Default Am I reading this current (amps) chart correctly?




Looking at Heating mode chart #2, it seems like, when the indoor set-point temp is 70F, and the outside temp is:

32F, the Sanyo uses 6.4 Amps
41F, the Sanyo uses 7.0 Amps
59F, the Sanyo uses 8.4 Amps

And if it was 70F indoors and 70F outdoors, it would be using over 9 Amps??

Is it me? Or is something wrong with this picture??

Xringer is offline   Reply With Quote
Old 02-27-11, 07:15 PM   #2
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

I think you're reading that correctly. Heating capacity declines with temperature.
RobertSmalls is offline   Reply With Quote
Old 02-27-11, 11:10 PM   #3
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

But, when it's cold outdoors, I use about 10 or 12 kWh per day.
When it's warmer (like 59F), I only use 5 or 6 kWh per day.

If it was 70F indoors and 70F outdoors, the dang thing wouldn't even turn on..(Not use 8.4 Amps).
Just 60 watts for the crankcase..

I think the amps scale is upside down..?..
Xringer is offline   Reply With Quote
Old 02-28-11, 04:51 PM   #4
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

The thermostat regulates duty cycle to match the heating/cooling needs of the house.
RobertSmalls is offline   Reply With Quote
Old 03-01-11, 08:25 AM   #5
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

The house stays at about 70F 24/7.

Right now, it's 30F outdoors and the Sanyo is using about 480 watts.
If it was 15 or 20F outdoors, it would be using more power, 600 to 800 watts.

The colder it gets, the more power is needed to extract heat from the extra cold air..

The chart seems to show that colder means using less power!
If it were true, then it would be cheaper to heat your home at when it was -12 deg outside!
Xringer is offline   Reply With Quote
Old 03-01-11, 05:35 PM   #6
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

So your thermostat scales back power draw instead of duty cycle. The effect is the same. Although the above plot shows how much power the heat pump is capable of drawing at any given temperature, that doesn't mean it will do so 24/7.
RobertSmalls is offline   Reply With Quote
Old 03-01-11, 06:35 PM   #7
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Like any other heating system, when it's real cold outdoors, it uses more power to keep the house warm.

Plus, I can see the power used instantaneously. (and by the day, week and month).

Xringer is offline   Reply With Quote
Old 03-01-11, 07:50 PM   #8
mrd
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Milford, DE
Posts: 106
Thanks: 5
Thanked 9 Times in 9 Posts
Default

The chart doesn't seem to make sense. Sure, the maximum capacity of the system declines as the outdoor temperature drops. But, does the power draw of the compressor also drop? I fail to see why that would be so.

The compressor may have a limited maximum RPM, and when it is colder outside, the maximum refrigerant temperature may be colder. Perhaps it takes less power to compress colder refrigerant, and the power draw is limited because the compressor RPM is limited due to friction at internal seals or some other mechanical limit? This is the only practical reasoning I can find. However, I would find it surprising that the max refrigerant temperature is so much lower that it could affect power draw so drastically.
mrd is offline   Reply With Quote
Old 03-01-11, 09:42 PM   #9
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default It sucks warm air out of the cold

and when it's really cold, it starts sucking the money out of my wallet..

I've seen the power increase and can heard the fan cranking up to max speed
on really cold nights.

When I saw the mistake in chart (2), I started worrying about Chart (1)..
I need that chart to be accurate, because I want to measure the R410A pressure.

It shows the pressure going up as the outdoor temp goes up..
Cold air is going to lower the pressure.. Sounds logical.?.
Xringer is offline   Reply With Quote
Old 03-02-11, 06:26 AM   #10
RobertSmalls
Journeyman EcoRenovator
 
RobertSmalls's Avatar
 
Join Date: May 2009
Location: Buffalo, NY
Posts: 344
Thanks: 3
Thanked 17 Times in 15 Posts
Default

Capacity declines faster than CoP as outdoor temperature falls. I assume this takes the form of lower RPM, lower pressure, and less current draw at lower temperatures.

A plot of total daily power consumption versus time would require them to know what sort of house you've installed it in, the orientation of your windows and the sun, etc. Do you think that's the sort of plot Sanyo has supplied you with here?

RobertSmalls is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:54 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design