desireable to not heat the slab be cause of our sudden temperature swings, 82F yesterday and 58F for today. Looking at some info from Homepower, 110F for solar hydronic floor heating and 120F for radiant wall. With my overall floor plan I'm considering a radiant common wall on the interior and loft floor/kitchen ceiling to minimize losses to the exterior. And maybe 2 fan coil units to speed up heating when the sun is really shining.

gtojohn is offline   Reply With Quote
Old 02-13-15, 06:00 AM   #12
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Given your heating needs, you can do all the heating with 30C (85F) water and that makes the floor attractive. You will gain in the day and lose it at night. The slab will be close to natural body temp so it will not feel too hot nor cold. Pump directly into it through a small buffer tank, 30% propylene glycol (might be 40% as I don't know what your coldest temp is). Use a ductless heat pump to top up if need be (or make a converted window shaker into a air to water HP as top up). Threads abound on here for instructions.
Mikesolar is offline   Reply With Quote
Old 03-19-15, 12:09 PM   #13
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

What did you end up doing? Did you get all 3 panels? Pics?
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 03-19-15, 04:41 PM   #14
gasstingy
Journeyman EcoRenovator
 
Join Date: Feb 2010
Location: Arab, AL
Posts: 491
Thanks: 109
Thanked 49 Times in 43 Posts
Default

Yes, more input please. And while you're at it, could you add some detail to this statement you made in an earlier post, "Perhaps 1-2 radiators will be all I need to take the chill out. I've found some 16x20 heat exchangers for less than $100. " Obviously, the emphasis I added, and I'd like to have a look at those myself.
gasstingy is offline   Reply With Quote
Old 03-19-15, 06:45 PM   #15
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Quote:
Originally Posted by gasstingy View Post
Yes, more input please. And while you're at it, could you add some detail to this statement you made in an earlier post, "Perhaps 1-2 radiators will be all I need to take the chill out. I've found some 16x20 heat exchangers for less than $100. " Obviously, the emphasis I added, and I'd like to have a look at those myself.
What do you mean by "16 x 20 heat exchangers"?
Mikesolar is offline   Reply With Quote
Old 03-20-15, 02:28 AM   #16
gtojohn
Journeyman EcoRenovator
 
gtojohn's Avatar
 
Join Date: Jul 2014
Location: Austin, TX
Posts: 314
Thanks: 39
Thanked 50 Times in 45 Posts
Default

http://ecorenovator.org/forum/renova...country-2.html
Pier and beam. Slab quote was over $4k. This was less than $1k. Additional benefits of a crawl space include room for a composting toilet storage tank as well as my water pumps and hot water storage tank. Walls have been completed and I hope to be dried in is about 2 weeks. For heat exchangers I found them on ebay under "water air heat exchangers". I have a few plans for heating including a copper water coil close to my wood furnace to help boost the output when occupied. There will be 1 to 2 minisplit heat pumps mostly for cooling. My main strategy is to insulate and build as tight as affordable and reduce my heating requirements and let the solar do what it can when unoccupied. Sadly winter ended about 2 weeks ago. Its been in the mid 70's lows in the 60s, today made it to 83f with high humidity.
gtojohn is offline   Reply With Quote
The Following User Says Thank You to gtojohn For This Useful Post:
gasstingy (03-20-15)
Old 03-21-15, 04:10 AM   #17
gtojohn
Journeyman EcoRenovator
 
gtojohn's Avatar
 
Join Date: Jul 2014
Location: Austin, TX
Posts: 314
Thanks: 39
Thanked 50 Times in 45 Posts
Default

I found a little info today. "For flat panel collectors expect 1000 btu per sqft per day in the south. In a more northern latitude expect 750 btu*sqft day. 10-20% of building sqft was recommended for sizing to provide 25% of annual heating demand. Also recommended 5 gallons of water per sqft of panel for storage will increase coverage to 50% of annual heating demand."
So in theory I can expect 63,000 btu output on a sunny day and 315 gallons of storage can help buffer for a cloudy day. Im already undersized for a 1000sqft space, man j shows 11kbtuhr on a 30f day (264kbtu day). Manipulating manual j with the panels I have I can expect to keep 6f above outdoor ambient. So, 240 sqft could help keep me closer to 18f above outdoor ambient and quite a bit more comfortable as a starting point before other heat sources.
gtojohn is offline   Reply With Quote
Old 03-21-15, 04:45 AM   #18
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Quote:
Originally Posted by gtojohn View Post
http://ecorenovator.org/forum/renova...country-2.html
Pier and beam. Slab quote was over $4k. This was less than $1k. Additional benefits of a crawl space include room for a composting toilet storage tank as well as my water pumps and hot water storage tank. Walls have been completed and I hope to be dried in is about 2 weeks. For heat exchangers I found them on ebay under "water air heat exchangers". I have a few plans for heating including a copper water coil close to my wood furnace to help boost the output when occupied. There will be 1 to 2 minisplit heat pumps mostly for cooling. My main strategy is to insulate and build as tight as affordable and reduce my heating requirements and let the solar do what it can when unoccupied. Sadly winter ended about 2 weeks ago. Its been in the mid 70's lows in the 60s, today made it to 83f with high humidity.
OK, Interesting quote for the slab. I just did a 1200ft slab at 4" and the concrete cost $3k and the finishing cost $2k.
Attached Thumbnails
Click image for larger version

Name:	floor tubing 8.jpg
Views:	440
Size:	483.8 KB
ID:	5089   Click image for larger version

Name:	concrete 3.jpg
Views:	419
Size:	475.5 KB
ID:	5090  
Mikesolar is offline   Reply With Quote
Old 03-21-15, 07:56 AM   #19
randen
Uber EcoRenovator
 
Join Date: Apr 2011
Location: Strathroy Ontario Canada
Posts: 657
Thanks: 9
Thanked 191 Times in 129 Posts
Default Texas Concrete

I was quite surprised at the quote for concrete for Gtojohn. I had made a comparison in an earlier post between the wood floor construction and heated concrete slab and I still find the heated slab is less cost expecially when the extras (ductwork & heatexchangers) are factored out.

Now I do understand Gtojohn already had some wood But.
I think its a lot less work. Two to three days and you have the main-floor finished.

Mikesolar what do you think of two separate loops one for solar and another for radiant heat. instead of trying to heat exchange into one main loop.

Maybe another thread on some of these ideas.!

Randen
randen is offline   Reply With Quote
Old 03-21-15, 08:00 AM   #20
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

I had thought about separate loops for solar and backup heat before. I wanted to have the solar at the bottom of the slab, tempered down temp of course. The backup heating would be sitting higher in the slab. Won't work well with a 2" slab but it would with a 4' slab. You could still have a diverting valve to do solar DHW.

Mikesolar is offline   Reply With Quote
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:21 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design