Old 02-21-14, 05:32 PM   #21
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I found a grossly oversized Hx here:

copper refrigerant pipe: $113
TURBOTEC | COILS, STEAM & WATER | 3-1/2 TON COAX COIL | Surplus City Liquidators

cupronickel refrigerant pipe: $208
TURBOTEC | COILS, STEAM & WATER | 4 TON COAX COIL | Surplus City Liquidators

Both are rated at 450 PSI working pressure (burst pressure much higher). Your water-source setup should run at much lower working pressure in cooling mode (450 PSI = 125 degF saturation temp, 100 degF Tsat = 317 PSI). In heating mode, pressure is not an issue (freeze-up is related to pump sizing).

OR

You could look into China and have one custom built for cheap. Some suppliers will pretty much design and build a single one-off part for you, given pertinent performance specs. Not very expensive, either.

http://www.alibaba.com/product-gs/15...Exchanger.html


Last edited by jeff5may; 02-22-14 at 06:36 AM..
jeff5may is offline   Reply With Quote
Old 02-22-14, 10:21 AM   #22
BeerGrylls
Lurking Renovator
 
Join Date: Dec 2013
Location: Austria
Posts: 25
Thanks: 1
Thanked 1 Time in 1 Post
Default

Thanks Jeff,
I've been looking at those before, but, with shipping and tax they end up half what I paid for my heat pump. Looking for a more budget friendly option. Secondly, I understand that a grossly oversized single hx will destroy my precious compressor due to low speed/flow of R410a. I read that there are minimum flow rates for 410 due to lubrication issues. This is why my hx has 3 circuits with thin lines among other things. Can anybody comment on the minimum flow rate ? At least this is what I read and I am trying to avoid lubrication problems.

Indeed it looks like the Chinese market is a good candidate even price wise, some offer this hx with free shipping:
Aliexpress.com : Buy free shipping fish piano music game carpet Fashion Children's Educational Toys fish Music crawling mat, baby toys blanket from Reliable carpet stair suppliers on Ningbo Haishu Chosen Trade Co., Ltd.
Not sure if the specs are ok. Will keep looking.
If oversized, I understand it is better to have several smaller hxs in parallel due to min flow rate required for 410a.
Cheers,
F

Last edited by BeerGrylls; 02-22-14 at 10:24 AM..
BeerGrylls is offline   Reply With Quote
Old 02-22-14, 10:59 AM   #23
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Oil carrying problems are unlikely in a condenser due to liquid refrigerant being a good solvent. You can add a little R290 (refrigeration grade propane) to act as an oil carrier.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
Old 02-22-14, 11:47 AM   #24
BeerGrylls
Lurking Renovator
 
Join Date: Dec 2013
Location: Austria
Posts: 25
Thanks: 1
Thanked 1 Time in 1 Post
Default

Many thanks for the input Mike. It is good know, however what if the coil becomes an evaporator ? I actually try to refrain from using those designations since they switch around. My outside hx will also be used for cooling/dehumidifying, therefore there will be gas flowing through it too, not just liquid. Should I still be concerned ?
BeerGrylls is offline   Reply With Quote
Old 02-22-14, 04:29 PM   #25
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

The multiple paths and thin lines are a method used in r410 units because they can tolerate more pressure drop in the lines. Since the high side is so high pressure, the smaller lines do not hinder flow like in r22 systems. By using more smaller lines, the mfr's can maximize the surface area of active piping.
jeff5may is offline   Reply With Quote
Old 02-24-14, 01:52 AM   #26
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by jeff5may View Post
...Since the high side is so high pressure, the smaller lines do not hinder flow like in r22 systems...
How do you know that this is true?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 02-24-14, 03:23 AM   #27
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

One of those Purdue research papers. I commented on and maybe cited the article in a past thread somewhere. It had to do with micro-tiny, rifled tube construction and performance optimizing specifically for r410a. I had commented "How will I hack a heat exchanger made out of cap tubes?"
jeff5may is offline   Reply With Quote
Old 02-24-14, 03:57 AM   #28
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I found some literature in a hurry: Micro-groove

main page

specific paper
http://www.microgroove.net/sites/def...6755_final.pdf
jeff5may is offline   Reply With Quote
Old 02-24-14, 03:34 PM   #29
doug30293
Too Many Projects
 
Join Date: Nov 2013
Location: georgia
Posts: 91
Thanks: 0
Thanked 6 Times in 6 Posts
Default

If I may expand somewhat on Jeff's comments:

R410A has roughly 40% greater saturation vapor density than R22. The higher working pressures allow smaller cross section in the same sense that high voltage lines permit smaller wire cross section.

This has multiple benefits. Smaller tubing has lower hoop stress for a given pressure, allowing for thinner walls. Thinner walls increase heat transfer and lower cost. More tubes in a given HX area further increase heat transfer. Higher fluid velocity also increases heat transfer.

R410A gets a bad rap because it doesn't work in old equipment. Systems designed for R410A can outperform R22 and R290.

Ref. " Effects of refrigerant properties on refrigerant performance" Prapainop and Suen. 2012
doug30293 is offline   Reply With Quote
Old 02-25-14, 12:33 AM   #30
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by doug30293 View Post
If I may expand somewhat on Jeff's comments:

R410A has roughly 40% greater saturation vapor density than R22. The higher working pressures allow smaller cross section in the same sense that high voltage lines permit smaller wire cross section.
I'm still having trouble with this notion. I just don't see how higher pressure equates to lower friction ("the smaller lines do not hinder flow like in r22 systems").

The electrical metaphor isn't doing it for me either.

The rest makes perfect sense.

Quote:
Originally Posted by doug30293 View Post
This has multiple benefits. Smaller tubing has lower hoop stress for a given pressure, allowing for thinner walls. Thinner walls increase heat transfer and lower cost. More tubes in a given HX area further increase heat transfer. Higher fluid velocity also increases heat transfer.

R410A gets a bad rap because it doesn't work in old equipment. Systems designed for R410A can outperform R22 and R290.

Ref. " Effects of refrigerant properties on refrigerant performance" Prapainop and Suen. 2012
A well-thought response.

I tried to find a copy of the Prapainop and Suen paper you mentioned, but none of the links I tried were live.

Do you have a working link to the paper?

-AC

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Reply


Tags
ashp, heat pump, inverter, minisplit, wshp

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 07:14 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design