Bench Testing DIY W/W Heat Pump
Thinking of a way to Bench Test COP of my DIY W/W HP.
Also needed for charging refrigerant. Using garden hoses, not pumps!!! Set & measure water flow rates through Evaporator & Condenser. say 6gpm Use 5gal bucket method. Temperature rise (delta-T*F) of Condenser water in/out can be measured. BTU = 500 x 6 (GPM) x delta-T*F With Amp meter on Compressor, is this a good way to estimate Watts? How about a Kill-a-Watt meter? Calculate COP = Energy out / Energy In Of course this isn't including the water pumps energy that will be in final product, I think manufactures conveniently don't include this either? Even better, but more expensive, is to get 2 x 55gal drums & use pumps. But as actual pump flow rates can't be determined very accurately, the tank temperatures would have to measured & averaged as temperature would vary with location within tank. I have a nice expensive water flow gauge, but its restriction effects flow some. Last edited by buffalobillpatrick; 11-18-14 at 01:56 PM.. |
|
|