Thermal Properties of Metals, Conductivity, Thermal Expansion, Specific Heat - Engineers Edge

I was looking at the heat conductivity of Aluminum,
and it seems like a copper-to-copper HX would give a lot more heat transfer.
My old Solar hotwater system used a copper-to-copper double-walled HX.
The problem was the clean-out access started leaking too much.

But, I still like the high pressure (and BTU) rating of this one..
20 Plate Cu Brazed Heat Exchanger SS304 1" MPT B3-32 | eBay
For a mere $175USD, that's one sweet HX..

It seems like a good choice for my old Sanyo unit, and it's small enough to easily package up inside a well insulated box..

Cheers,
Rich

Xringer is offline   Reply With Quote
Old 08-19-11, 07:45 AM   #902
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Xringer View Post
It seems like a good choice for my old Sanyo unit, and it's small enough to easily package up inside a well insulated box..
I hope you have better luck than I did keeping the high-pressure refrigeration gases from leaking out from MPT fittings. The refrigeration gasses are going through very large temperature cycles, to say nothing of the HX being subjected to vibration.


What you want on the refrigeration side is a "sweat fitting". Don't let the name fool you into thinking that it implies sweat soldering, that would be a mistake. You need to braze your refrigeration tubing, in order to withstand the temperature cycling and vibration... Or else use a compression fitting, which this is not.

The HX you linked to is a water-to-water HX.

-AC_Hacker
Attached Thumbnails
Click image for larger version

Name:	sweat-fitting.jpg
Views:	3424
Size:	20.5 KB
ID:	1689  
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 08-19-11, 08:56 AM   #903
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Except for those connections, it sure 'seems' like a good fit for a 2-ton ASHP water heater.

I was thinking that 1" MPT Screw-on Flare adapters for the 1/4" & 5/8" OD lineset,
might work for R290, and maybe even R410A..

It seems like a heating only app would not require "very large temperature cycles".

What if the HX was always kept above 40F, to avoid freeze damage,
and the maximum upper range was 120F to 170F ..?.
(How high does your Sanyo go)??

This seems very close to the normal temp range, of my current forced hot water baseboard system..
The largest extremes might occur during the Defrost cycles.
Depending on the way it was implemented.


If Propane was used, (outdoors of course) and the threads leaked a little,
I have to wonder if it would be a big deal, topping-off the charge once in a while.?.







Design pressure 3.0 Mpa (435 psi)
Test Pressure 4.5 Mpa (650 psi)
Design Temperature -195°C to +220°C (-319°F to 430°F)
Refrigeration Capacity 5-25KW (17,000-85,000 BTU/hour)

Applications:
SVO conversions, Heat pump system, household type central air conditioning,
after heat recycling, refrigeration equipment, industry cold water machine,
cooleroil and so on
Xringer is offline   Reply With Quote
Old 08-19-11, 09:56 AM   #904
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Xringer View Post

Except for those connections...

I was thinking that...

It seems like...

What if the HX was always...

This seems very close to...

If Propane was used... topping-off the charge once in a while.?.
Well, there's certainly nothing to stop you from actually trying it...

Then again, there's nothing to stop you from finding & ordering the correct heat exchanger either.

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 08-20-11, 01:26 AM   #905
launboy
Apprentice EcoRenovator
 
Join Date: Mar 2011
Location: SE Wisconin
Posts: 107
Thanks: 3
Thanked 11 Times in 9 Posts
Default

I know there has been talk of hacking an inverter minisplit in this thread. AC Hacker I believe you mentioned it. It's always been talked about in a way with the OD Unit still in tact and hooking it just to a Plate exchanger with no ID unit. The problem with that being the electronics. Why not just use the whole thing and replace the evap coil inside with the plate exchanger, then elecrtonics are not an issue. Does anyone know how the minisplits choose a fan/compressor speed? Is it just a computer logic thing, does it look at pressures, incoming/leaving air temp, coil temps, etc? Some of those would be easy to modify to still work without an actual evap coil, others wouldn't as much.

Adam
launboy is offline   Reply With Quote
Old 08-20-11, 07:31 AM   #906
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by launboy View Post
I know there has been talk of hacking an inverter minisplit in this thread. AC Hacker I believe you mentioned it. It's always been talked about in a way with the OD Unit still in tact and hooking it just to a Plate exchanger with no ID unit. The problem with that being the electronics. Why not just use the whole thing and replace the evap coil inside with the plate exchanger, then elecrtonics are not an issue. Does anyone know how the minisplits choose a fan/compressor speed? Is it just a computer logic thing, does it look at pressures, incoming/leaving air temp, coil temps, etc? Some of those would be easy to modify to still work without an actual evap coil, others wouldn't as much.

Adam
I was thinking of just buying a new indoor unit to use with my spare outdoor unit.
Not too expensive. Sanyo KHS2472 Heat Pump Indoor Wall Unit

But, I found my Sanyo OD unit has a test mode (T-Run), where it will run stand-alone.
http://ecorenovator.org/forum/geothe...html#post12206

So, if I can repair my OD unit and get the right HX hooked up, I might just
be able to warm up a lot of hot water..

Anyways, my point is, maybe some or all inverter type OD units have some
kind of stand-alone test mode, that might be useful to DIY hackers..
Xringer is offline   Reply With Quote
Old 08-20-11, 08:06 AM   #907
Xringer
Lex Parsimoniae
 
Xringer's Avatar
 
Join Date: Feb 2009
Location: Woburn, MA
Posts: 4,918
Thanks: 114
Thanked 250 Times in 230 Posts
Default

Quote:
Originally Posted by AC_Hacker View Post
Well, there's certainly nothing to stop you from actually trying it...

Then again, there's nothing to stop you from finding & ordering the correct heat exchanger either.

-AC_Hacker
Hey, for a measly $175, it comes in 1/2" copper sweat..

B3-32A 20 Plate Heat Exchanger [HX3220] | DudaDiesel Biodiesel Supplies



Have not seen this version in their Ebay store..
Xringer is offline   Reply With Quote
Old 08-20-11, 10:38 AM   #908
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by Xringer View Post
Hey, for a measly $175, it comes in 1/2" copper sweat..
Now you're talking.

This configuration will allow you to braze your refrigerant side and get a permanent seal, so no problem there.

The other side will constrict your water flow a bit but it should not be a problem, if you braze your water connectors (what ever they may be) to the outside of your fittings.

I have written to Dudadiesel & another ebay seller, inquiring about being able to order HXs with water pipe fittings on one side and sweat fittings on the other, but I have not heard back from either seller. Maybe if enough people inquire, they will be more motivated.

-AC_Hacker
__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Old 08-21-11, 09:21 AM   #909
okpiddler
Lurking Renovator
 
Join Date: Feb 2011
Location: NE Oklahoma
Posts: 15
Thanks: 0
Thanked 0 Times in 0 Posts
Default My one inch pipe threads are not leaking

I was short one brass fitting and tried to use a copper one and it leaked so had to get another brass fitting. I used plenty of teflon tape and a lot of torque. When I silver soldered the copper to the brass fitting I used a lot of heat and ran water over the wrench flats of the brass fitting. It has been running since last fall with no leakage. I even submersed the whole unit in water to verify no leakage and I use a sight glass in the liquid line. THe unit only holds about a pound of r 22 so if it were leaking performance would drop off quick. BUT, if I were going to do it again I would do as Hacker has said and stay away from the pipe threads at least on the high side.
Sorry I have been gone so long! Have been doing lots of other things.
okpiddler is offline   Reply With Quote
Old 08-21-11, 12:30 PM   #910
AC_Hacker
Supreme EcoRenovator
 
AC_Hacker's Avatar
 
Join Date: Mar 2009
Location: Portland, OR
Posts: 4,004
Thanks: 303
Thanked 723 Times in 534 Posts
Default

Quote:
Originally Posted by okpiddler View Post
Sorry I have been gone so long! Have been doing lots of other things.
Welcome back!

-AC_Hacker

__________________
I'm not an HVAC technician. In fact, I'm barely even a hacker...
AC_Hacker is offline   Reply With Quote
Reply


Tags
air conditioner, diy, gshp, heat pump, homemade


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 10:46 PM.


Powered by vBulletin® Version 3.8.11
Copyright ©2000 - 2024, vBulletin Solutions Inc.
Ad Management by RedTyger
Inactive Reminders By Icora Web Design