Old 03-31-14, 12:01 PM   #431
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Yes, more thermal conduction is goal.

buffalobillpatrick is offline   Reply With Quote
Old 04-01-14, 12:48 PM   #432
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by buffalobillpatrick View Post
Yes, more thermal conduction is goal.
I found THIS paper about additives to concrete to improve thermal conductivity.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
buffalobillpatrick (06-22-14)
Old 09-09-14, 12:55 PM   #433
Drake
DIY Guy
 
Join Date: Jan 2011
Location: Mpls,MN
Posts: 315
Thanks: 2
Thanked 17 Times in 17 Posts
Default

As I have been searching for a control panel system to match a simple 2 or 3 loop one zone radiant layout I have been asked by suppliers "what is the hot water source?" Are control systems that specific to method of hot water? I want to stay as generic as possible to be able to switch "sources" as availability, knowledge of DIY and economics change. The manifold and loops are constant if designed properly what are the components that are specific to water source? Is their a design that gives you the most options? Are the requirements based on on-demand or storage sources? Or high temp vs low temp supply?
Drake is offline   Reply With Quote
Old 09-09-14, 01:32 PM   #434
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Drake, Will your loops be in a slab that is properly insulated with FOAM R10 or more underneath, or in heat transfer plates, or suspended under subfloor?

The water temp. required for each method is quite different, say aprox. 25*F Delta up with each.

Gain in efficiency is pretty large with minimizing water temp.

No boiler is made small enough for a small heat load, thus a buffer tank would be required.

The PEX loops & manifold could stay the same regardless of heat source, mine have.
buffalobillpatrick is offline   Reply With Quote
Old 09-09-14, 06:05 PM   #435
Drake
DIY Guy
 
Join Date: Jan 2011
Location: Mpls,MN
Posts: 315
Thanks: 2
Thanked 17 Times in 17 Posts
Default

Yes, two loops will be in a high mass(4") slab with 1 1'2' thermax below. And a third loop in a thin slab(1 1/2") in a lofted bedroom. 600 sq ' new space will be built to "passive house" standards. Am favoring off peak heating a 120 gallon DHWH tank as storage and incorporating a mixing valve to lower loop temps as slab are said to work best supplied with lower temp fluid. Tank and loops a dedicated system, another DHWH sperate for potable use. But in the future I would like to go Geo or something when I have the time after completing the build(4-5 yrs) as a heat source with as little retrofit as possible.
Drake is offline   Reply With Quote
Old 09-09-14, 07:43 PM   #436
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Drake View Post
Yes, two loops will be in a high mass(4") slab with 1 1'2' thermax below. And a third loop in a thin slab(1 1/2") in a lofted bedroom. 600 sq ' new space will be built to "passive house" standards. Am favoring off peak heating a 120 gallon DHWH tank as storage and incorporating a mixing valve to lower loop temps as slab are said to work best supplied with lower temp fluid. Tank and loops a dedicated system, another DHWH sperate for potable use. But in the future I would like to go Geo or something when I have the time after completing the build(4-5 yrs) as a heat source with as little retrofit as possible.
If you think you will want to 'go geo', be sure you design your floors for geo now... it'll make your conventional heating cheaper too, in the meantime..

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 09-09-14, 11:56 PM   #437
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Drake, I would make it 2 zones with seperate thermostats, 2 zone valves & 1 pump.
With different slab thickness & bedrooms are usually set at lower temp.
I like the Grundfos Alpha, low electricity use & automatically sets its own speed to match backpressure.
Use O2 barrier 1/2" PEX spaced at 8" OC, limit each loop to 250'
Get a Taco Outdoor Reset Thermal mixing valve (ODR TMV). It will minimize water temp. to zones based on outdoor temp.

Last edited by buffalobillpatrick; 09-10-14 at 12:48 AM..
buffalobillpatrick is offline   Reply With Quote
Old 09-10-14, 08:51 AM   #438
Drake
DIY Guy
 
Join Date: Jan 2011
Location: Mpls,MN
Posts: 315
Thanks: 2
Thanked 17 Times in 17 Posts
Default

AC, to the best of my research high mass(concrete) floors are the best design for low temp hydronic radiant heating I have come across. It also is the best for solar passive gain storage. I have gotten a consensus that this floor design will function equally well with any source of hot fluid run thru it. From your comment am I missing an alternative design?

BBP, all your recommendation are now in my folder on hydronics for when I get to that part of my new construction. Am I correct that all these components would be part of what is considered the "control panel" portion of a hydronics system?
Drake is offline   Reply With Quote
Old 09-10-14, 09:18 AM   #439
Ormston
Apprentice EcoRenovator
 
Join Date: Mar 2013
Location: UK
Posts: 131
Thanks: 13
Thanked 35 Times in 32 Posts
Default

Quote:
Originally Posted by buffalobillpatrick View Post
Use O2 barrier 1/2" PEX spaced at 8" OC, limit each loop to 250'
Why limit to only 250' ?
I have 2 zones of 800-850' (240-260m) each as well as 6 other zones all fed from a a single grundfos alpha 2.
This is through 17mm PEX, the pump usually draws 21w so is not struggling at all.

Steve
Ormston is offline   Reply With Quote
Old 09-10-14, 09:49 AM   #440
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Drake, yes control components. What does your " 1 1'2' " mean? 1.5" not nearly enough.

THERMAX? Sheathing

Thermax is polyisocyanurate foam, this type should NEVER be used under a slab, it will waterlog & loose most all of its R-value.

In Mn. I would use 4" minimum or MORE of XPS (blueboard) or EPS type2 or 3

To push 1gpm through 800' takes 3.2X energy vs. 1gpm through 250'
Read: Modern Hydronic Heating by John Siegenthaler, P.E.


Last edited by buffalobillpatrick; 09-10-14 at 09:53 AM..
buffalobillpatrick is offline   Reply With Quote
Reply


Tags
diy, heat pump, hydronic, pex, radiant

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 06:26 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design