Old 06-09-16, 05:06 PM   #31
IdleMind
Helper EcoRenovator
 
IdleMind's Avatar
 
Join Date: May 2016
Location: SE Wisconsin
Posts: 55
Thanks: 3
Thanked 14 Times in 10 Posts
Default

Before I started this project I read that ground source heat pump thread. It would be good for me to read it again, I am better able to comprehend it now. Next week I will start collecting and reporting data.

It sure seems like the fan is pulling too much air for the large evaporator that I have. At some point I could rig up a weaker fan. The current fan takes about 85 of the 350 watts. My original plan was to use a passive evaporator to save those watts, I might get back to that sometime in the future.

IdleMind is offline   Reply With Quote
Old 06-09-16, 10:42 PM   #32
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I put a light dimmer on the fans I want to slow down. For the window units that become heat pumps, the low speed is still too fast for defrost mode. The fan motor can be varied to whatever speed you need. Super cheap, too.
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
IdleMind (06-10-16)
Old 06-11-16, 11:08 AM   #33
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Awesome thread. Being able to find txv for less than $10 is the way to go. You can learn A LOT by using cap tubes and even a needle valve in front of the cap tubes, but in the end a cheap txv saves time and money. In fact the coming week I will be posting the updates to the HPWH that include a txv.

Light dimmers are awesome for slowing the fan down. But a have had lots of luck with DC fans as well. More control and they use less watts per cfm.

It is hard to tell just how efficient your water tank heat exchanger is working. It looks freaking amazing, and by your numbers we know it is working pretty good for sure, I like how the copper doesn't have to be IN the water. This helps with corrosion.
Awesome work cant wait to see more updates.
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Old 06-12-16, 12:14 PM   #34
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by MEMPHIS91 View Post
Awesome thread. Being able to find txv for less than $10 is the way to go. You can learn A LOT by using cap tubes and even a needle valve in front of the cap tubes, but in the end a cheap txv saves time and money. In fact the coming week I will be posting the updates to the HPWH that include a txv.

Light dimmers are awesome for slowing the fan down. But a have had lots of luck with DC fans as well. More control and they use less watts per cfm.

It is hard to tell just how efficient your water tank heat exchanger is working. It looks freaking amazing, and by your numbers we know it is working pretty good for sure, I like how the copper doesn't have to be IN the water. This helps with corrosion.
Awesome work cant wait to see more updates.
Just keep the cap tube you have if a txv doesn't save more energy. After all, it is a moving part that can affect lifespan. They tend to work better for air coils where there is a decent amount of temperature gradient between the refrigerant and the air to drive heat flow. With your dx loop, the txv will probably be near wide open until the loop tries to flood. Who knows, it may work better. Can't hurt to try.

Last edited by jeff5may; 06-12-16 at 01:27 PM..
jeff5may is offline   Reply With Quote
Old 06-12-16, 01:21 PM   #35
MEMPHIS91
Journeyman EcoRenovator
 
MEMPHIS91's Avatar
 
Join Date: Apr 2015
Location: Oxford, MS USA
Posts: 496
Thanks: 69
Thanked 87 Times in 61 Posts
Default

Jeff, I more meant that if the cap has to be adjusted time and time and time and time again, that I txv saves time and money on refrigerate. I probably opened my system 6 or more times before getting it right. A cheap txv would have saved me SO much. BUT you are right once the right size cap tube has been made it is best to stay with it. Unless you alter the system SO much that more time again would be wasted on getting the right size yet again.
Plus I'm going to charge with R1270, and that stuff cost WAY to much to waste. =D
__________________
שְׁמַע יִשְׂרָאֵל ה' אֱלֹהֵינוּ ה' אֶחָד
MEMPHIS91 is offline   Reply With Quote
Old 06-12-16, 05:24 PM   #36
stevehull
Steve Hull
 
Join Date: Dec 2012
Location: hilly, tree covered Arcadia, OK USA
Posts: 826
Thanks: 241
Thanked 165 Times in 123 Posts
Default

Memphis,

Your future synopsis will be very instructive and I am eager to read it. For example, you completely buy in on a tvx. I too wish to make use of all your time effort and endless refills of your system.

A few parts may costs just a bit more, but we look forward to you bottom line wisdom.

Thanks in advance.

Steve
__________________
consulting on geothermal heating/cooling & rational energy use since 1990
stevehull is offline   Reply With Quote
Old 06-12-16, 10:53 PM   #37
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by MEMPHIS91 View Post
Jeff, I more meant that if the cap has to be adjusted time and time and time and time again, that I txv saves time and money on refrigerate. I probably opened my system 6 or more times before getting it right. A cheap txv would have saved me SO much. BUT you are right once the right size cap tube has been made it is best to stay with it. Unless you alter the system SO much that more time again would be wasted on getting the right size yet again.
Plus I'm going to charge with R1270, and that stuff cost WAY to much to waste. =D
You're sounding more and more like a professional fridgie tech every day. "Why mess around with something when you can slap in this miraculous part that will work until it doesn't. Spending more time than what is absolutely necessary is counterproductive. Besides, I've got three more stops to make today. How will you be paying for this? My estimate is thirteen hundred dollars..."
jeff5may is offline   Reply With Quote
Old 06-12-16, 11:12 PM   #38
RB855
Helper EcoRenovator
 
RB855's Avatar
 
Join Date: Jul 2012
Location: Jacksonville, fl
Posts: 48
Thanks: 3
Thanked 14 Times in 10 Posts
Default

Dont forget that the cycle is dependent on ALL variables. While your evap will probably remain fairly stable, you will still have seasonal differences with temperature and humidity. You are also dealing with a fairly significant temperature swing on your condenser from 60 to 120F. Captube flows are directly related to delta pressures. A txv takes care of highside pressure swings as a byproduct of maintaining superheat on the suction. A small receiver could help with the temperature swings and keep the highside more stable and always maintain liquid at the txv (since a cold tank will have significantly more liquid ref in it than a hot tank, it needs somewhere to go).

It also doesnt matter how much of your evap is flooded as long as the superheat is maintained. The txv mostly eliminates the purpose of the accumulator function on the compressor, which is why the receiver is suggested. Most txv come out of the box preset 10~20*F superheat and should work without adjusting at all. It dynamically changes flowrates as the conditions demand, vs fixed metering which is tunable only for a specific design condition. With a TXV you charge for subcooling instead. Charging with a receiver is a little bit of a different procedure, but it is more tolerant of high side pressure swings.
RB855 is offline   Reply With Quote
Old 06-13-16, 06:49 PM   #39
IdleMind
Helper EcoRenovator
 
IdleMind's Avatar
 
Join Date: May 2016
Location: SE Wisconsin
Posts: 55
Thanks: 3
Thanked 14 Times in 10 Posts
Default

I got 2 more thermocouples, the one on the tank is shown in photo. The cover over the thermostat was removed and the thermocouple is held tight against the tank by the shinny magnet in upper left. Then the cover was replaced.

The procedure is to unplug power and run 6 gal of water through the tank to cool it down. Then start it up and collect data. The first test is using the stock resistance heater.


The second test is using heat pump. I believe there is very small leak so I don't know the exact charge, but probably around 2 to 2.5 oz.

IdleMind is offline   Reply With Quote
Old 06-13-16, 08:34 PM   #40
RB855
Helper EcoRenovator
 
RB855's Avatar
 
Join Date: Jul 2012
Location: Jacksonville, fl
Posts: 48
Thanks: 3
Thanked 14 Times in 10 Posts
Default

That paints a much clearer picture of what's going on. It's without doubt undercharged, the calculated SC at the 30min mark is 17*F where you have 4-5*. I would bring up the SC and re-evaluate the SH and decide on fan speed and captube length. A lower SH will dehumidify better, but could cost you efficiency and may fall outside the compressors operating ability. Shooting for 10-15 is a good safe realm.

Some other calculations, you applied 916btu of heat from start to stop, which averages 30.55btu/minute or a total capacity of 1840btu/hr. With an average wattage of 378w, meaning your getting an averaged return of 1.4 times applied heat over just electricity consumed. The target evap exit temp is about 15* off, with a target at these conditions of a Delta of 18*F. This is a result of too much airflow and insufficient refrigerant flow. The evaporator absorbed 550btu/hr from the environment, some of which was applied to condensation of moisture. The other 1290btu was aquired from the compressor. (Note, the evaporator btu calc is skewed by the inclusion of the fan motor which does not apply appreciable heat to the system!)

There are 3.412142 BTU/hr in 1 watt
And 8.33 btu to raise 1 gallon 1 degree F.


Last edited by RB855; 06-13-16 at 09:16 PM..
RB855 is offline   Reply With Quote
The Following User Says Thank You to RB855 For This Useful Post:
jeff5may (10-11-16)
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 08:15 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design