#71 |
Apprentice EcoRenovator
Join Date: Aug 2014
Location: Saskatchewan, Canada
Posts: 117
Thanks: 10
Thanked 16 Times in 12 Posts
|
![]() Interesting mikesolar, I'll have to look into that
|
![]() |
![]() |
![]() |
#72 |
Apprentice EcoRenovator
Join Date: Aug 2014
Location: Saskatchewan, Canada
Posts: 117
Thanks: 10
Thanked 16 Times in 12 Posts
|
![]() Oh and that register in the bathroom is well inside the insulated area, they all are.
|
![]() |
![]() |
![]() |
#73 |
Apprentice EcoRenovator
Join Date: Apr 2012
Location: Phillips, WI
Posts: 109
Thanks: 10
Thanked 30 Times in 25 Posts
|
![]() I just ran across this thread. I built a house 12 years ago. Calculated heat loss was 13,000 BTUH at 70 deg F inside and -20 F outside for 1320 square feet. It was built on a crawlspace, with the crawlspace walls insulated R20, but no insulation in the floor.
I noticed the heating system was running more than it should, so I measured the heat loss at 18,000 BTUH. THEN I got hold of a copy of ASHRAE Handbook of Fundamentals and found the section on basement floors. The estimated heat loss through the floor was almost 5,000 BTUH. I also had trouble with the heater cycling several times per hour. Turned out that the electronic thermostat was designed to cycle five times per hour. It only changed the percentage of run time. I finally found a thermostat that cycled on and off based only on temperature. Now it runs for an hour or two and shuts off for a half hour or more on cold days. I do not feel the temperature variation when it's less than 1.5 deg F or so. |
![]() |
![]() |
![]() |
#74 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
|
![]() Quote:
I did some underfloor insulation under my kitchen floor. I don't have the numbers like you do, but prior to the insulation, on cold winter nights, my floor measured a degree more than the crawlspace temperature. Now, with the insulation in (my scheme is 50% complete), on cold winter nights, the floor measures about a degree less than average kitchen temperature. Do you have a solution for your floor? -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
![]() |
![]() |
![]() |
#75 |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
![]() Speaking of underfloor heating not being as well insulated as it should be, I once did a solar pool heater to replace gas heaters that were only lasting 3-4 years each. The owner had high gas bills and thought the solar would help. I put in a system that was sized right for the pool area but it wouldn't heat. I added a couple more panels. Still not enough heat.
Turns out there was an aquifer running under the pool and sucking out all the heat. Live an learn. Point is, when I first started doing floor heating, I was trying to get people to put 1.5" of SM under the floor, then it was 2", now it is 4"+ if possible ( code in the UK, I'm told) and the passivhaus is 6". Heat loss is dT x U value x area. JR, Maybe you can get an opening to the crawlspace and get some SM on the floor. Do a world of good. |
![]() |
![]() |
![]() |
#76 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
|
![]() Quote:
Are you recommending SM foam (AKA: "blue foam"), rather than white foam because of it's better R-value? I see that it is strongly recommended for applications where a foam insulation would come in direct contact with water, such as exterior foundation insulation, etc. -AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker... |
|
![]() |
![]() |
The Following User Says Thank You to AC_Hacker For This Useful Post: | Ron342 (03-12-15) |
![]() |
#77 | |
Apprentice EcoRenovator
Join Date: Apr 2012
Location: Phillips, WI
Posts: 109
Thanks: 10
Thanked 30 Times in 25 Posts
|
![]() Quote:
My (near) future retirement home was just finished about two years ago. Same size, similar insulation, but the crawlspace has four inches of XPS (extruded polystyrene) insulation. Vapor barrier on the bottom, then the foam, then two to three inches of sand on top for fire resistance. The total calculated and measured heat loss is about 13,000 BTUH. |
|
![]() |
![]() |
![]() |
#78 | |
Master EcoRenovator
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
|
![]() Quote:
SM (XPS) is just a trademark of Dow. Celfort sells the same thing in a pink board. The extruded polystyrene has only one density that I know about (R5/in) and is traditionally used under inverter roofs and underslab but has a much higher GHG content in its manufacture than EPS so people want to use the EPS (it is also cheaper/ Rvalue) |
|
![]() |
![]() |
![]() |
#79 |
Helper EcoRenovator
Join Date: May 2011
Location: Western Washington
Posts: 89
Thanks: 46
Thanked 20 Times in 13 Posts
|
![]() I did the dig for my brothers geothermal.
http://ecorenovator.org/forum/geothe...m-install.html He has a couple of vacuum tube solar collectors on a separate loop with heat exchangers. He can take the peak summer solar heat and put it into the ground for storage. Maybe you can do something along those lines? His first year in there he was not that thrilled with his heat, his ground got cold too. Turns out he uses very little AC so he puts no heat in that way, and he was way late on trying to push heat in with the solar. This year he will aggressively heat the ground heat sink starting in late July. |
![]() |
![]() |
![]() |
#80 | |
Supreme EcoRenovator
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
|
![]() Quote:
When he did a heat load analysis on his house, what were the results? How many feet of pipe are in the ground? -AC
__________________