03-14-14, 12:29 PM | #111 | |
with flow of 3.65 gpm in each loop at Delta T of 20* F , (tank vs. water inside pex) should transfer about 15 Tons of heat = 180K btus At a head loss of 7.65' HL = K x C x L x F^1.75 K = .0034, C = .933, L = 250, F = 3.65 Way more than enough HX for radiant floors. There are two things 180,000 btus would be too much for a solar heated well insulated house. Also two loops of 250' pex is very little. Spacing between pipes should be no more than one foot apart and they need to be closer where there are restrictions like in bathrooms so 500 feet run covers 500 square feet maximum. The length of pipe needs to match the heat requirement of each room so the pipes may need to be closer than one foot. |
The Following User Says Thank You to dhaslam For This Useful Post: | buffalobillpatrick (03-21-14) |
03-14-14, 12:52 PM | #112 |
dhaslam,
I was discussing the solar tank HX that will provide heat to radiant floor system, when solar tank is hotter than 80* F The radiant floor will have 3000' of 1/2" O2 barrier pex. "I will pull heat out via a HX of 3/4" x 500' loop of o2 barrier pex" Sizing is difficult because I want this HX output to be as close as possible to solar tank temp. within budget. BBP Last edited by buffalobillpatrick; 03-14-14 at 12:57 PM.. |
03-14-14, 02:21 PM | #113 |
What's the name of the nearest town, or what is your zip code?
The Following User Says Thank You to AC_Hacker For This Useful Post: | buffalobillpatrick (03-21-14) |
03-14-14, 03:02 PM | #114 |
80813
Teller County Co. Zone 5/B dry Design temp 2* F AFI = 2500 Mean Annual Temp. 40* F HDD 6415 Lat = 38.8* Altitude 8,800' Very good Solar, lots of UV, I can get a sunburn in 30 min. BBP Last edited by buffalobillpatrick; 03-14-14 at 03:12 PM.. |
03-14-14, 03:23 PM | #115 |
The ACR tubing that I can find is 3,000psi with "Rated Internal Working Pressure" = 363psi
I don't know what "Internal Working Pressure" means? BBP |
03-14-14, 05:22 PM | #116 |
Here's one good for more than 700PSI working pressure:
WP96602 Copper Coil, For Water, Type L - Grainger Industrial Supply You'll want 1/2" OD. Note that "for water" just means that you'll have to blow out any dust with nitrogen before using it in a HVAC application. Any moisture inside would be taken care of when you pull the vacuum.
The Following User Says Thank You to NiHaoMike For This Useful Post: | buffalobillpatrick (03-14-14) |
03-14-14, 05:41 PM | #117 |
You don't need type L tubing it is only really used for water lines underground and for commercial and resi towers.
As long as the tube meets ASTM B-280 it is good. Don't worry about the pressure rating. A general rule is that the smaller the tube diameter, the higher it pressure rating. |
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (03-21-14) |
03-14-14, 05:45 PM | #118 | |
The Following User Says Thank You to Mikesolar For This Useful Post: | buffalobillpatrick (03-14-14) |
03-14-14, 05:47 PM | #119 | |
ACR and type L are equivalent.
Copper Tube Handbook: II. Recommendations for Various Applications Quote:
03-14-14, 05:50 PM | #120 | |