EcoRenovator  

Go Back   EcoRenovator > Improvements > Renovations & New Construction
Advanced Search
 


Blog 60+ Home Energy Saving Tips Recent Posts Search Today's Posts Mark Forums Read


Reply
 
Thread Tools Display Modes
Old 01-22-13, 01:05 AM   #31
SolarUtah
Cheap Renovator
 
Join Date: Jan 2013
Location: Utah
Posts: 10
Thanks: 0
Thanked 1 Time in 1 Post
Default

Great thread. The system I installed under the basement floor uses 3 parallel circuit with a single pump, I think it is a Taco 9, uses 135 watts.

See graphic of the system below. Works well, I used about 450' of Pex tubing and about 70 ' of copper. Only used 45 degree fittings to limit pressure drop.

Attached Thumbnails
Click image for larger version

Name:	3DBasement Floor Layout.jpg
Views:	771
Size:	51.2 KB
ID:	2899  
SolarUtah is offline   Reply With Quote
Old 01-22-13, 07:58 AM   #32
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Great to hear I'm not the only one thinking along these lines. How is the floor working out for you so far?
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 01-22-13, 10:49 AM   #33
Blue Bomber Man
Lurking Renovator
 
Join Date: Jun 2009
Posts: 24
Thanks: 3
Thanked 5 Times in 5 Posts
Default

I used to in stall hydronic floor systems with my father years ago.... this was the preferred layout due to the way it averages out heat distribution.

Additionally we would decrease the spacing between parallel runs near exterior walls or other heat sinks to improve comfort
Attached Thumbnails
Click image for larger version

Name:	hydroniclayout.jpg
Views:	753
Size:	55.0 KB
ID:	2900  
Blue Bomber Man is offline   Reply With Quote
The Following User Says Thank You to Blue Bomber Man For This Useful Post:
buffalobillpatrick (12-01-14)
Old 01-22-13, 06:31 PM   #34
SolarUtah
Cheap Renovator
 
Join Date: Jan 2013
Location: Utah
Posts: 10
Thanks: 0
Thanked 1 Time in 1 Post
Default

My system works well, I was concerned with the air entrapment issue using a parallel arrangment. By installing a common manifold, I was able valve off one or more circuits to purge the air, as well as balance flows for even temperatures. See pics below of the Manifold I used.

There are actually 3 circuits, not 2 as shown in the graphic.
Attached Thumbnails
Click image for larger version

Name:	img_0395.jpg
Views:	743
Size:	57.0 KB
ID:	2901   Click image for larger version

Name:	Solar%20Screenshot%206-20-2011%205-09-02%20PM.jpg
Views:	828
Size:	159.7 KB
ID:	2902  
SolarUtah is offline   Reply With Quote
Old 09-24-13, 11:04 AM   #35
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

I'm bringing this thread back. I'm pretty close to starting to work on the office hydronic floor. I am going to go with a few parallel lines in it. I don't know quite how many yet. Somewhere between 3 and 6 is most likely. I'm also still trying to decide between 1/2" and 3/8" pex for it.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
Old 09-24-13, 07:00 PM   #36
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Remind us how many ft2 the floor will be? When we design these for boilers we are using trying to get a 20F dT and this usually meant we needed about 250' of 1/2' tube per loop. Head loss is quite reasonable and I recently did an 8 loop floor with a Alpha pump and the display goes back and forth from about 3gpm to a power consumption, when it settled somewhat down, of 12-15w. It is hard to get much better as this was the whole house.
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (09-11-14)
Old 09-25-13, 07:41 AM   #37
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

This specific room is about 14x12, so 168 sqft. The whole house is about 1600. I'm also planning on using 3/8" tubing for the floor versus 1/2" due to space constraints.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Last edited by Daox; 09-25-13 at 07:47 AM..
Daox is offline   Reply With Quote
Old 09-25-13, 08:59 AM   #38
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

The flow through each of the parallel circuits (each of the legs) will only be the same, if the diameter of the supply conduit is slightly larger than any of the parallel legs.

Here is why.

Imagine a flow circuit with the parallel "legs" (all the same diameter) being vertical and a supply manifold "header" is at the top of each and a return manifold is on the bottom. The parallel circuit is fed water from the upper left.

If the manifold and each of the legs are the same diameter, then the parallel legs closest to the inlet get the most water flow (heat). The further you are from that inlet, then the lesser the flow. This is because there is a pressure drop along that manifold.

The reason for this is that there is a finite resistance in the manifold "header" tubing. But if you put it in slightly larger in diameter, then the pressure drop along the length is negligible compared to any one parallel resistance.

In physiology, this is why supply arteries (aorta for example) are always larger than the downstream arteries (femoral, iliac, renal, etc). The downstream arteries are all in parallel. Such a system keep the pressure at each downstream artery virtually the same and thereby flow through any one organ system is simply regulated by the resistance of the arterioles (smallest arteries) in that organ. This is an example of a constant pressure system with flow being regulated simply by resistance and being directly proportional to changes in pipe diameter.

If the supply manifold (aka "header") is the same size as the parallel circuits, increasing pressure in the system somewhat negates the pressure drop along the manifold pipe. But in general, radiant floors are low pressure systems.

Flow always goes into the parallel circuit with the lowest resistance (electricity or water). In the above parallel system, there will be flow in each of the parallel legs, but the flow will be highest in the legs that are closest to the inlet supply.

By increasing the manifold diameter slightly, you decrease the resistance in the manifold markedly. Only a 11% increase in diameter will decrease resistance in half (double the flow). This is because flow is proportional to radius to the forth power.

Having a larger manifold diameter also allows you to have parallel circuits of differing lengths have similar (not identical) flows.

You can model this as either a constant flow inlet - or constant pressure inlet system, but the results will be the same.


Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990

Last edited by stevehull; 09-25-13 at 01:29 PM..
stevehull is offline   Reply With Quote
The Following User Says Thank You to stevehull For This Useful Post:
buffalobillpatrick (09-11-14)
Old 11-30-14, 06:45 AM   #39
Zwerius
Helper EcoRenovator
 
Zwerius's Avatar
 
Join Date: Aug 2014
Location: The Netherlands
Posts: 70
Thanks: 19
Thanked 26 Times in 14 Posts
Default

Just read this discussion.
What I didn't read in this discussion, are these two things:
1. The heat transfer from water to the pipe is depending on water velocity.
As soon as waterflow is so low, that the flow isn't turbulent anymore but it becomes a laminar flow, the heat transfer from water to the inner pipe wall is reduced considerably.
So by dividing the flow over 18 parallel pipes (as in the first example), the water velocity is only 1/18 th of the original value, so there's a good chance velocity is too low to keep a turbulent flow.
So heat transfer might be much lower than expected.
2. It seems nobody was taking Bernouilli's law into account.
Let's assume the first lay out with the 18 parallel pipes.
Assume the input is at the bottom right of the drawing and the output is top left.
Since a radiant floor heating is in one horizontal surface, there's no difference in height between the pipes.
Then according to Bernouilli's law: 1/2*rho*(velocity)^2 + Pstatic = constant.
This leads to the fact that (contrary to what many people think), the flow is not evenly distributed over the 18 pipes. The highest flow will be in the most left pipe en the lowest flow in the most right pipe.
Zwerius is offline   Reply With Quote
The Following User Says Thank You to Zwerius For This Useful Post:
Mikesolar (11-30-14)
Old 11-30-14, 08:00 AM   #40
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

My manifolds are always piped supply opposite to the return or "reverse return". Flow is partially defined by pump speed which means that the dT can be designed, to some extent. While turbulence does help in heat transfer, 50% or more will still occur with laminar flow. When the heat loss of a particular building gets close to passivHaus standards, it is very difficult to pump fast enough to have a high reynolds number and meet the design criteria for the system.

If we are using the heat pump as a heat source and you want to have a 10C dT over the loop (typical with a boiler), some the capacity of the buffer tank will be quickly overcome. The HP may have some trouble keeping up. The dT over the loop will probably have to be lowered which means shorter loop lengths.

Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (12-01-14)
Reply


Tags
floor, head, heating, hydronic, pressure

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 04:35 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design