Old 11-19-14, 10:21 PM   #291
I just finished some reading on the AVR/ATMEGA chipset, and learned something useful: the processor has no hardware support for division at all! Integers, longs, floats, whatever gets divided will be compiled into repeated subtraction. WOW.
Old 11-20-14, 01:44 AM   #292
takyka
Default floats and 1w temp sensors
In my hetpump controller sw I use long and float operations alot. In such application the speed of the uC is plenty to waste for emulated floating point operations. Even there are several frequent interruts from flow sensors, timer, there is tcp/ip communication and the user interface is still responsive.
In my code, I implemented setup menu for dallas temp sensor assignment.
I store the assigned 1w addresses in eeprom, in the background, the program periodically read the temperature information from sensors one by one and stores the result in a global array.
From "main" program I just use the temperatures from the array.
The setup menu looks like this:
l 1w
List of 1W devices:
Bus:0 1W bus number
00;28B0BFA704000088 20.44C 0; (0) Air in device number, serial, measuret temperature (if device support it) assigned function number, assigned function description
01;28328EA704000045 20.81C 2; (0) Air evap. gas
02;286AC6A70400001D 20.13C 7; (0) Condenser gas
03;282EC6A7040000B4 20.44C unassigned device
04;28AED4A7040000A1 20.75C
05;28055CA80400006A 20.81C 1; (0) Air out
06;284382A7040000CB 20.06C 13; (0) Suction temp
07;2857FEA704000000 19.25C 8; (0) Condenser liquid
08;285F8DA704000082 20.06C
09;28FFBDA70400005A 19.31C 9; (0) Heating water in
Bus:1 no device on bus
Bus:2
00;281239BB030000BD 24.63C 11; (2) Electric box
Functions:
00; * Air in * means device assigned to function
01; * Air out
02; * Air evap. gas
03; Water evap. liquid
04; Water evap. gas
05; Well water in
06; Well water out
07; * Condenser gas
08; * Condenser liquid
09; * Heating water in
10; Heating Water out
11; * Electric box
12; Compressor
13; * Suction temp
14; Discharge temp
a 0 3 10 assign command, bus number, device number, function number see above
a 0 4 06 like above
l1w list new 1w config
If you want to import it, i'm willing to help you to dig out from my code the related parts.
In my topic you can find details
http://ecorenovator.org/forum/geothe...iscussion.html
This post is here about it:
http://ecorenovator.org/forum/39116-post8.html
T.
takyka is offline   Reply With Quote
The Following 2 Users Say Thank You to takyka For This Useful Post:
buffalobillpatrick (11-21-14), jeff5may (11-20-14)
Old 11-20-14, 03:27 AM   #293
theoldwizard1
Hmmm ... I missed that !
Even the whimpy μprocessor I programmed on 35 years ago had hardware divide. That was quite unusual back then, but I just kind of assumed it was there.
theoldwizard1 is offline   Reply With Quote
Old 11-20-14, 08:03 AM   #294
theoldwizard1
... I would like not to have to resort to adding any extra shields to the basic controller to gain memory for comm buffers and the like. I have a feeling this will be a challenge given the severely limited amount of onboard program memory and RAM.
Arduino Mega or Arduino Due. IMHO, the 3.3v Vref of the Due is a big strike against it.
Old 11-20-14, 04:43 PM   #295
Nope, not for this project. This one gets a Uno.
Maybe somebody might start a project based on a Mega, but why? It shares the same instruction set and cpu as the Uno. If you can rig up a Uno and get it working, you can rig up a Mega. If you have that many sensors and output pins to deal with, to need a Mega, the system is no longer a general-purpose-friendly setup. It does have more onboard flash and ram, though.
If I really needed more memory, I would add a shield that I could stick an SD card into. With the shield, I would probably add some sort of wireless comms also. Cheap thrills.
If I really really wanted more processing power, I might hold out for the Zero. A whopping 256k of flash and 32k of ram. ARM Cortex processor @32 bits and 48 MHz. Oooh la la! But alas, it runs at 3.3VDC. Shucks.
I can always give up my prefab LCD keypad shield for another display if I really need the extra pins. Given the fact that there are all kinds of sensors, displays, and control devices that will work over serial comms or the 1wire or 2wire interface standards, I doubt this basic controller would need a whole lot else to do its "basic" job..
Old 11-21-14, 01:50 AM   #296
takyka
The arduino mega is a 5V device! As long as one doesn't need computation power of 32bit systems, but for more pins or memory does, arduino mega can be a good choice.
Unlike some are thinking multiplexed analog inputs or IO port expanders, these are needless with mega. And all UNO shields are compatible...
In relationto this, one more tought about 1wire adressing.
As separate arduino pins can be used for analog sensor reading, the same way, dallas sensors can be connected to separate pins too (one ds18xxx on one pin). This way temperature reading can be done without the knowledge of sensor ID, sensor swap is as easy as in case of NTC.
Where temperature reading speed is not a concern, (more than one reading/ second), I prefer DS sensors over NTC because of accuracy, noise immunity and unnecessarity of calibration.
T.
buffalobillpatrick (11-21-14), jeff5may (11-21-14)
Old 11-21-14, 08:00 PM   #297
In relation to this, one more tought about 1wire adressing.
T.
I agree with you pretty much completely. If a particular user wanted to wire up the dallas sensors so they never need to be decoded and would swap out just like analog sensors, it would be easy to assign a separate onewire pin for every sensor. Each pin (or sensor cable) could be labeled for later recollection in case a sensor ever went crazy or failed. The new sensor would "just work" when the unit was powered back up after the swap. Using a Uno, one would quickly run out of available digital pins. This is a compelling reason to choose a Mega as a starting platform.
The reason I brought up the Zero is because it looks as if it will be the "nexgen" replacement for the Uno. Likewise, the Due will be the "nexgen" replacement for the Mega. The Arduino crew is working hard to make sure that "old school" programs and libraries can migrate to the new boards and work. I don't know how seamlessly this will end up, but the time is coming soon when the retail version of the Zero will hit the market. As I write this, competitors are already releasing "knockoff" boards based on the pre-production architecture.
I believe that the Uno and Mega will remain the most widely used boards in the line for quite some time. Until the "modernized" boards get lots of specific code and support content tailored for them (as with the Uno and Mega), they won't attract users and beginners like the "original" boards do. That doesn't mean they're not useful. They just haven't stolen the spotlight from their parents yet.
buffalobillpatrick (11-24-14)
Old 11-25-14, 10:38 PM   #298
Default Here she comes
OK, since nobody is doing any interaction with the code I put up on github, I'll just post it in here. This rough alpha version is basically a wall thermostat with auto-change-over. There have been a few pieces chopped out of it that are giving me problems, but what is here will compile with the libraries off hacktronics and run like magic.
Come get some:
Code:
// include the library code:
#include <LiquidCrystal.h>
#include <OneWire.h>
#include <DallasTemperature.h>
// define pin configuration:
#define  defrostSensor      A2
#define  lcdBacklightPin    10
#define  reversingValve     11
#define  indoorPump         12
#define  compressor          3
OneWire  ds(13);      // Temperature sensors on pin 13
DallasTemperature sensors(&ds);
int x = 1;
// initialize the LCD library with the numbers of the interface pins
LiquidCrystal lcd(8, 9, 4, 5, 6, 7);
boolean fan = false, thermostat = false, heatingCall = false, coolingCall = false, compressorLockout = true ;
float temp_c, temp_f;
int y, heat_sp, cool_sp, defrost_t, settemp = 25;
int state = 0, right = 0, left = 0, up = 0, down = 0, last_st = 0, st = 0;
byte sel = 0, mode = 0;
unsigned long up_time_1 ,up_time_2, up_time, last_request, lastLockout;
double time_1, time_2, time;
void process_io();
void process_display();
void setup() {
  // set up the LCD's number of columns and rows:
  lcd.begin(16, 2);
  sensors.begin();
  pinMode( lcdBacklightPin, INPUT );
  pinMode( defrostSensor, INPUT);
  pinMode( reversingValve, OUTPUT );
  pinMode( indoorPump, OUTPUT );
  pinMode( compressor, OUTPUT );
  last_request = millis();
  digitalWrite(lcdBacklightPin, LOW); //Turn on the backlight
  // Print a message to the LCD.
  lcd.setCursor(0,0);
  lcd.print("Control center");
  lcd.setCursor(0,1);
  lcd.print("Startup Delay");
  delay(12000);
  up_time_1 = millis();
  time_1 = millis();
  compressorLockout = false;
void process_io() {
  if ((millis()-last_request) > 15000) {
    get_temp();
  switch(mode) {
  case 0: //mode is off
    heatingCall = false;
    coolingCall = false;
    lastLockout = millis();
    break;
  case 1: //mode is heat
    digitalWrite(reversingValve,false);
    if (temp_c < (settemp - 1))
      heatingCall = true;
    if (settemp < temp_c) {
      compressorLockout = true;
    break;
  case 2: //mode is cool
    digitalWrite(reversingValve,true);
    if (temp_c < (settemp + 1))
      coolingCall = true;
    if (settemp > temp_c) {
    break;
  case 3: //mode is auto
    if (abs(temp_c - settemp)>2) { //auto-changeover territory
      if  (temp_c < settemp){
        digitalWrite(reversingValve, false); //changeover to heating
        heatingCall = true;
      else {
        digitalWrite(reversingValve, true); // changeover to cooling
        coolingCall = true;
    if ((temp_c - settemp) > 1)
    coolingCall = true;
    if ((settemp - temp_c) > 1)
   heatingCall = true;
    if (abs(temp_c - settemp)<.05) {
    break;
  if (heatingCall || coolingCall && (millis() - lastLockout < 120000)&& compressorLockout) { //2 minute lockout
    digitalWrite(compressor,true);
    digitalWrite(indoorPump,true);
  else {
    digitalWrite(compressor, false);
    digitalWrite(indoorPump,false);
void process_display() {
  switch (right) {
  case 0:
    lcd.clear();
    lcd.setCursor(0,0);
    lcd.print("Current ");
    lcd.print(temp_c);
    if (up>0){
      settemp=settemp+1;
      up=0;
    if (up<0) {
      settemp=settemp-1;
      up=0;
    lcd.setCursor(0,1);
    lcd.print("Setpnt ");
    lcd.print(settemp);
    break;
  case 1:
    lcd.clear();
    lcd.setCursor(0,0);
    lcd.print("Mode ^ ");
    switch(up) {
    case 0:
      lcd.print("OFF v");
      mode=0;
      break;
    case 1:
      lcd.print("HEAT v");
      mode=1;
      break;
    case 2:
      lcd.print("COOL v");
      mode=2;
      break;
    case 3:
      lcd.print("AUTO v");
      mode=3;
      break;
    case 4:
      up=0;
      break;
    case -1:
      up=3;
      break;
    lcd.setCursor(0,1);
    lcd.print("Press select to set");
    if(sel == 1){
      mode=up;
      sel = 0;
      lcd.clear();
      lcd.setCursor(0,0);
      lcd.print("Mode set.");
      lcd.setCursor(0,1);
      lcd.print(temp_c);
      lcd.print("C//");
      lcd.print(temp_f);
      lcd.print("F");
      delay(3000);
    break;
  case 2:
    lcd.clear();
    lcd.setCursor(0,0);
    lcd.print("Get up time");
    lcd.setCursor(0,1);
    lcd.print("Press select");
    if(sel == 1){
      get_up_time();
      sel = 0;
      lcd.clear();
      lcd.setCursor(0,0);
      lcd.print("Up time");
      lcd.setCursor(0,1);
      lcd.print(up_time);
      lcd.print(" sec");
      delay(3000);
    break;
  case 3:
    lcd.clear();
    lcd.setCursor(0,0);
    lcd.print("RxBuffer up");
    lcd.setCursor(0,1);
    if(sel == 1){
      sel = 0;
      lcd.setCursor(0,0);
      lcd.print("VALUE ");
      lcd.print(up);
    break;
  case 4:
    lcd.clear();
    lcd.setCursor(0,0);
    lcd.print("Thermostat?");
    lcd.setCursor(0,1);
    if (thermostat) {
      lcd.print("YES");
    else {
      lcd.print("NO");
    if (up>0){
      thermostat=true;
      up=0;
    if (up<0) {
      thermostat=false;
      up=0;
    break;
void process_state(){
  switch (state) {
  case 1: //right
    right = right + 1;
    if(right > 4) {
      right = 0;
    break;
  case 2: //up
    up = up + 1;
    break;
  case 3: //down
    up = up - 1;
    break;
  case 4: //left
    right = right - 1;
    if(right < 0) {
      right = 4;
    break;
  case 5:
    break;
void read_state(){
  state = 0;
  y = analogRead (0);
  //lcd.setCursor(10,1);
  if (y < 100) {
    //lcd.print ("Right ");
    state = 1;
  else if (y < 200) {
    //lcd.print ("Up    ");
    state = 2;
  else if (y < 400){
    //lcd.print ("Down  ");
    state = 3;
  else if (y < 600){
    //lcd.print ("Left  ");
    state = 4;
  else if (y < 800){
    //lcd.print ("Select");
    state = 5;
    sel = 1;
void get_up_time(){
  up_time_2 = millis();
  up_time = up_time_2 - up_time_1;
  up_time = up_time/1000;        //time in seconds
void get_temp() {
  if ((millis() - last_request)>5000) {
    sensors.requestTemperatures();
    temp_c = (sensors.getTempCByIndex(0));
    temp_f = (sensors.getTempFByIndex(0));
void loop() {
  time_2 = millis();
  last_st = state;
  read_state();
  st = state;
  if(st != last_st){
    process_state();
    //delay(45);
    time_1 = millis();
  time = time_2 - time_1;
  time = time/1000;
  if(time <=10){
    pinMode( lcdBacklightPin, INPUT); //deals with possible hardware bug, turns backlight on.
  else{
    pinMode( lcdBacklightPin, OUTPUT ); //deals with possible hardware bug, lets pin float, backlight shuts off via shield pullup resistor.
    right = 0;
    up = 0;
  delay(190);
  process_display();
  process_io();
This works with the LCD keypad shield I bought and a single 1-wire sensor as it sits. If you look at the code, there are probably a dozen loose ends which do nothing yet. Feel free to play with this and help me optimize what's here already.
I am dealing with a defrost function now that will work with an air-source unit. I'm doing n adaptive defrost algorithm based on a carrier board that has been around for a long time.
Old 11-25-14, 10:47 PM   #299
How is the water-source controller coming along? Have you all sorted out a serial interface? Does anything work?
As long as the blasted machine doesn't go off the deep end with interrupts, I might be able to integrate some of the functionality into what I have working. I could ditch the keypad shield if I had to. If I don't have to, I won't. But I might....
Old 12-27-14, 10:40 PM   #300
BBP,
I was beginning to worry that you'd partied yourself right into the Great Refrigerant Reservoir in the sky... good to hear from you.
Regarding the controller project, I've gone through the available code(s) with the Arduino compiler, and also with the Arduino Simulator, and I'm pretty much at a standstill... I really have no idea if anything works in the available code(s) and with my limited programming experience, I'm not getting far with analyzing the code either.
Also there have been reliability issues reported regarding the flow sensors, so for this, the most basic controller, I am leaving out "pump flow verification".
I built a basic test fixture that I'll use for GPC#1.
Here's a photo:
I have it set up and tested and have verified that all the hardware elements are in place and working.
I have two lm35 type temp sensors, and have verified that they can send temperature data through the USB serial link. They are quite accurate, and in agreement.
I have tested that all the relevant inputs are correctly initialized and working.
I have tested that all the relevant outputs are correctly initialized and working and I can successfully send AC power to the 4 light bulbs.
The light bulbs are (L to R):
(compressor) (insidePump) (outsidePump) (axillary option).
Here's the code I've come up with.
It goes through it's power-up 2 minute wait (shortened to 15 sec for testing) successfully.
It then waits for the 5 volt "heat demand" signal
It then sequentially lights each of the bulbs in series for about 10 seconds each, in endless repetition.
Also the temperature sensor hardware, and code is working but I have commented out that code for now.
Code:
  * General Purpose Controller for a water-to-water heat pump, basic version)
  * Provides for:
  *     2 minute startup dalay for compressor protection
  *     Temperature monitoring of:
  *         Evaporator HX temp
  *         Storage Tank Temp
  *     Controlling line voltage power to appropriate components:
  *         Outside loop pump
  *         Inside loop pump
  *         Compressor
  *         NOTE: Indoor operation is assumed, no compressor crankcase heater.
  * PIN ASSIGNMENTS:
  * Digital Pins:
  *    D0 (reserved for USB & serial communication RX)
  *    D1 (reserved for USB & serial communication TX)
  *    D2 (* reserved for input loop flow data *)
  *    D3 (* reserved for output loop flow data *)
  *    D4 user input request for heat
  *    D5 output to Compressor SSR
  *    D6 output to Inside Loop Pump SSR
  *    D7 output to Outside Loop Pump SSR
  *    D8 output to Auxillary Output SSR
  *    D9 (* not used *)
  *    D10 (* not used *)
  *    D11 (* not used *)
  *    D12 (* not used *)
  *    D13 LED (onboard)
  * Analog Pins:
  *    A0  input Temperature of Evaporator HX
  *    A1  input Temperature of Condenser Tank
  *    A2 (* not used *)
  *    A3 (* not used *)
  *    A4 (* not used *)
  *    A5 (* not used *)
#define  One_Sec              1000
#define  Quarter_Min         15000
#define  Half_Min            30000
#define  One_Min             60000
#define  Two_Min            120000
#define  Startup_delay      Quarter_Min
 float temp_in_celsius_0 = 0,
       temp_in_celsius_1 = 1,
       temp_in_kelvin_0 = 0,
       temp_in_kelvin_1 = 0,
       temp_in_fahrenheit_0 = 0,
       temp_in_fahrenheit_1 = 0;
 // Associating Variable Names with pins
 int HeatDemand = 4;
 int Compressor = 5;
 int inPump = 6;
 int outPump = 7;
 int auxOut = 8;
 int LED = 13;
 void setup()
// Setting the mode of the digital pins
pinMode(HeatDemand, INPUT);
pinMode(Compressor, OUTPUT);
pinMode(inPump, OUTPUT);
pinMode(outPump, OUTPUT);
pinMode(auxOut, OUTPUT);
pinMode(LED, OUTPUT);
   // Initialize print
   Serial.begin(115200);
// ****************** Startup Delay to Protect Compressor ********************
   Serial.print("begin startup delay");
   delay(15000);
   Serial.println(", end startup delay");
// ***************************** End Startup Delay ***************************
 void loop(){
 delay(Two_Min);
 void loop()
 Serial.print("Activating Compressor");
  digitalWrite(Compressor, HIGH);
  delay(5000);
 Serial.println(", Deactivating Compressor");
  digitalWrite(Compressor, LOW);
  delay(500);
 Serial.print("Activating inPump");
  digitalWrite(inPump, HIGH);
  delay(5000);
 Serial.println(", Deactivating inPump");
  digitalWrite(inPump, LOW);
  delay(500);
 Serial.print("Activating outPump");
  digitalWrite(outPump, HIGH);
  delay(5000);
 Serial.println(", Deactivating outPump");
  digitalWrite(outPump, LOW);
  delay(500);
 Serial.print("Activating Auxillary Output");
  digitalWrite(auxOut, HIGH);
  delay(5000);
 Serial.println(", Deactivating Auxillary Output");
  digitalWrite(auxOut, LOW);
  delay(500);
// Serial.println("starting loop");
   //Reads the input and converts it to Kelvin degrees
   temp_in_kelvin_0 = analogRead(0) * 0.004882812 * 100;
   temp_in_kelvin_1 = analogRead(1) * 0.004882812 * 100;
   Converts Kelvin to Celsius minus 2.5 degrees error
   temp_in_celsius_0 = temp_in_kelvin_0 - 2.5 - 273.15;
   temp_in_celsius_1 = temp_in_kelvin_1 - 2.5 - 273.15;
   //Converts Kelvin to Celsius minus 2.5 degrees error
   temp_in_fahrenheit_0 = ((temp_in_kelvin_0 - 2.5) * 9 / 5) - 459.67;
   temp_in_fahrenheit_1 = ((temp_in_kelvin_1 - 2.5) * 9 / 5) - 459.67;
   //Print the temperature in Celsius to the serial port
   Serial.print("Celsius_0: ");
   Serial.print(temp_in_celsius_0);
   Serial.print("Celsius_1: ");
   Serial.println(temp_in_celsius_1);
   //Print the temperature in Fahrenheit to the serial port
   Serial.print("Temp_0: "); Serial.print(temp_in_fahrenheit_0);Serial.print(" deg.F"); Serial.print(", Temp_1: "); Serial.print(temp_in_fahrenheit_1);Serial.print(" deg.F");
   Serial.println();
   delay(One_Sec);
I'm only going to have:
  • 2 minute delay at power on (maybe a blinking LED to indicate)
  • "on and waiting" (maybe a 'breathing' LED pattern to indicate)
  • respond to request for heat (true)
  • test for evaporator HX => 34 F = true (variable here)
  • test for storage tank temp =< 90 F = true (variable here)
  • if any of the above go false, then
  • cut power to compressor AND
  • keep running pumps for an additional 60 seconds (variable here)
  • return to initial "on and waiting"
So, I'm not really a programmer, and I'm not quite sure how to proceed at this point. I do know that if I read and try and test (and repeat), that I'll eventually get it to work.
I could use some help.
Here's an example sketch that reads the hall effect flow sensors you are planning on using:
http://diyhacking.com/projects/FlowMeterDIY.ino
The main article is here:
Measure Water Flow Rate and Quantity Arduino DIY Project - DIY Hacking
It seems you have decided to go the way BBP has, using interrupts to count pulses. It is less code intensive to use this method, but you have to remember that there are multiple things that can be going on at any given time. With the simplistic nature of your device, it might not give you much trouble. One interrupt for measuring evap side flow, one interrupt for measuring condenser side flow.
Sorry it took so long for me to reply to this post. I had the general idea that you and BBP had worked out an algorithm that worked for both of you. If you need some coding done, I can help.