Default Delayed off relay/circuit for circulation pump

Is there a simpe way to delay the turning off of a circulation pump?

My boiler has only two options for the circulation pump's operation - either always on, or only when the burner is on. I'd like it to keep going for 5-10 minutes after the burner shuts off, so that the heat in the plumbing keeps getting distributed, but I don't want it to run 24/7. I've seen a few relays with adjustable time delay, but they seemed complicated/expensive and I thought that it could be done in some other manner.

Any ideas?

__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
Old 08-24-11, 03:27 PM   #2
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Another way to handle it would be to use a thermal switch of some sort since what you really want is the pump to be on while there is still warm water in the pipe.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
Daox is offline   Reply With Quote
The Following User Says Thank You to Daox For This Useful Post:
Piwoslaw (10-07-11)
Old 08-24-11, 07:12 PM   #3
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

My circulation pumps (from forced hot water /oil heat) turn on when
one of the thermostats calls for heat.

The closed contact on the thermostat pulls in a relay (using 24VAC) that connects 120VAC to the pump.

Seems like you could select the "always ON option", and insert an SSR in series with
the AC going to the pump. Then, you could easily control SSR using 3 to 15 DC
control voltage from a thermostat or a simple 555 timer circuit..

555 Timer Operating Modes
Monostable mode.
Xringer is offline   Reply With Quote
Old 08-25-11, 12:37 AM   #4
Piwoslaw
Super Moderator
 
Piwoslaw's Avatar
 
Join Date: May 2009
Location: Warsaw, Poland
Posts: 961
Thanks: 188
Thanked 110 Times in 86 Posts
Default

The thermal switch is a good idea. I'd wire it in parallel to the burner/pump signal, to make sure it turns on when it should.

__________________
Ecorenovation - the bottomless piggy bank that tries to tame the energy hog.
Piwoslaw is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 12:04 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design