Old 11-11-14, 12:20 AM   #1
launboy
Apprentice EcoRenovator
 
Join Date: Mar 2011
Location: SE Wisconin
Posts: 107
Thanks: 3
Thanked 11 Times in 9 Posts
Default Simple, Efficient, Defrost

So back in my hottub heatpump experimenting days my biggest problem was by far and wide defrost. I was running my 8,000 btu window a/c with the condenser in nice 104* water, and my evaporator in anywhere between 50* and 15*F Temps. I even ran it a few times while it was snowing.

I tried the Clixon, and a couple other methods, but none were reliable with the simplistic methodolgy I was using and the wide temperature range.

Something that I consistently noticed was that airflow dropped when the coil frosted up, so it got me thinking, there's a fool proof way to determine when the coil is no longer moving air and pulling in heat.

My idea, a flap in the exiting air with a flap and switch, when coil frosted over, air flow reduced, flap lowered, defrost initiated. Obviously a flap isn't ideal, but it pushed me to my next idea, a pressure differential switch. No frost = little differential, frost = more suction between coil and blower wheel. So I Googled it, and I'm not the first guy to try this.

Heat Pump Defrost Cycle Information

He had extraordinary success with his design, and it's exactly what I was scheming. This is the direction I plan to take with my defrost control.

Seeing all the threads regarding different defrost methods and problems, I figured this may be of interest to many here.

Happy Hacking,

Adam

launboy is offline   Reply With Quote
The Following User Says Thank You to launboy For This Useful Post:
AC_Hacker (11-11-14)
Old 11-11-14, 08:01 AM   #2
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

With the evaporator fan not running, while the unit was defrosting, how would the unit know when the hx was frost free? Without another sensor, defrost wouldn't automatically terminate.
jeff5may is offline   Reply With Quote
Old 11-11-14, 09:07 AM   #3
mejunkhound
Apprentice EcoRenovator
 
Join Date: Apr 2011
Location: PNW
Posts: 197
Thanks: 0
Thanked 47 Times in 31 Posts
Default

Most commercial HP defrost cycles either are timed or terminate at a preset evap temperature.

Saw this thread, so thought I'd throw in a VERY simple method I use.
Since am a retied old fart, and home most the time, we have a mirror on a tree outside that allows us to see the evap coils from a few different windows we go by during the normal day.
Also have a manual internal push button switch - look out and see frost, push the button and defrost cycle starts, simple as that. This was before we added out DIY GSHP.

If one wanted to get fancy, LED with photosensor to detect frost to activate switch.

The option most in use here is having the GSHP operates when outside air temp is below 42F, above that the air-air HP functions. For the air-air HP, 4T Evap coil with 2T compressor assures that evap coil never drops below 32F, so 'frost-free'.
mejunkhound is offline   Reply With Quote
Old 11-11-14, 04:53 PM   #4
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I read through the cited article and the author has multiple sensors in play. Besides the evaporator pressure sensor, the system described has thermometer and pressure switch sensors and a thousand dollar controller. The system was remotely logged and trended before a custom defrost program was written.
jeff5may is offline   Reply With Quote
Old 11-11-14, 10:32 PM   #5
launboy
Apprentice EcoRenovator
 
Join Date: Mar 2011
Location: SE Wisconin
Posts: 107
Thanks: 3
Thanked 11 Times in 9 Posts
Default

You guys have made a few good points.

Yes, this guy has a thousand dollar control and many sensors attached to the unit, but he also has a program written to calculate instantaneous SEER and integrate it with his home automation. Point being although he does not do it cheap, it could be done very cheap. In my mind all that is really needed beyond standard heatpump parts are the pressure transducer, and a timer(to terminate defrost). If you want to get fancy, a thermistor on the output of the evap would give you more of a demand termination solution. This is how I plan to run mine.

Mejunkhound, the LED and photosensor is something another member, Xringer I believe, has done some experimenting with, though I'm not sure what his results were.

Adam
launboy is offline   Reply With Quote
The Following User Says Thank You to launboy For This Useful Post:
jeff5may (11-21-14)
Old 11-12-14, 03:11 AM   #6
takyka
Helper EcoRenovator
 
Join Date: Jul 2014
Location: Hungary
Posts: 34
Thanks: 0
Thanked 16 Times in 10 Posts
Default

Quote:
Originally Posted by jeff5may View Post
With the evaporator fan not running, while the unit was defrosting, how would the unit know when the hx was frost free? Without another sensor, defrost wouldn't automatically terminate.
I have a temperature sensor attached between the fins of the evaporator close to the intake and one at exhaust pipe end. When HP stops, The temperature start to rise at both. If there is frost at intake, the intake sensor stop to rise at 0°C (freezing point) and remains there until all ice melts down. Meanwhile the exhaust sensor's temperature continue to climb to a few degrees higher than ambient temp. As long as the heatpump is cycling (even if outdoor temperature is below freezing), with these two sensors one can clearly identify frost buildup and meltdown.

T.

takyka is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 05:29 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design