Default Fireblock foam burns

I know that spray foam is generally considered to be combustible even when cured but I figured that Dow Great Stuff™ Fireblock foam would be a little harder to ignite than it is.

I didn't put much thought to it and I've been using it since it is available and figured that most people that I've talked to and most online sites about conservation say to use spray foam and don't generally display a concern for fire safety in its use. I figured that this fireblock foam was a better option than the standard stuff, but after playing with it, I'm not sure I'll be paying the extra expense anymore.

I figured I'd need a torch to light the stuff but when I took it outside on the concrete front step, it took about two seconds of contact with the flame of a common butane lighter and it was lit and continued to burn unaided when the lighter was removed.

Here are the points that I figure that people are sold on:
Impedes spread of fire and smoke through service penetrations
Recognized as an Alternate Fireblocking material for residential construction
Tested according to ASTM E84, ASTM E814 (modified), UL 1715
Bright orange colored foam for easy code identification

The only understanding that I have is that the idea of preventing air movement could prevent flame spread.

Here is part of a statement from Dow in response to someone's online review of this product.
"GREAT STUFF (TM) Insulating Foam Sealant products should not be used around heaters, furnaces, fireplaces, or recessed lighting fixtures where it contacts heat conducting surfaces. Cured foam is combustible and may present a fire hazard if exposed to flame or temperatures above 240F."
and
"GREAT STUFF™ FireBlock Insulating Foam Sealant is a minimal-expanding, single-component foam sealant for general purpose building envelope air sealing. This product is defined by the International Building Codes as the use of approved building materials installed in concealed spaces to resist the migration of fire and hot gases. GREAT STUFF™ FireBlock is tinted orange to be more recognizable to building code officials. This product is not approved for use in firestop systems. The Dow Chemical Company makes the GREAT STUFF™ products, if you are looking for other material other than GREAT STUFF™, please refer to 3M’s website."

I added the bold above instead of just posting a partial quote the second statement to keep it in context.

My point is that this product is not an intumescent firestop like some spray foams or encapsulants for spray foams can be. The can does say "Residential Fireblock Penetration Sealant". It also has flame spread characteristics but I don't know what those numbers mean but figured they were numbers that indicated that it was not very flammable. I think that 'FireBlock' is a little bit deceiving as it seems very similar in name to firestop, which is something Dow says its not. Although when looking at the can it doesn't say that it isn't a firestop. The part that says "Flammable. Avoid sources of ignition, open flame, temps above 240f (116c). Pressurized. Can may burst. Do not punture or incinerate. Avoid temps above 120f (49c)." suggested to me that this was when applying the product due to the flammable nature of the propellants used in spray foam.

Why am I posting this thread?
I have seen others on this forum either mentioning its use(and at least one picture) to seal up the knockout penetrations for wires around junction boxes such as light switch boxes, electrical outlet boxes, and light fixture junction boxes. A junction box is designed to be a fire resistant container designed to contain most short circuit arcing(such as bad twist-on wire connections) and overloads until the circuit breaker or fuse blows. They are a specific size, thickness, and material to contain a certain amount of heat. It's my opinion that the knockouts should be sealed, especially when these are covered in insulation in an attic and that heat or arcing would otherwise contact the insulation along with the air sealing needs for conservation.

I personally use a fire rated caulking UL 1479 rated for filling the air gaps in the attic facing junction box knockouts. I think spray foam is just fine in places other than electrical junction boxes and combustion venting, since it is then behind drywall or other fire rated materials in the same area that other materials that burn are located such as wood framing for example. A UL 1479 fire-rated product similar to this is what I think is ideal for electrical junction box air sealing. DAP Fire Stop 10.1 oz. Silicone Sealants (2-Pack)-181244 at The Home Depot I actually used a White Lightning based UL 1479 product but I can't find the same product(their UL 1479 stuff) anymore.

Thoughts?


Last edited by MN Renovator; 11-15-13 at 09:43 AM..
MN Renovator is offline   Reply With Quote
The Following 3 Users Say Thank You to MN Renovator For This Useful Post:
Daox (11-15-13), james martin (11-19-13), Piwoslaw (11-16-13)
Old 11-15-13, 09:53 AM   #2
Daox
Administrator
 
Daox's Avatar
 
Join Date: Aug 2008
Location: Germantown, WI
Posts: 5,525
Thanks: 1,162
Thanked 374 Times in 305 Posts
Default

Good to know. I know I've used regular great stuff in my electrical boxes. While I don't foresee it being an issue, I will change what I use in the future. Thanks.
__________________
Current project -
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.



To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.
&
To view links or images in signatures your post count must be 0 or greater. You currently have 0 posts.

Last edited by Daox; 11-15-13 at 10:29 AM..
Daox is offline   Reply With Quote
Old 11-15-13, 10:14 AM   #3
MN Renovator
Less usage=Cheaper bills
 
MN Renovator's Avatar
 
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 939
Thanks: 41
Thanked 116 Times in 90 Posts
Default

Granted it doesn't light up and burn like paper but it is easier to start on fire than say holding a lighter to a 2x4, for example.

I found a couple of demonstrations of how it burns. My experience of using a lighter to this stuff was very similar to the DAP fireblock video.

DAP fireblock


Dow Great Stuff Pro Gaps and Cracks


Comparison of one firestop foam and two fireblock foams

Last edited by MN Renovator; 11-15-13 at 10:17 AM..
MN Renovator is offline   Reply With Quote
The Following User Says Thank You to MN Renovator For This Useful Post:
Scifficus (11-15-13)
Old 11-15-13, 10:37 AM   #4
MN Renovator
Less usage=Cheaper bills
 
MN Renovator's Avatar
 
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 939
Thanks: 41
Thanked 116 Times in 90 Posts
Default

Here's another nice video, it goes into some detail with informal torch application to a number of different insulation materials including multiple forms of batt insulation, cellulose, aircrete and foams.
MN Renovator is offline   Reply With Quote
Old 11-15-13, 08:56 PM   #5
Minimac
Lurking Renovator
 
Join Date: Oct 2012
Location: Upstate NY
Posts: 29
Thanks: 7
Thanked 2 Times in 1 Post
Default

Thanks for posting! Fortunately for me, I had access to a commercial firestop product when I needed it while I was building. Very interesting that the closed cell insulation seemed to perform better than the greatstuff "firestop".
Minimac is offline   Reply With Quote
Old 11-15-13, 10:02 PM   #6
iamgeo
Apprentice EcoRenovator
 
Join Date: Aug 2010
Location: Lakehills, Tx
Posts: 168
Thanks: 4
Thanked 10 Times in 9 Posts
Default

Wow! Thanks for the information.
iamgeo is offline   Reply With Quote
Old 11-15-13, 10:24 PM   #7
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

I prefer using drywall mud in the cheese whiz container, whatever it's called. Inherently cheap, not gonna burn. Seals up like real mud.
jeff5may is offline   Reply With Quote
Old 11-16-13, 07:46 AM   #8
Servicetech
Apprentice EcoRenovator
 
Servicetech's Avatar
 
Join Date: Nov 2013
Location: Moore Oklahoma
Posts: 267
Thanks: 108
Thanked 23 Times in 21 Posts
Default

You could use duct mastic to seal the holes. Would be interesting to see a burn test done on it since it's used on furnaces.
Servicetech is offline   Reply With Quote
Old 11-16-13, 10:27 AM   #9
MN Renovator
Less usage=Cheaper bills
 
MN Renovator's Avatar
 
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 939
Thanks: 41
Thanked 116 Times in 90 Posts
Default

I understand that duct mastic is used on ductwork but is it also used on the critically hot areas such as exhaust flues? I'd figure a masonry fireplace sealant would be okay too. It might be a good idea to check the conductivity(in case it flows into the box a little) and adhesion to the surfaces you want to have it attach to as well. I think its still a better idea to stick with something that is rated for both UL 1479 and UL 2079 when in an area that has an increased hazard. Granted a 4 hour fire rating with a product like this might be a little overkill but it's only $11.47 and the tube could handle all of the more hazardous air sealing for most houses. Shop 3M 10.1-oz Red Specialty Caulk at Lowes.com
MN Renovator is offline   Reply With Quote
Old 11-16-13, 02:28 PM   #10
Quest
Apprentice EcoRenovator
 
Join Date: Feb 2011
Location: Canada
Posts: 109
Thanks: 13
Thanked 13 Times in 11 Posts
Default

I'm not aware of ordinary duct mastic able to handle the high heat on furnace exhaust piping.

I'd go with what MN Renovator suggested RE: masonry fireplace sealant instead (or any proper UL rated/fire rated sealant).

Q.

Quest is offline   Reply With Quote
Reply


Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:56 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design