EcoRenovator  

Go Back   EcoRenovator > Improvements > Tools
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 04-24-14, 05:38 PM   #11
ecomodded
Supreme EcoRenovator
 
Join Date: Sep 2012
Location: Vancouver Island,Canada.
Posts: 1,037
Thanks: 116
Thanked 100 Times in 87 Posts
Default

Good to see your success with this , sounds like you have it tweaked perfectly.

ecomodded is offline   Reply With Quote
Old 04-24-14, 09:13 PM   #12
Elcam84
Apprentice EcoRenovator
 
Join Date: Jun 2013
Location: TX
Posts: 275
Thanks: 2
Thanked 31 Times in 24 Posts
Default

The current electronic residential meters do read power factor. According to the elec guy that I talk to that installs and sets up the commercial meters the elec company does monitor what is going on the PF in residential applications and said not to be surprised if it becomes a place for fees like it is for commercial as it has been talked about.
Elcam84 is offline   Reply With Quote
Old 04-26-14, 01:27 AM   #13
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

I have seen a digital residential meter that had a tally for counting "80% VA" power consumption.
I can only assume they are collecting your power consumption when average power factor going onto the house drops below 0.80, to charge you more.
The meter I saw had collected 100s or thousands of regular watts of consumption, but only 10k of the infamous "80% VA".

On an electromechanical residential meter, it doesnt track power factor but as you use more VoltAmps those VoltAmps spin the meter faster.
oil pan 4 is offline   Reply With Quote
Old 04-26-14, 04:02 AM   #14
WyrTwister
Master EcoRenovator
 
Join Date: Jun 2013
Location: USA
Posts: 543
Thanks: 6
Thanked 44 Times in 38 Posts
Default

Quote:
Originally Posted by oil pan 4 View Post
I have seen a digital residential meter that had a tally for counting "80% VA" power consumption.
I can only assume they are collecting your power consumption when average power factor going onto the house drops below 0.80, to charge you more.
The meter I saw had collected 100s or thousands of regular watts of consumption, but only 10k of the infamous "80% VA".

On an electromechanical residential meter, it doesnt track power factor but as you use more VoltAmps those VoltAmps spin the meter faster.
I was told , in school , that the traditional electro-mechanical meters Measure only true kilowats , not volt amprts ?

God bless
Wyr
WyrTwister is offline   Reply With Quote
Old 04-26-14, 04:59 PM   #15
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

Check out my watt versus VoltAmp tests in the OP using a residential electromechanical meter.
It definitely responded to the excessive VoltAmps load I put on it as if they were watts.
The way excessive voltamps load down a generator I think the power company should charge for them.

I originally started out on this power factor thing to make my machines corporate with long extension cords and being powered remotely by a generator. Its turned into an attempt to turn the utility meter slower, which is working quite well.

Last edited by oil pan 4; 04-26-14 at 05:03 PM..
oil pan 4 is offline   Reply With Quote
Old 05-13-14, 02:50 PM   #16
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

I recently constructed another air compressor. A 220volt machine this time.
I was able to power factor correct it to save about 1.7 amps, about a 5% power savings, nothing compaired to the 25% to 30% power savings capacitors were giving me on my 120v machine.
oil pan 4 is offline   Reply With Quote
Old 05-17-14, 05:55 PM   #17
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

I am having another go at power factor correcting my large arc welding machine.
Since I do not have a machine that figures power factor cosine for 240v power I am shooting from the hip with my box of capacitors and fluke325 amp clamp.
First I like to start small. Power factor correcting the blower fan that cools the transformer.
It started out using 0.71 amps of 240v power, which seems like a lot.
Started off by connecting a 8uf capactor to the fan, that reduced power to 0.55 amps, not bad.
Then tried a 10uf which I figured would be to big. Power consumption went up to 0.65 amps, definitely too big. Next try was with a 4uf, power consumption was down to a half amp even.
Figured what the hech might as well try the 5uf cap I have, that reduced amps to 0.48, not bad, thats saving 55 VoltAmps from just the fan alone. Thats enough power to run a fan or some lights.
I run the fan a lot, I cut power to the transformer and just run the fan to cool down the trasnformer in between welds.

Now on to the main arc welding transformer....

Last edited by oil pan 4; 05-26-14 at 02:31 AM..
oil pan 4 is offline   Reply With Quote
Old 05-17-14, 06:30 PM   #18
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

Other power factor corrected 240 volt transformer welding machines run 40 to 60uf of capacitors connected line to line. So the amout of capacitance will be some where around there.

The main transformer runs 3.77 amps no load.
First try was with the 10uf capacitor since I already had it sitting there, result: it dropped the power consumption to 3 amps even.
Next try was with a 25uf capacitor, that dropped no load current to 2 amps even and quieted the angry hum the transformer makes.
Still thinking there is more to be had I connected the 10uf capacitor to the 25uf, making a 35uf capacitor, that reduced power to 1.71 amps.
Then swapped out the 35uf assembly for a single 40uf capacitor, that increased power consumption to 1.76 amps.

So 35uf of capacitance saves around 535 voltamps at no load.

For testing I am going to connect twin 440volt 40uf caps line to neutral, since arc welders have a way of killing 440volt motor run capactors connected line to line.

Weld output appears unchanged.

Connecting the capacitors in parallel, running each capacitor L to N seems to lessen their capacitance, causing the machine to draw 2.2 amps at no load as opposed to 1.76 amps during the quick and dirty L to L single capacitor test.

Twin 55uf capacitors connected L to N seemed to do the trick.
Twin L to N 55uf capacitors plus a 5uf for the fan is almost exactly what welding machines running PFC use.

It would seem that when you run them at lower voltage they have less capacitance. Or has the effect of serriesing them up.

I ordered a set of 80uf motor run capacitors to install L to N on each line. The L to N connected 55s are causing the machine to draw around 2 amps. The 80s should get that down to around 1.75 amps.

Last edited by oil pan 4; 08-15-15 at 04:14 PM..
oil pan 4 is offline   Reply With Quote
Old 06-16-14, 01:22 AM   #19
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

I salvaged some actual powerfactor correction capacitors made by mallory.
They are 60uf, 480v rated and are about 3 times the size of a standard 440v 60uf motor run capacitor.
Not sure what to do with them. Had I found these before I bought the 80uf capacitors to put in my large arc welder I would just use twin 60s, since its hard to beat the pirce I paid for them, free.

I did some more work with my mig welding machine. I swapped out the internal component capacitors for a single externally mounted 40uf motor run capacitor. I found the 40uf reduced amp consumption a little better than 30uf. Total saved is about 2 amps. It wont save much on the power bill but it will make the welder more extension cord or generator friendly.
oil pan 4 is offline   Reply With Quote
Old 06-16-14, 05:19 PM   #20
Elcam84
Apprentice EcoRenovator
 
Join Date: Jun 2013
Location: TX
Posts: 275
Thanks: 2
Thanked 31 Times in 24 Posts
Default

I was looking at the PF of my well pump and its 98 after start up but it's around 50 or so when it starts. Big dip at start up with it course it's on a 100' cord though it's only 3' from the panel. I haven't built a permanant enclosure for it so I haven't run permanent power to it yet.

Elcam84 is offline   Reply With Quote
Reply


Tags
apparent power, kva, power factor, true power, welder

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:49 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design