Originally Posted by buffalobillpatrick View Post
dhaslam,

"That doesn't sound right. I use a calculation of about 6 watts per metre which would be about 7 watts per foot pipe run. I have 1/2 mile of pipe for a 2500 sq' bungalow. Of course being close to passive standard less than half if the circuits are used normally. South facing rooms and kitchen usually have enough passive heat."

what don't sound right?

BBP
It looks like 2 x parallel loops of 250' of 3/4" pex,

with flow of 3.65 gpm in each loop
at Delta T of 20* F , (tank vs. water inside pex)
should transfer about 15 Tons of heat = 180K btus
At a head loss of 7.65'
HL = K x C x L x F^1.75
K = .0034, C = .933, L = 250, F = 3.65
Way more than enough HX for radiant floors.


There are two things 180,000 btus would be too much for a solar heated well insulated house. Also two loops of 250' pex is very little. Spacing between pipes should be no more than one foot apart and they need to be closer where there are restrictions like in bathrooms so 500 feet run covers 500 square feet maximum. The length of pipe needs to match the heat requirement of each room so the pipes may need to be closer than one foot.

dhaslam is offline   Reply With Quote
The Following User Says Thank You to dhaslam For This Useful Post:
buffalobillpatrick (03-21-14)
Old 03-14-14, 12:52 PM   #112
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

dhaslam,

I was discussing the solar tank HX that will provide heat to radiant floor system, when solar tank is hotter than 80* F

The radiant floor will have 3000' of 1/2" O2 barrier pex.

"I will pull heat out via a HX of 3/4" x 500' loop of o2 barrier pex"

Sizing is difficult because I want this HX output to be as close as possible to solar tank temp. within budget.

BBP

Last edited by buffalobillpatrick; 03-14-14 at 12:57 PM..
buffalobillpatrick is offline   Reply With Quote
Old 03-14-14, 02:21 PM   #113
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

What's the name of the nearest town, or what is your zip code?

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
buffalobillpatrick (03-21-14)
Old 03-14-14, 03:02 PM   #114
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

80813

Teller County Co.

Zone 5/B dry

Design temp 2* F
AFI = 2500
Mean Annual Temp. 40* F

HDD 6415

Lat = 38.8*

Altitude 8,800'

Very good Solar, lots of UV, I can get a sunburn in 30 min.

BBP

Last edited by buffalobillpatrick; 03-14-14 at 03:12 PM..
buffalobillpatrick is offline   Reply With Quote
Old 03-14-14, 03:23 PM   #115
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

The ACR tubing that I can find is 3,000psi with "Rated Internal Working Pressure" = 363psi

I don't know what "Internal Working Pressure" means?

BBP
buffalobillpatrick is offline   Reply With Quote
Old 03-14-14, 05:22 PM   #116
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

Here's one good for more than 700PSI working pressure:
WP96602 Copper Coil, For Water, Type L - Grainger Industrial Supply
You'll want 1/2" OD. Note that "for water" just means that you'll have to blow out any dust with nitrogen before using it in a HVAC application. Any moisture inside would be taken care of when you pull the vacuum.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (03-14-14)
Old 03-14-14, 05:41 PM   #117
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

You don't need type L tubing it is only really used for water lines underground and for commercial and resi towers.

As long as the tube meets ASTM B-280 it is good. Don't worry about the pressure rating. A general rule is that the smaller the tube diameter, the higher it pressure rating.
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (03-21-14)
Old 03-14-14, 05:45 PM   #118
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Quote:
Originally Posted by dhaslam View Post
It looks like 2 x parallel loops of 250' of 3/4" pex,

with flow of 3.65 gpm in each loop
at Delta T of 20* F , (tank vs. water inside pex)
should transfer about 15 Tons of heat = 180K btus
At a head loss of 7.65'
HL = K x C x L x F^1.75
K = .0034, C = .933, L = 250, F = 3.65
Way more than enough HX for radiant floors.


There are two things 180,000 btus would be too much for a solar heated well insulated house. Also two loops of 250' pex is very little. Spacing between pipes should be no more than one foot apart and they need to be closer where there are restrictions like in bathrooms so 500 feet run covers 500 square feet maximum. The length of pipe needs to match the heat requirement of each room so the pipes may need to be closer than one foot.
3.65gpm with a 20F dT is 36,500btu x 2 loops is 73Mbtu. I don't know where 180Mbtu comes from.
Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (03-14-14)
Old 03-14-14, 05:47 PM   #119
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

ACR and type L are equivalent.
Copper Tube Handbook: II. Recommendations for Various Applications
Quote:
Air-Conditioning and Refrigeration Systems
Copper is the preferred material for use with most refrigerants. Use Types L, ACR or as specified.
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (03-14-14)
Old 03-14-14, 05:50 PM   #120
Mikesolar
Master EcoRenovator
 
Mikesolar's Avatar
 
Join Date: Aug 2012
Location: Toronto
Posts: 958
Thanks: 40
Thanked 158 Times in 150 Posts
Default

Quote:
Originally Posted by NiHaoMike View Post
Having taken apart or built a lot of frig systems, I can't remember finding much type L tubing in it but, I am sure someone will use it. Depends on the manufacturer I guess.

Mikesolar is offline   Reply With Quote
The Following User Says Thank You to Mikesolar For This Useful Post:
buffalobillpatrick (03-21-14)
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 02:45 AM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design