The default position of the valve is, to cool the HX, but i want to heat my HX.
The whole idea is to heat the house i will never use the cooling function probably only on defrost if necessary. But i assume i cant change the valve, because it is inside the unit what was pre-charged with gas. In my case i can just power the valve when compressor starts and shut off at the same time? is it also possible to change the valve while compressor is running? like in a sudden defrost action? of should you first turn of the compressor? stef |
07-21-14, 02:09 PM | #32 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
|
Quote:
Let's hear it from some others. -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
07-22-14, 04:54 AM | #33 |
Helper EcoRenovator
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
|
Just did my first bench test:
DT = 20 degrees Mass = 100 liters C = 4180J PW = 0,528 kWh of used electricity Q = M * C * DT = 100 * 4180 * 20 = 8360000 joule E = 3600000 * 0,528 = 1900800 joule COP= 4,398 stef Last edited by Daox; 07-22-14 at 01:42 PM.. |
07-22-14, 01:04 PM | #34 |
Helper EcoRenovator
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
|
Maybe tomorrow I will install the heat exchanger inside the house.
From what i know and how i hooked everything up now, The hot gas flows from the top of the hx to the bottem right? And the water on the other will flow from the bottom to the top right? I need also need to get my r410a back in to the outdoor unit. From what i read you close the gas service valve, turn on the compressor and wait till the gauge on the manifault go in to the vacuum area. Then you close the liquid line, and right after that you turn of the compressor. Is this the correct way? stef |
07-22-14, 02:02 PM | #35 | ||
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
|
Quote:
Quote:
-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
||
07-22-14, 07:07 PM | #36 | |
Supreme EcoRenovator
|
reversing valve operation
Quote:
The only time the reversing valve should not be energized in heating mode is during defrost. The wire from the thermostat will remain active throughout heating mode, regardless of whether the unit is defrosting or not. The defrost control circuit will spool the reversing valve (and control other devices in the outdoor unit) when it needs to. It operates on its own schedule, and there are many different kinds of defrost controls, some smarter than others. You don't want to tie the reversing valve to the compressor control circuits. Lets say you've been heating for awhile, and the thermostat is satisfied. If the reversing valve spools back to cooling mode when the compressor isn't running, the high pressure liquid in the condenser will flow backwards through the valve and straight into the compressor. It will push its way through the crankcase, foaming up the oil and carrying some of it into the cylinder or scroll . The gas then flows through the compressor exhaust valve, finding the low pressure it has been seeking. When the compressor is running, it can quickly spit out the oil carried in with the refrigerant. If you listen to the outdoor unit when it enters or leaves defrost mode, you can hear the distinctive "whoosh" sound as this happens. When the compressor is still, the scroll or cylinder tends to trap the oil inside it. When the compressor starts up on the next cycle, the trapped oil has to be pushed out all at once, hammering your cylinder or scroll hard as it squeezes through the exhaust valve. This is not good. Last edited by jeff5may; 07-22-14 at 07:21 PM.. Reason: more words |
|
07-22-14, 10:48 PM | #37 |
Supreme EcoRenovator
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
|
To pump it down, first close the liquid line valve, run the compressor until the suction side starts to go into a vacuum, then close the suction valve. (If there's a low pressure control, you'll have to bypass it.) Then backfill with nitrogen before opening the system, after which you tape over or cap the open ends until you're ready to put it back together.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her... |
07-23-14, 01:41 PM | #38 |
Helper EcoRenovator
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
|
Thanks for the info, today I pumped down the system en removed the HX.
I also hooked the HX up to the central heating system. Today I also placed the electronics in a nice box. |
07-24-14, 01:23 PM | #39 |
Helper EcoRenovator
Join Date: May 2014
Location: Holland
Posts: 58
Thanks: 6
Thanked 3 Times in 3 Posts
|
Today i created the circuit board for the outdoor unit, his job is to read values from 5 one-wire temperature sensors and spit them out by the rs485 bus.
It also has a push button, that i can use to turn the system on, when i am outside for testing purpose. At the moment I am really busy with coding. stef |
07-24-14, 09:00 PM | #40 |
Supreme EcoRenovator
|
Awesome, totally awesome! You must own a pipe bender, because I see a whole lot of custom-bent pipes. Very nice.
|
|
|