Old 09-15-17, 05:23 PM   #11
oil pan 4
Land owner
 
Join Date: Nov 2012
Location: NM
Posts: 1,026
Thanks: 12
Thanked 127 Times in 107 Posts
Default

Is that BVC or BPVC or something to that effect?
The plastic piping that gave all plastic piping a bad name.

oil pan 4 is offline   Reply With Quote
Old 09-15-17, 10:07 PM   #12
mejunkhound
Apprentice EcoRenovator
 
Join Date: Apr 2011
Location: PNW
Posts: 197
Thanks: 0
Thanked 47 Times in 31 Posts
Default

for a coax tube reference, I have a 70 ft long 3/4 copper inside 1-1/4" pvc evaporator on WSHP, 9 gpm flow. I get 5 Tons at COP of 5.2 for 56F entry water.

Scale accordingly for your 2T unit. e.g. 3.5 gpm and 30 feet long for 3/4 Cu pipe. Probably can scale by OD area for smaller copper.
mejunkhound is offline   Reply With Quote
The Following User Says Thank You to mejunkhound For This Useful Post:
jeff5may (09-17-17)
Old 09-17-17, 10:53 PM   #13
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by oil pan 4 View Post
Is that BVC or BPVC or something to that effect?
The plastic piping that gave all plastic piping a bad name.
It's polybutylene, aka poly-b or PB pipe. The main problem with this type is that the chlorine or chloramine the utilities use to disinfect the water attacks the plastic. It becomes brittle and weakens from the inside out and can fail without warning. To make matters worse, lots of plumbers used acrylic fittings with the poly-b pipe, which suffers the same degradation.

The trailer was originally purchased by me to live in for a few years while I built a house next to it. When I moved into it, I had no clue that my wife hated the property and the trailer from day one. I about got a divorce over that one. We ended up moving out, and my parents assumed the mortgage. Twenty years later, the trailer is still where I put it, and the house never got built. They are charging three times the mortgage payment in rent now.

The piping by the inlet froze a few times before I figured out how to insulate it sufficiently. Both hot and cold supply lines have manifold rigs directly under the water heater, which froze and leaked also. This is why I highly recommend shark-bite fittings. Everything else I used replacing manifold components ended up leaking eventually. Both of the manifolds are now PEX pipe and shark-bite fittings, and have held up for a decade without incident. When the water heater was replaced this summer, it got PEX and shark-bite fittings all the way to the manifolds.

The poly-b pipe is actually pretty stout when it's new. It held it's own and didn't burst during freezing events. It did deform a bit, though. The stuff blows up like a balloon. I couldn't fit a lot of it into the new fittings, so it got replaced with PEX pipe. A good portion of the rest of the place still has gray pipe in it.

Last edited by jeff5may; 09-18-17 at 07:17 AM..
jeff5may is offline   Reply With Quote
Old 09-19-17, 09:27 AM   #14
Ron342
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Maryland
Posts: 120
Thanks: 26
Thanked 12 Times in 8 Posts
Default cheap HEs

Great project!
If you're looking for easily made inexpensive exchangers, I use a coil of refrigeration copper tube which I turned into a similar size coil of poly pipe with copper fitting adapters on the ends, see pics. Mine was 3/8 copper inside 3/4 poly and the 3/4 copper pipe at the adapter ends if sharpened would just fit inside the poly if the poly was warmed.
Use pex if you need it for hi temp.
The copper coil feeds easily into the slick poly and in an hour you can have any size exchanger you want and easily resize it.
Attached Thumbnails
Click image for larger version

Name:	EvappLeft.jpg
Views:	382
Size:	309.6 KB
ID:	7903   Click image for larger version

Name:	IMAG0427.jpg
Views:	363
Size:	505.8 KB
ID:	7904  
Ron342 is offline   Reply With Quote
The Following User Says Thank You to Ron342 For This Useful Post:
geoff (12-19-17)
Old 09-26-17, 10:16 AM   #15
Ron342
Apprentice EcoRenovator
 
Join Date: Feb 2010
Location: Maryland
Posts: 120
Thanks: 26
Thanked 12 Times in 8 Posts
Default

Quote:
Originally Posted by mejunkhound View Post
for a coax tube reference, I have a 70 ft long 3/4 copper inside 1-1/4" pvc evaporator on WSHP, 9 gpm flow. I get 5 Tons at COP of 5.2 for 56F entry water.

Scale accordingly for your 2T unit. e.g. 3.5 gpm and 30 feet long for 3/4 Cu pipe. Probably can scale by OD area for smaller copper.
What's your winter and summer exit temps look like?????

Ron342 is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:10 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design