Old 05-12-14, 03:07 PM   #21
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

Blue Bomber, did U read post #9?

A/C 8,800' altitude.

Many differences vs. England. Does this change the question?

Closer to the Alaska climate than to England, but not as severe & with better solar.

8" snow yesterday.


Last edited by buffalobillpatrick; 05-12-14 at 03:11 PM..
buffalobillpatrick is offline   Reply With Quote
Old 05-12-14, 05:44 PM   #22
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

That's the two things I don't miss most about Colorado: the snows in May and the thin air. I can run a few miles here and still have energy for the rest of the day. I still get heckled for carrying a coat with me year-round, though. I don't know if I'll ever shake that habit.

Last edited by jeff5may; 05-14-14 at 03:57 AM..
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (05-29-14)
Old 05-12-14, 07:03 PM   #23
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by buffalobillpatrick View Post
...A/C 8,800' altitude... Many differences vs. England. Does this change the question?
Since you're building your house and building your solar/heat pump/radiant system, you might want to check the HDDs and solar gain potentials of the places you're trying to compare.

It might be in your interest to do so before you build.

BTW, did you ever post your building drawings on the forum?

Somehow, I must have missed that part.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following User Says Thank You to AC_Hacker For This Useful Post:
buffalobillpatrick (05-12-14)
Old 05-13-14, 03:06 AM   #24
MN Renovator
Less usage=Cheaper bills
 
MN Renovator's Avatar
 
Join Date: Nov 2010
Location: Minneapolis, MN
Posts: 939
Thanks: 41
Thanked 116 Times in 90 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
Do you actually think that a traditional hydronic heating setup (which is designed for 140F - 160F feed temps) will provide the required heat transfer?

This is exactly the place where traditional thinking fails in low temperature heating installations like solar, geothermal, etc.

Very few hydronic installations (Daox excepted) have built-in efficiency to take advantage of feed temps on the 110 range (and lower).

Vlad's house works with 12" spacing & aluminum heat spreaders because he heats all the floor area, has rigorously reduced infiltration, and put in very good insulation from the start. With three floor levels, his floor area/house volume ratio is fairly high, which favors radiation. Also because his house is large and vaguely tends toward a cubic form, his external area/house volume ratio is relatively low so his house favors lower skin losses.

Did I mention his floor is topped with porcelain tiles, which has a very high U-value?

Lastly, he lives in the Vancouver Canada area and the HDD are not as high as they are in a place like Minneapolis, MN.

Vlad reported feed temps in the 112 range when the weather got really awful.

Of course, awful in Vancouver could be a relief in a Minneapolis winter, or a Colorado winter at high elevation.

-AC
When I was talking traditional, I was actually thinking of in-floor as opposed to radiator against the wall. Traditional being hydronic as opposed to a heat pump setup. Even Daox has loop overkill for his serious window and high levels of insulation with 110f input temps. A hydronic in-floor loop, air sealing of 3ACH or less, insulation better than code(I prefer double of the older R20/R13+5 code and a step better than the 2012 IECC 20+5 or 13+10 values for climate 6+), and double pane or better windows with good seals should be fine with 110f input temps and a reasonable water flow rate.

"Lastly, he lives in the Vancouver Canada area and the HDD are not as high as they are in a place like Minneapolis, MN."

Values are in SI (C, not F).
Minneapolis, MN
http://cms.ashrae.biz/weatherdata/STATIONS/726580_s.pdf
Vancouver, BC
http://cms.ashrae.biz/weatherdata/STATIONS/718920_s.pdf

You weren't kidding, Vancouver seems nice.
MN Renovator is offline   Reply With Quote
The Following User Says Thank You to MN Renovator For This Useful Post:
buffalobillpatrick (05-13-14)
Old 05-13-14, 10:39 AM   #25
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

What I wanted was discussion on solar recharge of shallow loop field.
Then I asked about insulation over loop field.

I expect to have excess solar heated water most of the weeks per year.
360ft2 panels mounted close to vertical.

For $800 I could buy a 2nd 1000 gallon fiberglass tank.

House is 48' x 36' rectangle ICF, main level is a walkout basement.

About 40% of walls will be below grade. Simple 2 plane roof, ridge running East & West.
Front faces East, high ceiling greatroom/kitchen, 2 bedrooms with 2 bathrooms in rear 1/2 (West end) Rear 1/2 will have upstairs 3rd bedroom & bathroom.
R23 walls R51 vented steel roof.

Last edited by buffalobillpatrick; 05-13-14 at 10:47 AM..
buffalobillpatrick is offline   Reply With Quote
Old 05-14-14, 01:34 AM   #26
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by MN Renovator View Post
...Even Daox has loop overkill for his serious window and high levels of insulation with 110f input temps...
I haven't actually talked this issue over with Daox, but it seems pretty clear that he is working on the principle that a highly efficient house, coupled with a highly efficient floor, means that sufficient heating can be achieved at very low feed temperatures.

That is at the core of 'low temperature heating'.

With fossil fuel, the difference in lowering feed temperatures a degree or two is pretty small.

With a heat pump, lowering the feed temp a few degrees makes a big change in efficiency.

With solar, it means that you can heat directly with solar heated water down to a lower temperature before you need to either extract more heat with a heat pump or else rely on a back-up heat source.

-AC
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
The Following 2 Users Say Thank You to AC_Hacker For This Useful Post:
buffalobillpatrick (05-14-14), jeff5may (05-29-14)
Old 05-29-14, 09:27 AM   #27
buffalobillpatrick
Master EcoRenovator
 
Join Date: Mar 2014
Location: Florissant, Colorado
Posts: 599
Thanks: 814
Thanked 59 Times in 55 Posts
Default

http://www.byfy.lth.se/fileadmin/byf...-1018EKweb.pdf

Solar + heat pump Combisystem, Sweden study.

System 5 pg82 gave best performance.
buffalobillpatrick is offline   Reply With Quote
Old 05-29-14, 07:06 PM   #28
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

Quote:
Originally Posted by AC_Hacker View Post
I haven't actually talked this issue over with Daox, but it seems pretty clear that he is working on the principle that a highly efficient house, coupled with a highly efficient floor, means that sufficient heating can be achieved at very low feed temperatures.

That is at the core of 'low temperature heating'.

With fossil fuel, the difference in lowering feed temperatures a degree or two is pretty small.

With a heat pump, lowering the feed temp a few degrees makes a big change in efficiency.

With solar, it means that you can heat directly with solar heated water down to a lower temperature before you need to either extract more heat with a heat pump or else rely on a back-up heat source.

-AC
This statement fits perfectly in BBP's other thread, concerning the operation and design of his combo system. Just as with very low (outdoor/source) temperatures, the efficiency of the heat pump suffers when you demand high heating temperatures out of it. He was concerned on how to efficiently source 130+ degree domestic water from the heat pump. When I suggested running a gas boiler when the sun source ran out, the wolves jumped on me.

At a certain point, the gas boiler would do a better job than the heat pump at providing hot water. Especially when the hot water tap is running, the heat pump may just not keep up with demand. It is better doing the recovery of the hot water tank after the demand has stopped. In any case, the heat pump would just rob more solar energy from the solar heat store, where the boiler would not.

Last edited by jeff5may; 05-29-14 at 07:09 PM..
jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (06-01-14)
Old 05-29-14, 10:04 PM   #29
NiHaoMike
Supreme EcoRenovator
 
NiHaoMike's Avatar
 
Join Date: Oct 2008
Location: Austin, TX
Posts: 1,154
Thanks: 14
Thanked 257 Times in 241 Posts
Default

The heat pump, being a pretty big unit at 2 tons or so, will have no problems keeping up with DHW demand. (My little 1/2 ton unit easily keeps up with demand running only 3-4 hours per day on average.) So the only remaining reasons to switch to the boiler are if the heat pump breaks down, if the heat pump can't keep up with home heating demand (at which point you switch into hybrid mode if it's still above the balance point), if the incoming water gets too close to the freezing point, or if it becomes more efficient to use the boiler.

The only demand for 130F water (dishwasher) only needs a few gallons per use. As such, just warming up the boiler will significantly cut into the efficiency. The heat pump condenser has much less thermal mass (especially for a plate exchanger) so the heat pump will still be more efficient than using the heater built into the dishwasher. (Of course, it would help a lot to have the dishwasher as close to the heat pump as possible. Like put the heat pump in the basement directly below the kitchen.)
__________________
To my surprise, shortly after Naomi Wu gave me a bit of fame for making good use of solar power, Allie Moore got really jealous of her...
NiHaoMike is offline   Reply With Quote
The Following User Says Thank You to NiHaoMike For This Useful Post:
buffalobillpatrick (06-01-14)
Old 05-30-14, 04:06 AM   #30
jeff5may
Supreme EcoRenovator
 
Join Date: Jan 2010
Location: elizabethtown, ky, USA
Posts: 2,428
Thanks: 431
Thanked 619 Times in 517 Posts
Send a message via Yahoo to jeff5may
Default

The topic was what happens when I fill up my hot tub.

jeff5may is offline   Reply With Quote
The Following User Says Thank You to jeff5may For This Useful Post:
buffalobillpatrick (06-01-14)
Reply



Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 03:03 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design